Question about my mppt app statistics
bgu1982
Registered Users Posts: 73 ✭✭
I have a question. On my Bluetooth app for my mppt controller ,for instance, the SOC says 75% but the battery voltage says 12.7v. I thought a reading of 12.7v for FLA batteries is a full charge. Sorry if this is a stupid question but I'm concerned because I don't want to go below %50 dod. I'm using chargepro 2.0 app. Other than that everything seems to be working great.
Comments
-
I guess I never reprinted my battery charging info, see if this helps;The voltage you are seeing is the system voltage and not the battery voltage. If you are connected to charging or a load it will effect the system voltage.During charging, there are basically 3 stages of charging, Bulk, Absorb, and Float.BULK;First thing when charging starts you will be in bulk, the voltage rises from what ever the system voltage was to a set point, around 14.5 volts. At that point the Charge controller stops the voltage from rising. Higher voltage can damage sealed batteries.ABSORB;Once the battery hits the preset point the charge controller keeps it at that point. Your batteries are roughly 80% full. Flooded batteries will start accepting less current at 80-85% full AGM/Sealed may go a little longer before accepting less current.On many controllers you can set this point, Some will have different presets for Flooded, and sealed batteries, or flooded, AGM, and sealed batteries.The charge controller has a couple ways to know when to switch to float, Most inexpensive Charge controller are just timed for 1.5-2 hours. Some will also see less current flowing through the charge controller and shut it down when minimal current is flowing through the controller. On more expensive charge controller. You can set battery capacity to give the Controller a better idea of when to stop. you can also set a longer Absorb time. Or set 'end amps' a amount of amps flowing through the charge controller to stop Absorb and switch to the final stage.FLOAT;Once the Controller has determined the battery is fully charged it reduces the voltage to a point where very little current is flowing to the battery. This will prevent the battery from over charging and heating up.While in 'Float' the charge controller watch for voltage drop, which would indicate a load. If the voltage begins to drop the charge controller will allow as much current to flow from the panels/array to compensate and maintain the voltage. If the voltage can be maintained, the load will in essence be running directly off the array/solar. If the voltage drops below the preset float voltage, the controller may start a whole new cycle if it stays there for a period of time.The system voltage drop you see at night when the sun goes down is the charge controller moving into a resting mode with no energy to contribute to the system.The morning voltage may reflect a load present that is effecting the voltage level. With sealed batteries, you would want to disconnect the battery from the system and allow it to 'rest' for a while to get an accurate idea of it's SOC (State Of Charge) from the voltageHome system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Oh I think I see what your saying. At night time when there's no power coming in from the panels the batteries need to sit awhile with no load to get a accurate SOC reading. So what I'm seeing under load at night is more of an approximation.
-
bgu1982 said:Oh I think I see what your saying. At night time when there's no power coming in from the panels the batteries need to sit awhile with no load to get a accurate SOC reading. So what I'm seeing under load at night is more of an approximation.
I'm lazy and working this out for 6 - 8 volt 5 year old batteries that I've replaced my 12 year old forklift battery with, hoping I can see reduce price on LiFePo4 batteries that are UL1741 for home use as competition increases. I paid about 60% more than scrap for them but I knew the previous owner and they were well maintained and lightly cycled. They are also Trojan which is a premium battery.
I've not yet done a commissioning equalizing, it's been too hot. I'll check the SG and record after I do. So, understand roughly what I've pulled from the battery bank and knowing the rough capacity if new (170 ah x 2 strings for 340 ah at 24 volts or about 8,000 watt hours). I can rough out my energy use, about 1000 watt hours for my 20 year old fridge and around 2000 watt hours from my air conditioner running 3-4 hours as and another couple hours through the night. Add another 500 watt hours for laptop, lights, fan and inverter use. I should be around 50% or just above.
So, checking the battery in the morning before I get effective charging in the morning and finding the battery at 24.6 I was quite happy. representing about a 70% full battery with loads equaling the charging both minimal <100 watts. The batteries are warm, this is damaging but also adds some capacity. It reminded me to move my battery temperature sensor over the new/used battery bank.
It's certainly a touchy-feely way to figure battery capacity. Your charge controller might be more or less accurate... It's using voltage too! and information you have given it. Unless you have a Midnite Classic with a WhizBang Jr to measure input and output of amps into the battery bank, I think Schneider has a similar system and Outback reads the use of everything and input to system shouldn't be as accurate. They guys who designed the Outback system abandoned it when they made the Midnite classic.
Clear as mud?Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed