truss load calcs.
Jburgess
Solar Expert Posts: 130 ✭✭✭
My local building department red-lined my permit application to expand my solar system wanting structural load calcs for the trusses and additional load of the solar panels. Is this common?
Re: truss load calcs.
For our building permit (California) we needed the sign-off of a PE (Professional Engineer) to validate the roof loads and mounts met code.
Re: truss load calcs.My local building department red-lined my permit application to expand my solar system wanting structural load calcs for the trusses and additional load of the solar panels. Is this common?
Very common. You will be adding a fairly heavy load, and possibly increasing the wind load of the roof.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
I have 72 panels on my roof, they surely wanted the load calcs but they were also concerned that the racks were attached into the truss directly I suspect for wind loading.
This house is somewhat over trussed because of the concrete roof tile. -
A properly built roof would be able to handle the panels because they are nothing compared to what it should be able to withstand. But there's that bug-a-bear: "properly built". That's what they want to make sure of. In some cases it's the building department's own fault for having too little demanding code in the first place. I couldn't believe what is allowed here in BC when I first found out. Things like 3/8" sheathing, which would be laughed at back East (insufficient for any sort of snow load unless the rafters are about two inches apart!) -
Thanks for the feedback. A couple of days and a few hundred dollars will get me my permit.
Has anyone ever had trusses fail to be sufficient? -
In Florida, one can most certainly fail as building codes have become more strict over the years. Homes built in the 70's for example don't meet the current wind load required of new structures. Now they don't make a home owner have to meet the new codes UNLESS your doing structural changes, which adding a few tons of solar panels clearly is. Your mileage will vary ... -
Yes, engineered mountings are now the rule here in my area. I kind of think it is a make work program because the building dept here is twiddling a lot of thumbs lately and since solar projects are about half of what they are doing - they are giving us full scrutiny. Will admit however that this has meant the discovery of two roofs so far that were weak even with out the solar addition.
It can be a real hassle though, as many roofs are difficult to quantify. The homeowner may not have the original plans (or the plans have poor or no roof loading specs on them), or the attic is sealed so you don't even know what is in there, or the steel building company farmed out their design to a guy that died 10 years ago (my case), or you have to go back to the truss company that made some complicated scissor truss. Nobody wants to be responsible for the liability involved with structural roof loading. We are adding solar systems to roofs that were not designed for it, and while the 3psf or so the solar array adds may seem pretty trivial, if for whatever reason there is a failure, it will get the blame. I've made friends with a local small time PE, willing to do minor calcs like this for $200-$400 (if I do the drawings for him), and it keeps everybody happy.