Solar Expert Posts: 122 ✭✭
I did a search and did not find the answer to my question.
I am looking at installing a 4 ton geothermal system ( I gave up on the Freewatt Plus).
The dealer is recommending a unit that will replace my air source central air and dump the extra heat in my pool during summer. During the winter the unit will heat my finished basement. The installer intends to install solar thermal panels.
As far I can tell the unit will use 3500 at draw, what I can not figure out is how much power I can expect to use during a winter day or month.
I have a 11.61kw PV system, I use about 800kw a month currently, I have two 5k sunny islands backing up a 60 amp sub panel that includes the fridge, freezer, well pump, and other necessities.
If I installed more PV would it be feasible to back up the geothermal for 24 hours?
I am looking at installing a 4 ton geothermal system ( I gave up on the Freewatt Plus).
The dealer is recommending a unit that will replace my air source central air and dump the extra heat in my pool during summer. During the winter the unit will heat my finished basement. The installer intends to install solar thermal panels.
As far I can tell the unit will use 3500 at draw, what I can not figure out is how much power I can expect to use during a winter day or month.
I have a 11.61kw PV system, I use about 800kw a month currently, I have two 5k sunny islands backing up a 60 amp sub panel that includes the fridge, freezer, well pump, and other necessities.
If I installed more PV would it be feasible to back up the geothermal for 24 hours?
Comments
-
Re: Geo Thermal off-grid
What is your location, will pulling heat out of your pool, turn it into a giant ice cube ?
Will the solar thermal panels directly heat your house, or a thermal transfer tank for the geothermal ? What about pre-heating for your domestic hot water ?Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: Geo Thermal off-grid
3500 watts sound high for a GeoThermal unit, My SEER 15 3 ton pulls 2400-2700 watts in the Florida ( Air )
Geo units should be +20 SEER or better. Also, you can't use a pool for the Sink or Source because of the chemicals, you would need an exchanger that can handle chlorine
GEO = Ground based, not swimming pool based -
Re: Geo Thermal off-grid
I was not clear in my first post, I am looking into a Geothermal unit with inground loops.
During cooling season cool refrigerant will go to my air handler, just like it does with my central air unit, the heated refrigerant returning from the air handler will dumped into a transfer tank (to be used by the pool, and possible to preheat domestic water).
During winter months the unit would only heat the basement, there would be no need for poop heating. -
Re: Geo Thermal off-grid
GeoThermal units are single units, they are not split like air based heat pumps. What your describing is a desuperheater which is used to heat hot water, again this is for air based heat pumps
everything you have described is a generic air based heatpump, not Geothermal -
Re: Geo Thermal off-grid
waterfurnace makes a split Geothermal unit. -
Re: Geo Thermal off-grid
This is really a 'ground source heat pump' (GSHP) sometimes called ground linked or ground coupled. It is not geothermal - that term refers to hot water from down below.
You can get the same de-superheater for making hot sink water with a GSHP that you can an ASHP.
GSHP can provide either warm air or warm water - whichever system you buy.
İf you are located where an ASHP (air source heat pump) will function efficiently - meaning not in North Dakota - they are far more cost effective than a GSHP. The cost of the ground loops or wells and associated piping is very significant. The additional savings offered by a GSHP over an ASHP are small while the cost differences are great.
The water loop that goes through the pipes in the ground has to be separated from the water to be consumed by a heat exchanger in all cases. The last thing you want is poor quality water going through the heat pump - it will ruin the refrigerant to water heat exchanger there.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed