Safety Switch?
jACKr
Registered Users Posts: 16 ✭✭
Aloha! I'm hoping to set up a safety switch that cuts power from a small array of 2 REC 320s in series. Before it gets to a Combiner. This is a temporary scenario while I put on a new roof where my main PV lives, and use the REC320s while the other roof array is off line.
I have a small Breaker Panel that's unused. I'm wondering if anyone has ever used a Breaker as a Switch to cut DC power? If its doable? And, any caveats?
In Advance! Thanks!
jACKr
I have a small Breaker Panel that's unused. I'm wondering if anyone has ever used a Breaker as a Switch to cut DC power? If its doable? And, any caveats?
In Advance! Thanks!
jACKr
Comments
-
jACKr said:I have a small Breaker Panel that's unused. I'm wondering if anyone has ever used a Breaker as a Switch to cut DC power? If its doable? And, any caveats?
Available here and elsewhere, Some are polarized requiring them to have the flow in a certain direction.
Most common are Midnightt's Din rail breakers;
Midnite Solar MNEPV 150 Volts 15 Amps DC Circuit Breaker | Northern Arizona Wind & Sun (solar-electric.com)
DC breakers are typically magnetized to help interrupt DC's stead flow.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
For temporary you could use the breaker panel. If they are AC breakers they will work for awhile. You should then discard the breaker you use as DC will ruin an AC breaker over time. For 2 panels in series (about 80vdc guess) you could just use a switch from an auto store for awhile. Look for a Knife switch as a cheap and decent solution.
You really should get away from this and use the correct voltage rated DC voltage circuit breaker. Since the current is low for this solar application, most any amperage of a correctly rated 125 to 150 vdc breaker is what you want. It is just a switch and over current protection is not needed unless you have more than 2 strings of panels. You have one string here.
Alooooh haaaa !"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Aloha! I abandoned the Breaker option as a Temp safety switch.
There's no DC breakers available for the GE box I have.
I went to a real Safety Switch. But, I'm perplexed by what is hobbling me from success.
My PV array string of 2 REC 320s in series meters to the switch, but not thru the New 30amp fuse. I can meter the 72vdc In, with switch Off. But, not with switch in On position. It's apparently blocked at 30amp fuse? I've repeated it, and its confirmed, the PV voltage does not pass thru switch fuse to downstream wire to MX60, when in On position?
I'm wondering is there's a special fuse (solar?), or does the switch require a chassis ground? My Ground side, bypasses and is bussed at the combiner.
There's a work around, but I hope not to circumvent the Safety Switch.
Anyone, familiar with this scenario?
Thank You! -
Just to be clear--When you mean "Safety Switch", you are talking about over current protection such as a circuit breaker or fuse?
Typical Fuses and Circuit Breakers are just as they seem. When "on", they pass current (and voltage) across them. When "off" (or tripped), they are an "open circuit" and no current or voltage will pass through them.
Assuming these are your panels:
https://d140hlzzaoq16w.cloudfront.net/media/sparsh/product_attachment/custom/upload/REC-N-Peak-solar-panel-datasheet.pdf
The recommended series fuse/circuit breaker is 25 amps, not 30 amps.
The thing that is "special" about solar fuses/breakers/switches is that they are rated for DC Current/Voltage (and you need them to be rated, at least, for the maximum circuit voltage--Or ~80 VDC minimum in your case).
DC current is much more difficult to "stop" vs AC current... DC current sustains arcs really well, and DC breakers/fuses/switches are usually heavier duty than a similar AC version (i.e., you find that AC voltage rating is typically much higher than the DC rating for the same switch).
https://www.youtube.com/watch?v=Zez2r1RPpWY
When measuring the voltage... Where/how are you measuring? If you are measuring "across" the two terminals of the fuse//breaker, then with the switch open, you should see voltage (if the solar panels are in sunlight), and with the switch closed (turned on), you will not see any voltage... While the measurement is "valid", you may not be using the meter leads correctly(?). You want to measure the voltage across the panel + and - leads (in sunlight).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Aloha Bill, My Safety Switch has a single purpose. To disconnect the string 72vdc (2 series panels) completely when working at the Outback combiner. I don't really need the fuses the switch uses. The Combiner does that task. I'm likely to bridge where fuses would be. And simply use the disconnect via Switch Handle. That's all I really need. Make sense?
Mahalo, jACKr -
More or less... The combiner boxes come in both Fused and Breaker (aka switching breakers)... You only need "one safety device" (over current for three or more parallel panel strings--Or one "switch" per string (aka a combiner box type) or one switch for all--Your choice). Two safety devices (such as one fuse followed by one breaker) is overkill--And can lead to confusion down the road (was it the fuse or the breaker that opened, etc.).
Having a set of "switches" (one per parallel string) is nice for debugging (i.e., is one string not working... Can switch off one at a time and see if the current goes down; working. Or if the current from the one string having low or zero amps.
Breaker based combiner box:
https://www.solar-electric.com/mnpv3.html
Touch Safe fuse hold type:
https://www.solar-electric.com/misomnsoarco3.html
Note: Do not pop the fuse holder(s) out when the unit is under power... The holders can and will arc if they are popped open under load (see YouTube video above).
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed