System Compatibility???
Comments
-
Re: System Compatibility???SolarSteve wrote: »Thank you both for your replies. I just want to make sure I do this right.
There is a u-tube video showing the terminal boxes on the panels, located by searching Utube for "Sunforce 39126 246-Watt"
Web is http://www.youtube.com/watch?v=wFh_x8DTAjk
There are FIVE connections in the terminal box. A plus and a minus on each end, and then the 3 in the middle that go down to potted electronics (diodes?). With the parallel setup, I was required to hook the charge controller to ONE TERMINAL IN FROM THE REGULAR PLUS AND MINUS on each end of one panel.
I am still confused. I have done the minus to plus between the 2 panels. Please take a quick look at the terminal box in the video and let me know exactly where the rest of the wires should go.
Thank you so much!
Steve, I actually count 6 connections in the junction box in that video. If you're sure this is the same set up that you have on your PV panels then you don't need to worry about the middle terminals if wiring in series. In some ways you could argue that the wiring is even simpler than the parallel wiring they show, just follow Mikes directions he spelled it out quite clearly and ignore the middle terminals. -
Re: System Compatibility???
Thanks guys! I got her all wired up. Ok, I totally trust you guys, and did not use any of the middle terminals on the panels. What about all these blocking diodes, going to the center connections??
I did put a 20A fuse and holder in the positive of the lead going to the controller (output is 15A). There too, I wondered what end of the wire I should put it on. Figured I should put it by the panel end, where the power is actually coming from?
If the shed is still there when I get up tomorrow, I'll buy you guys all a few beers if you ever pass through Sebastian, Florida. (:
I'll report in tomorrow. Thanks again! -
Re: System Compatibility???SolarSteve wrote: »I did put a 20A fuse and holder in the positive of the lead going to the controller (output is 15A). There too, I wondered what end of the wire I should put it on. Figured I should put it by the panel end, where the power is actually coming from?
And, how, pray tell, will the 20 A fuse ever blow ? If your panels
have a sticker that says { 7A series fuse } , then you need a fuse that is very close to the sticker or the Isc spec of the panel.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: System Compatibility???
the fuse is inline between the cc and batteries so its purpose is to protect the wires from a short from the batteries and should be closer to the batteries. 20a should do fine in this case imho. -
Re: System Compatibility???
Everything is working great. Thank you again -all of you- for your help! It is greatly appreciated, and I could have never done it without your help.
The battery was charging nicely even with it being totally overcast this afternoon. Seemed to have noticeably more "umph" with the 2 panels wired in series. Probably only due to the MPPT controller doing it designed job with higher voltage.
I will install another fuse in the line between the battery and controller. The Morningstar CC manual calls for 25A as near the battery as possible.
Mike, in regard to your comment on the fuse size... I chose 20A because the 2 panels put out just over 7 amps each. And this fuse is in the final positive line going back to the controller. 2panels x7.15A =14.30A. So I chose a 20A fuse???
Or do I have that wrong too, because we now have the panels in series? The voltage has doubled (getting a 32-33V reading at the controller) but now the current has fallen in half? On the bottom of the spec sheet (shown below) from Sharp, it shows a "series fuse rating" of 15A. --Ok, what fuse would you suggest I install?-- I will then do so immediately this evening.
I guess here is what matters after all this...
My wife was upset that I spent so much on all this solar equipment. I know to you guys, what I have is nothing but toys. What I wanted was something for our property up North in Wisconsin. The RV is 600' from the road, and even if they were to allow a temporary power pole without a building permit, the cost was estimated by them to be approximately $5,000. So this should work nicely for one fifth that cost. I have 2 Honda eu2000i for backup.
Today my wife came home, and I just smiled and pointed at her "pride and joy," our 55' Samsung LCD TV. The solar was powering this TV and the DirecTv box and a clock with ease. My kill-a-watt showed 300 watts. I'm using a Sunforce 1000W pure sine. She looked at me with a puzzled look, and actually walked up to look behind the TV to prove to herself that it was not plugged into the wall. Sweet! Now she has a complete change of attitude, and she is PRO-SOLAR!!! (:
ABSOLUTE MAXIMUM RATINGS
Cell Poly-crystalline silicon
No.of Cells and Connections 36 in series
Open Circuit Voltage (Voc) 21.8V
Maximum Power Voltage (Vpm) 17.2V
Short Circuit Current (Isc) 7.99A
Maximum Power Current (Ipm) 7.15A
Maximum Power (Pmax)* 123W (+10%/-5%)
Module Efficiency (ηm) 12.39%
Maximum System Voltage 600VDC
Series Fuse Rating 15A -
Re: System Compatibility???SolarSteve wrote: ».......Mike, in regard to your comment on the fuse size... I chose 20A because the 2 panels put out just over 7 amps each. And this fuse is in the final positive line going back to the controller. 2panels x7.15A =14.30A. So I chose a 20A fuse???
Or do I have that wrong too, because we now have the panels in series? The voltage has doubled (getting a 32-33V reading at the controller) but now the current has fallen in half? On the bottom of the spec sheet (shown below) from Sharp, it shows a "series fuse rating" of 15A. --Ok, what fuse would you suggest I install?-- I will then do so immediately this evening.
......Short Circuit Current (Isc) 7.99A
......Series Fuse Rating 15A
I think a 10A series fuse would be fine, in a series ckt,
your amps stay the same, and I don't see why they recomend 15A over 10A. Your 2 panels at 8 amps, should never blow a 10A fuse. Or maybe 4 years of thermal stress weakens the fuse and 10A would fail, so they go up to the next size - 15.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: System Compatibility???
You really do not need a fuse for a single or two parallel strings.
The 15 amp rating is based on the ability of the solar panel wiring (and internal construction) to handle a 15 amp maximum current without overheating the wiring and causing a fire.
If there is more than 15 amps (per string--power coming from other paralleled solar panels), then the 15 amp fuses protect the "shorted string" from being over powered by the other parallel connected panels (if that run-on sentence makes sense:roll:).
The assumption for the panels is that they are the power source for short circuits--Not the charge controller.
NEC is designed around a single fault and subsequent resultant failures.
In other words, the only way that you could have a solar panel wiring failure in your setup would be if the array got a short AND the solar charge controller would also have to have an internal fault (battery to solar panel input short)--then a fuse in the solar panel wiring could protect against excess current.
But in normal day to day usage/design, that (double fault failures) is not a problem that is addressed by code.
If you have the fuse holder--put a 15 amp fuse in it. Why not.
20 amp may OK but does not meet the specifications.
10 amp fuse is getting close to where you may have a false blow years in the future--plus smaller fuses have higher resistance (fuses are small heating elements) and there is no reason to loose the extra power by having a smaller than needed fuse.
Fuses and circuit breakers are designed to be "unreliable"--so that the will eventually trip at 100% load and not trip at all at 80% load.
If you don't need the fuse--it is just one extra thing that could fail in the future.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: System Compatibility???
By the way, keep track of your power/battery usage...
300 watts is a significant load on your system and you probably can get an hour or two per day of power out couple hundred watts of solar panels to operate your big screen TV.
You don't want to kill the battery with cycling it too deeply.Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: System Compatibility???
i believe the nec wants the imp x 1.5 (or is it isc?) and then round up to the nearest commercial value. now the fuse may deteriorate some and the pvs may upon occasion put out more due to high insolation, reflection, or focusing due to edge of cloud events putting that 10a fuse as borderline. i agree that a 10a fuse could be used though if you are aware of the possibility that it may pop when you don't want it to.
for series, as was said, the current stays the same and the voltage goes up. -
Re: System Compatibility???i believe the nec wants the imp x 1.5 (or is it isc?) and then round up to the nearest commercial value. now the fuse may deteriorate some and the pvs may upon occasion put out more due to high insolation, reflection, or focusing due to edge of cloud events putting that 10a fuse as borderline. i agree that a 10a fuse could be used though if you are aware of the possibility that it may pop when you don't want it to.
for series, as was said, the current stays the same and the voltage goes up. -
Re: System Compatibility???
ok it was the isc, but that wasn't my main point here as a 10a fuse can be used. it just could pop early. going to a 10a fuse will not compromise safety. -
Re: System Compatibility???
Thanks guys! I follow what you tell me, and I do not argue. I have a fuse right at the panels in the positive lead to the controller. I have removed the 20A and installed a 15A fuse as you directed.
BUT NOW... please beat this into my head, because I still don't understand...
I have TWO solar panels in series. In series the current stays the same, but the voltage doubles. (Today it hit 40 V. on the controller). But if EACH of these panels is putting out roughly 7+ Amps, why would a 15A fuse be big enough??? On a perfect day, wouldn't I be taxing that fuse with almost or even slightly over the full 15A????
That's why initially I put in a 20A fuse. Thanks! Here is the specs again of --one of the two panels.--
Sharp ND-123 ujf 123 W
ABSOLUTE MAXIMUM RATINGS
Cell Poly-crystalline silicon
No.of Cells and Connections 36 in series
Open Circuit Voltage (Voc) 21.8V
Maximum Power Voltage (Vpm) 17.2V
Short Circuit Current (Isc) 7.99A
Maximum Power Current (Ipm) 7.15A
Maximum Power (Pmax)* 123W (+10%/-5%)
Module Efficiency (ηm) 12.39%
Maximum System Voltage 600VDC
Series Fuse Rating 15A -
Re: System Compatibility???SolarSteve wrote: »I have TWO solar panels in series. In series the current stays the same, but the voltage doubles. (Today it hit 40 V. on the controller). But if EACH of these panels is putting out roughly 7+ Amps, why would a 15A fuse be big enough??? On a perfect day, wouldn't I be taxing that fuse with almost or even slightly over the full 15A????
Sharp ND-123 ujf 123 W
Series Fuse Rating 15A
A battery is a "voltage source" and can output between 0 and 100's of amps at 12 VDC (depending on size / specifications of battery)...
A solar panel is actually a current source that reaches near Voc (Voltage Open Circuit) as soon as there is weak sunlight (morning or evening) direct sunlight on the panel...
At that point, more or less, the panel will output X amps of current--no matter if the load is Vmp (voltage maximum power) or near zero volts (into a dead short). So, solar panels naturally limit their output current to the amount of sunlight hitting the panel.
The amount of output current from the panel is pretty much proportional to the amount of sunlight hitting the panel... Near zero watts per square meter of sun light, then it will output near zero current.
When the full noon time sun hits the panel at ~1,000 watts per square meter--The panel will output around rated current. If you have a big mirror putting 2x1,000 w/sqmeter on the panel, you will get 2x rated current (assuming panel and wiring does not overheat).
So, Isc is basically the maximum current the panel will output under "full sun" at standard test conditions. Using a fuse that is around 2x Isc is picking a value that the panel will never reach in normal operation--so it should never blow in normal use.
And the copper wiring/insulation/solar panels construction is designed to handle a maximum of 15 amp of current safely (no overheating).
If the panel gets more than 15 amps (short circuit, miss-wired connections, etc.)--the Fuse will pop and (hopefully) will greatly reduce the risk of fire/electrical failure for the panel.
In your case, the two panels are in series--so the current from one panel flows through the second panel... The Varray output voltage adds because you placed the two panels in series--but the output current is still ~8 amps from each panel maximum (current does not add with series connections).
If you paralleled the connections, the voltage would not add, but the current would double--but you would place a 15 amp fuse in series with each panel--so that no failures would "back feed" a shorted panel and possibly cause it to overheat from a short circuit.
Does that make sense to you? (too many words--I know:roll:).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: System Compatibility???
Never too many words Bill! Thank you.
Ok... here's my simplistic thought/understanding, if I understand the basics of your last reply.
1. You can have more amps or you can have more volts. But not more of both, one or the other. It's your choice.
2. One gives you more quantity of electricity (amps) but the push (volts) through the wire is less, so in the end you don't get anything extra, no free lunch.
3. If you have more volts, you don't need as many amps because what there is, is coming in under greater pressure (volts).
4. SUMMATION: You can have more amps or more volts by simply wiring it different, BUT IN THE END YOU WILL HAVE THE SAME --WATTAGE-- which is what really does the work.
5. And in my situation, I have these 2 panels in series because I am gaining a slight advantage over parallel wiring because I have a MPPT controller. Correct? -
Re: System Compatibility???SolarSteve wrote: »1. You can have more amps or you can have more volts. But not more of both, one or the other. It's your choice.
Two "batteries" in series--the voltage goes up.
Two "batteries" in parallel--the current goes up.
Of course, you can do combinations (series/parallel)--but they still follow the same basic rules.2. One gives you more quantity of electricity (amps) but the push (volts) through the wire is less, so in the end you don't get anything extra, no free lunch.
The basic governing equation in this situation is:- Power = Voltage * Current
But, as you can see, nothing magic with the basic math.3. If you have more volts, you don't need as many amps because what there is, is coming in under greater pressure (volts).
The MPPT charge controllers (typically switch mode buck type power supplies with computer control) are almost like the transmission on your car...
In low gear, the engine revs at high RPM (but low torque of the motor) to low RPM / High torque of the tires...
Or in high gear, the wheels turn faster (because you are now going 70 MPH), but the torque to the tires is less (you have to down shift to go up hill).
Same amount of Horse Power from the engine--just adjusting the RPM/Torque to the requirements of the load (speed and drag).
If you are familiar with Variacs (variable/adjustible AC transformers)--the MPPT controllers are, sort of, the DC version of the AC transformer.
They both can take high voltage/low current and "down convert" to low voltage/high current... Still the same amount of power (100 watts in, roughly 100 watts out).4. SUMMATION: You can have more amps or more volts by simply wiring it different, BUT IN THE END YOU WILL HAVE THE SAME --WATTAGE-- which is what really does the work.
It is very difficult to send significant amounts of energy at 12 volts any more than 10-20 feet or so.
Your house wiring is 120/240 volts and you can send the same power (1/10 or 1/20th the current) hundreds of feet.
Or your electrical company will have 12,000-24,000 volts on the poles in your neighborhood so they can send the power 1,000's of feet.
etc...5. And in my situation, I have these 2 panels in series because I am gaining a slight advantage over parallel wiring because I have a MPPT controller. Correct?- High array voltage allows you to use smaller wire and/or send your power longer distances (array to controller/battery bank) more efficiently and without spending a ton of $$$ for heavy copper cables.
- A second effect is that solar panels in hot weather actually have their output voltage depressed (maybe 20% or so)--Very hot batteries and very cool batteries, and your panels may not output full current to your batteries. Your setup with the high Varray voltage completely bypasses that issue.
- Lastly, you will see claims that MPPT controllers can give you 25-30% more power--Sort of yes--If your in a very cold (way below freezing) environment. Cold solar panel output voltage rises and the MPPT controller can convert that extra higher voltage into more current for charging your battery bank..
However, the first two reasons are more than enough reason (usually) to justify the extra costs when building out a larger system.
Also, MPPT charge controllers tend to be more expensive (and newer designs), so you will see more bells and whistles (networking, data logging, programmable charging options, etc.). Sometimes very nice options to have.
Under 200 watts, think about PWM controllers (less expensive and may be more efficient).
Over 400-800 watts, probably MPPT will be the better choice.
In between--"it depends" on your needs and wallet... :roll:
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: System Compatibility???
Excellent Bill! Thank you. It really means a lot to me to have the ability to learn from guys like you and the others who are helping. Thank you to all of you!
Now... since I've shown my stupidity on even the basics, I might as well keep going.
So... if I understand you right, I am currently -not- maxing out my Morningstar SS-MPPT-15L charge controller (15A limit) because I have my 2 panels in -series-, so therefore I could actually run/add ANOTHER set of the same panels again in series, where only then would I be up to the 15A limit????
From my prior posts you'll remember I had asked how to wire the 2 panels in series, confused by all the connections on each panel. Tell me... there must be some practical use for all the other connections that go to all the potted diodes, etc. Each panel has SIX connections. Now we're just using the plain end terminals that don't attach to any diodes. I've tried to study a bit, and some may be bypass diodes that would help if any part of one of the panels got shaded. There's lots of trees up on my property, and I know early morning and late afternoon will unfortunately have abundant shading. Shouldn't we be taking advantage of some or all of those diodes??? -
Re: System Compatibility???SolarSteve wrote: »Excellent Bill! Thank you.
By asking the questions and documenting your system--You also help the next person too.So... if I understand you right, I am currently -not- maxing out my Morningstar SS-MPPT-15L charge controller (15A limit) because I have my 2 panels in -series-, so therefore I could actually run/add ANOTHER set of the same panels again in series, where only then would I be up to the 15A limit????
It is Vmax/Vmin and issues around input current (too much, need an input fuse; too little and you waste power/money).
Voc (voltage open circuit) or the maximum input voltage from a cold solar array becomes the issue with placing panels in series...
The MS 15 amp MPPT controller has a Voc limit of 75 volts... Assuming you are in Florida and your cold days are not very low... For your panels (using the Xantrex Calculator) for a 20 F day, the maximum series Voc for 3x panels is 73 volts.
Getting pretty close to the 75 volts maximum. It is not a very expensive charge controller if you ever had a cold snap and fried the controller--MorningStar does not replace over voltaged controllers. Perhaps you should call them and confirm that 3x panels in series for your area is a good idea or not.
You are now looking at ~369 watts on a 15 amp MPPT controller charging a 12 volt battery bank (correct?). You are about 20-30% larger than the 15 amp controller can manage--so it will spend significant amount of time with more power than it knows what to do with.
Personally, I would think it is not a good use of your money... A second controller or a higher rated controller might be a better choice.
Part of the decision will be your eventual plans (never more than 3 panels, etc.).From my prior posts you'll remember I had asked how to wire the 2 panels in series, confused by all the connections on each panel. Tell me... there must be some practical use for all the other connections that go to all the potted diodes, etc. Each panel has SIX connections. Now we're just using the plain end terminals that don't attach to any diodes. I've tried to study a bit, and some may be bypass diodes that would help if any part of one of the panels got shaded. There's lots of trees up on my property, and I know early morning and late afternoon will unfortunately have abundant shading. Shouldn't we be taking advantage of some or all of those diodes???
The fact that the string will still pass some useful current if one panel is partially shaded is an advantage for two panels in series vs two panels in parallel.
For your needs, these extra connections are not going to do a thing for you.
Some panels, this allows a person to replace the bypass diodes if there is damage--but hopefully you never need to do this.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: System Compatibility???
Ok Bill, this one I understand. Stick to just the 2 panels I have with the controller I'm using with my 12V bank (3 deep cycle Grp.27 marine).
I'm having -great fun- learning and setting up my first ever solar system! Even if it is just to watch my big 55" Sammy for about 3 hours a day. I ordered just the low cost Morningstar Remote Panel RM-1 ($75), so I can keep track of when to shut it down from inside the house instead of having to run out to my shed. For up north, my basic system will be put to more practical and modest use!
What voltage on the meter would you personally turn off the inverter at for reasonable battery life?
Have a Great Weekend! -
Re: System Compatibility???
There is no really right or wrong answer (at least as defined by me)--Just what makes best sense towards meeting your needs.
What voltage to turn off the inverter--Actually that is not an easy answer. Battery voltage as a measurement of state of charge is only accurate after the battery has sat for a few hours (no charging or discharging current).
A battery monitor would be a better tool... But if you are limited to what you have on hand, you can start with 11.5 volts or so and see how that works for you.
You can estimate the power and simply time your TV time... For example, say you have a 300 watt 120 VAC load, on a 85% efficient inverter, with a 225 AH 12 volt battery bank, and you want to run it to ~50% of rated AH capacity (good cycle life for battery)... The amount of time to run the system would be:- 225 AH * 12 volts * 0.50 max discharge / (300 watts * 1/0.85 inverter eff) = 4 hours of run time
It is probably going to take your solar panels ~2 days to fully recharge the battery bank back to 100% after that 4 hours of use in average sunny weather...
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed