Battery bank vs. PV input
![NZRR](https://w0.vanillicon.com/055e007b96f86a569dcd7dcade8977f7_100.png)
NZRR
Registered Users Posts: 28 ✭✭
Is there an easy way to determine the balance between the battery bank size and the PV production? As an example, I will shortly have 3720 watts of PV on my roof, and 900 AH of battery capacity. My main concern is being able to completely charge the batteries with a day or two of sun, and not have to use the generator. Any suggestions would be appreciated.
Comments
-
Re: Battery bank vs. PV input
Voltage of your system? -
Re: Battery bank vs. PV input
Fire ! Ready ! Aim!Is there an easy way to determine the balance between the battery bank size and the PV production? As an example, I will shortly have 3720 watts of PV on my roof, and 900 AH of battery capacity. My main concern is being able to completely charge the batteries with a day or two of sun, and not have to use the generator. Any suggestions would be appreciated.
Your charging amps, should be about 10% of your battery amps, so if you have 900A of battery, you need 90A of charging. That keeps current limit below plate warping heat, and still enough amps to stir / bubble electrolyte in the EQ cycle.
What you haven't told us, is the battery voltage, and the array voltage, if all batteries are in series, or parallel, or series-parallel combo. What is your charge controller, and how cold in winter, and hot in summer . Those all affect the PV voltage and how to set it up with the charge controller.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: Battery bank vs. PV input
Basic, "starting point" formula used for off-grid:
Battery Amp/hrs ('20 hr rate') * 10% = Target Charging Current
TCC * charge Voltage = effective array Watts needed
Watts / system efficiency (typically 80%) = total array size
Without the system Voltage, this is as close as anyone can come to an answer. -
Re: Battery bank vs. PV input
My system voltage is 48. I have an Apollo T80HV and the batteries will be two banks of 8 Rolls S600s connected in parallel (450 Ah for each bank). I am using UniSolar PVL-124s, three in series for 90 volts, with 10 arrays, which should generate up to 40 amps. It gets to around 86 degrees on average in the summer, and to maximum -32 degrees (F) in the winter. Thanks for the input. -
Re: Battery bank vs. PV input
This thread had good discussion from the opposite imbalance. If you two were neighbors solar perfection would be within reach.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed