Re: Measuring amps
For temporary testing purposes or permanent monitoring?
Individual panel or array measurement?
What type (if any) of meter do you have now? -
Re: Measuring amps
For quick temporary measurements a DC capable clip-on amp meter is the simplest.
For a permanent setup, a shunt, or an open loop or closed loop hall effect current sensor can be used.
A resistive shunt on negative terminal can be used but must be aware of grounding implications particularly with GFI function of controller. Putting it on positive leg is possible but must deal with the voltage potential from ground. If the meter circuit is totally isolated from ground then there is no problem.
http://store.solar-electric.com/mka-100-100.html
An open loop hall effect sensor uses the magnetic measurement of hall effect sensor in the gap of a torroid core with the feed wire going through the torroid donut hole.
http://www.allegromicro.com/en/Products/Part_Numbers/0756/index.asp
A closed loop hall effect sensor is similar to open loop but has a feedback amplifier that feeds a counter magnetic generating coil to drive the magnetic field in core to near zero. This makes the closed loop sensor more accurate since the core operates near zero net field eliminating much of the torroid core magnetic non linearities.
http://www.sypris.com/test-and-measurement/magnetics-fw-bell/closed-loop-sensors -
Re: Measuring ampsWhat's the simplest easiest way to measure amps from my solar panels with an ampmeter?
If you input is below 50A a simple panel meter works well for a visual reading. I use one of these on my setup.
http://www.newark.com/jsp/search/productdetail.jsp?CMP=ILC-1c127onlinecatalog&sku=55F5257
Partsexpress has some 30A cheap models I've used in a few projects. http://www.parts-express.com/pe/showdetl.cfm?Partnumber=320-233
More meters. http://www.parts-express.com/wizards/searchResults.cfm?srchExt=CAT&srchCat=954&CFID=13387164&CFTOKEN=84761813 -
Re: Measuring amps
I have an ohm ammeter but not sure how to use it and I can't find the
manual,. I read somewhere you have to put the + lead and the - lead on the same wire at different places and connect the + and - of the panel together but I need to make sure before I blow something up or burn my panels.
My other option would be to buy one of those clip around meters I know! -
Re: Measuring amps
Multimeter typically can only handle a maximum of 10 amps and not very well. They use separate terminals which is just a piece of calibrated shunt wire between the separate terminals.
You want an amp meter to have low resistance.
You can buy a 100 amp shunt ($24) and one of the 200 mVdc digital LCD displays for about $7. http://www.mpja.com/prodinfo.asp?number=6929+ME. You can set the decimal point position with jumpers on the DVM module. 1 mV equals 1 amp. The 3 1/2 digit meter will only give you 1 amp resolution.
If you want 0.1 amp resolution get the 4 1/2 digit DVM for about $19. http://www.mpja.com/prodinfo.asp?number=7160+ME -
Re: Measuring amps
When you measure amps, you have to "cut the wire" and bridge it with your Amp Meter (rated to carry the needed current).
If you are not sure of what you are doing, or have a lot of circuits to measure current on (temporary connections)--Look for a Clamp On Amp Meter.
There are two major types. Clamp on that can measure AC current only (transformer type coupling). Easy and pretty accurate to use.
The other major type uses a magnetic sensor (transistor) that can measure AC or DC magnetic fields. Great for use with DC--but it is not that accurate (zero will tend to drift--especially at lower current readings--also much more expensive).
Here is one for $100:
400A AC-DC AND AC/DC CLAMP METERS
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Measuring amps
Sir,
.
May I ask what device you chose to monitor your amps?
.
I have looker at the TED and the eMonitor, they do tons more than just read your amp out put but they cost tons more too......
.
As they say, you get what you pay for????
Thank you, glenn -
Re: Measuring amps
The original poster was looking at the DC side of the solar / battery system of measuring current.
The others you are taking about measure AC amps on the utility side of the system... More or less, completely different hardware and sensors.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Measuring amps
I'm got a watts up meter and love it. It's great for experimenting. i have mine wired with powerpole connectors so that I may swap it from device to device. It's a lot of bang for the buck, very portable, and just a couple ma off what my fluke meter says it should be. I have a doc watson meter on order, too.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed