C60 Controller

My system comprises 6 Kyocera 120 watt solar panels wired for 24V, an Xantrex C40 Controller, 8 x 6 volt Surrette batteries, 700AH at 24V and an Xantrex 4024 Inverter. I have a brand new spare C60 Controller. If, as and when my C40 Controller fails can I safely use the C60 in my system?
Thanks, Lone Ranger

Comments

  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Re: C60 Controller

    I don't know - you may have to add 4 more panels.
    Oh wait, you COULD add more panels.
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • crewzer
    crewzer Registered Users, Solar Expert Posts: 1,832 ✭✭✭✭
    Re: C60 Controller

    The KC120's STC Voc is 21.5 V, so two in series would be 43.0 V. Allowing for the NEC's 125% temp correction factor for fairly cold climates (down to -40 F / -40 C), your array's early morning Voc somewhere in Ontario, Canada, could well be 43.0 V x 125% = 53.75 V. This is very close to the C60's max input voltage spec of 55 V, so you'll need to give that some consideration, especially if you factor in reasonable performance tolerances (+/- 5%? 10%?)

    See: http://www.xantrex.com/web/id/72/p/253/pt/25/product.asp

    Otherwise, the C60 PWM controller is rated for both 12 V and 24 V systems and should work satisfactorily. However, it's not an MPPT controller, and your array is large enough (720 W STC) that your system would probably benefit from this feature, especially in the winter.

    HTH,
    Jim / crewzer