Lightning strike blew battery caps off
Lighting storm…. Two panel circuits with multiple Midnight Solar SPDs on both. One is ground mount and SPDs are lit so good. A smaller set of panels facing West on the roof and both SPDs are blown.
48v battery bank with 3 of the caps blown off so hard that the plastic battery necks are ripped off the Rolls 5000 series batteries with plastic neck pieces blown 8’ away. Acid fumes rolling out of 2 of the cells so garage is full of fumes.
Both charge controllers and inverter look good on Conext SCP. Battery v is @ 58.4v so I don’t think I shorted any plates.
what the hell just happened?
Both charge controllers and inverter look good on Conext SCP. Battery v is @ 58.4v so I don’t think I shorted any plates.
what the hell just happened?
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
Comments
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
Our founder of the forum (Wind-Sun... Retired) once said that he saw (on average) more AC inverter outputs blown by lighting (and nearby strikes?) vs the DC side of the system--My two cents was the battery bank offered pretty good surge suppression.
Checked electrolyte levels?
If you have an IR heat gun--Might check the battery/cell temperatures to see if anything untold is happening (internal shorts, heat generated by charging/discharging current flow, etc.).
Electronic devices (diodes, transistors, etc.) are sensitive to over voltage (even static electric charges)--And if they don't fail right away, they can have an early life failure.
For the equipment... Just continue to run until something breakers (if it breaks). =
Might look into your spares/backup plans... You have grid--So that just may be the ability to bypass the main AC inverter with grid power until the inverter gets repaired (etc.).
-Bill
Firstly, lead acid gives out HYDROGEN, and hydrogen is very explosive.
Secondly, hydrogen gas can be absorbed by spider webs, organic string and the like, and a couple of times the main 250 amp battery to Inverter Midnite/Outback breaker that was also in with the open covered battery shed, when operated the brief instant surge illuminated all the spider webs in the building, very impressive but also very worrying.
Thirdly, I have seen on still Autumn evenings just after the sun has set Blue balls, the size of a soccer ball, of gently glowing gas riseing from the battery sheds and just hovering about 12 meters from the ground. I call them the BLUE MEANIES.
So, i now insist that the lead acid batteries are always kept in there own speicial well ventilated shed and with no switch gear in that shed/building.
For you, I suspect that the lightning in that brief instant discharged all over the place and any hydrogen anywhere would instantly ignite, and hay presto blow off your battery Miser caps. And as long as the battery cases are good then there should be no issues, as the miser caps were the weak spot and took the hit.
I have also seen, during a thunder storm an electric cattle fence, about 50 yards away, start shorting out about a minute before a ground strike, with large sparks from the fence wire hitting the ground as the surrounding air starts to ionize charge, then BANG, everything back to normal. Again a suspect during certain Meto conditions the lightining strike around or near your batteries would begin ionization of the air, so hence those miser caps allowing the air inside them to ionize and except an electrical charge.
So always allow that hydrogen to get away.
Everything is possible, just give me Time.
The OzInverter man. Normandy France.
3off Hugh P's 3.7m dia wind turbines, (12 years running). ... 5kW PV on 3 Trackers, (8 years) .... 14kW PV AC coupled using Used/second hand GTI's, on my OzInverter created Grid, and back charging with the AC Coupling and OzInverter to my 48v 1300ah batteries.
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
Interesting idea about hydrogen gasses igniting inside the cells blowing the caps off. The damage I see and the hydrogen gas coming out of a few cells match your explanation
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
How close were the strikes? Good Luck !
htps://offgridsolar1.com/
E-mail [email protected]
One of the battery cells blew the top so I will call Surette tomorrow and see if I can order just the one cell instead of having to buy a very expensive battery. But that 3 cell battery is reading 6.34 V so I guess in a pinch I could use it for testing but I may just hold off until I get the battery fixed.
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
The thing you are looking for inside XW is small black pieces of MOSFET.
htps://offgridsolar1.com/
E-mail [email protected]
htps://offgridsolar1.com/
E-mail [email protected]
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
The no load start showed no problems except that the controller was throwing a code 71 (high v) which would be expected after lightning in the system. Since i’ve learned that quite often controller codes do not go away until they get Sunshine the next day for the moment I’m ignoring that code and praying that when I do a soft start on Saturday they charge controller will function correctly for a 42V battery bank.
I then switched from grid power to solar power pulling 1Kw with good results and no unusual odors.
For now the entire system is shut down and we are running grid power only. I hope to play more with it on Saturday to catch a gentle power Increase on the panels.
Wish me luck!
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
dsl line
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
Maybe a capacitor in the charge controller holding a charge?
I spoke with the battery distributor and they are going to see about getting me a single 2v cell for the blown battery. The distributor said they had shipped single cells before.
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
You have probably thought of this, or, already done it, but, as you know the Surrette 5000-series batteries have each cell of the battery bolted together.
It is fairly "easy", to carefully unbolt the blown up cell, remove it, and jumper between the neighboring cells of your 6V battery, to create, a 46 V battery. This should give you more DC voltage operating range.
It is probably best to ask for a replacement cell to be shipped, Dry, unless the battery distributor can have a wet cell shipped, strapped to other batteries on a pallet of similar batteries.
The Jars of these batteries are thin, so, dry is often best, and you can Activate the dry cell, fairly easily.
FWIW, Good Luck! Vic
Vic, I already have the bad cell Unbolted from the other cells with a nylon strap slung so when someone comes over to help me we can drag the 110 pound beast out of that hole. At that time I may move the two outer cells together and create the 46 V battery bank you suggested.
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
I ordered a single replacement cell instead of a complete 6v battery partially to minimize the price and partially to avoid the weight of dealing with a 345 lb battery which was a chore to install 4 years ago.
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
there is no way to get under the cell so that is not a viable option. We will give it it a good old heave ho tomorrow night and will see
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
A picture of my battery box is in post #27 of this thread. Cooling the batteries — northernarizona-windandsun (solar-electric.com)
As you can see the box is water tight to allow me to cool the batteries down in the hot garage. I'd rather lift a single 115 lb cell than the entire 340 lb battery out of the box.
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
Gotta love the wide programming range Schneider equipment has.
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P