I was shocked because I was under the impression it would draw 1100 watts. My new array runs it just fine. I thought I would be able to run my 2000/1600 watt generator with it. I as it climbs up over 1600 watts it causes my genny to stumble. A friend runs her 1 ton unit off a Honda 2000 genny but she has a different 1 ton unit. Must be more efficient.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
littleharbor2 said:I was shocked because I was under the impression it would draw 1100 watts. My new array runs it just fine. I thought I would be able to run my 2000/1600 watt generator with it. I as it climbs up over 1600 watts it causes my genny to stumble. A friend runs her 1 ton unit off a Honda 2000 genny but she has a different 1 ton unit. Must be more efficient.
Next year if I find the right minisplit. What brand does your friend have?
Off Grid. Two systems: 1) 2925w panels, OB VFXR3648, FM80, FNDC, Victron BMV-712, Mate3s, 240 xformer, four SimpliPHI 3.8; 2) 780w, Morningstar 30a, Grundfos switch, controller and AC/DC pump, 8 T105. Honda EU7000is w/AGS. Champion 3100. HF 4550, Miller Bobcat. -
JRHill said:littleharbor2 said:I was shocked because I was under the impression it would draw 1100 watts. My new array runs it just fine. I thought I would be able to run my 2000/1600 watt generator with it. I as it climbs up over 1600 watts it causes my genny to stumble. A friend runs her 1 ton unit off a Honda 2000 genny but she has a different 1 ton unit. Must be more efficient.
Next year if I find the right minisplit. What brand does your friend have?2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
littleharbor2 said:Well, I was shocked just now. Not with voltage, with the current reading of my minisplit. It is pulling 14.6x amps @115 vac, 1660+ watts
I hope so because with 110+F outside and 90+F water temp the only relief left is an underground bunker where you most likely would find that 90+F water again.
Thanks for the comparison. -
Those portable A/C units are the worst. What the engineers decided to do with those is bring the noisy part of the A/C and park it next to your La-Z-Boy and make it so that 50% of the air that you just cooled gets sucked back out the window so you get to cool it again.
If Rube Goldberg were alive he would applaud. -
Remember the issue with measuring AC Voltage and Current...
AC Power = Voltage * Current * Power Factor (shape of waveform--Example of current "peaks" vs purse sine wave)
AC power = Voltage * Current * Cosine of the phase angle between Voltage and Current
And there is VA (volt*amps)
VA = Voltage * Current
For transformers, AC inverters, Residential Generators, Wiring, etc.--VA is the Number needed to size the system.More or less, VA=Watts for sizing.
For Commercial systems (and some other specialized systems), there can be an 80% fudge factor--I.e., VA * 0.80 PF = Watts
When working with solar harvest (in Watts) and generator fuel usage (i.e., gallons per hour, etc.), more or less those numbers depend on the Watts (not VA) numbers.
It is relatively easy to measure Voltage and Current separately (Digital Multi-Meter, Current Clamp meter, etc.). If the voltage and current wave forms are "sine wave", "cheap" DMMs can give "accurate" numbers (they "assume" sine waves).
For non-sine voltage and current wave forms, then need "better meters" with True-RMS (root mean square) capability. These meters calculate the proper voltage and current values for arbitrary wave forms.
https://www.fluke.com/en-us/learn/blog/electrical/what-is-true-rms
To measure actual power, then you need a meter than does True-RMS and measures both the wave form, and the phase angle between V and A.
A kill-a-Watt meter can do a "decent job" of giving Watts.
~15 years ago (2008), somebody compared a Kill-a-Watt ($20 at the time) to a Fluke power meter ($2,000 at the time).
https://forums.anandtech.com/threads/kill-a-watt-power-meter-accuracy.137169/
You get what you pay for... But even lab grade power meters can have their issues too giving accurate/consistent with other meters results..
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
SteveK said:littleharbor2 said:Well, I was shocked just now. Not with voltage, with the current reading of my minisplit. It is pulling 14.6x amps @115 vac, 1660+ watts
I hope so because with 110+F outside and 90+F water temp the only relief left is an underground bunker where you most likely would find that 90+F water again.
Thanks for the comparison.I used a true rms clamp meter and watched the current rise over about 3 - 4 minutes to the peak I mentioned. I ended up settling down to the 12.xx amp range.
This is an inverter type unit and it is 110 volts, not 220.2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
littleharbor2 said:This is an inverter type unit and it is 110 volts, not 220.
-
BB. said:Remember the issue with measuring AC Voltage and Current...
AC Power = Voltage * Current * Power Factor (shape of waveform--Example of current "peaks" vs purse sine wave)
AC power = Voltage * Current * Cosine of the phase angle between Voltage and Current
And there is VA (volt*amps)
VA = Voltage * Current
For transformers, AC inverters, Residential Generators, Wiring, etc.--VA is the Number needed to size the system.More or less, VA=Watts for sizing.
For Commercial systems (and some other specialized systems), there can be an 80% fudge factor--I.e., VA * 0.80 PF = Watts
When working with solar harvest (in Watts) and generator fuel usage (i.e., gallons per hour, etc.), more or less those numbers depend on the Watts (not VA) numbers.
It is relatively easy to measure Voltage and Current separately (Digital Multi-Meter, Current Clamp meter, etc.). If the voltage and current wave forms are "sine wave", "cheap" DMMs can give "accurate" numbers (they "assume" sine waves).
For non-sine voltage and current wave forms, then need "better meters" with True-RMS (root mean square) capability. These meters calculate the proper voltage and current values for arbitrary wave forms.
https://www.fluke.com/en-us/learn/blog/electrical/what-is-true-rms
To measure actual power, then you need a meter than does True-RMS and measures both the wave form, and the phase angle between V and A.
A kill-a-Watt meter can do a "decent job" of giving Watts.
~15 years ago (2008), somebody compared a Kill-a-Watt ($20 at the time) to a Fluke power meter ($2,000 at the time).
https://forums.anandtech.com/threads/kill-a-watt-power-meter-accuracy.137169/
You get what you pay for... But even lab grade power meters can have their issues too giving accurate/consistent with other meters results..
-Bill
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed