Switching to a compressor type Refer…

My truck camper is now up to 560w mppt solar and with two 200a/hr LFP batteries…Considering swapping out our 6 c/f Norcold refer with a 8.1 c/f Danfoss-Secop compressor-type refer rated nominally at 5.23 amps (so say, 125a/hrs over a 24 hr period)…Harvest under ‘ideal conditions’ might even be around 34-35 amps, but (per BattleBorn estimates) about a 3.75 amp hourly average over an 8hr harvest period, per each 100w panel, thus 168 net averaged recovered a/hrs…
Question here is, just wondering what experiences others might have had when using a compressor type refer??
Question here is, just wondering what experiences others might have had when using a compressor type refer??
Thanks, Bunkysdad
Comments
What you really want to know is how many Watt*Hours or Amp*Hour (@ 12 or 24 volts) uses per day.
https://norcold.com/product/norcold-nrf-60-portable-refrigerator/ (???)
For example, say the fridge (compressor type) uses 5.3 Amp*Hours and guess that it has a 50% duty cycle in "normal" operation:
- 5.3 AH * 24 hours per day * 0.50 duty cycle = 63.6 AH per day (guess)
- 63.6 AH per day * 12 volts = 763 WH per day
For a small DC refrigerator, 763 WH per day (guess) is a fair amount of energy usage... 500-250 Watt*Hour per day would be "nicer" (could not find ratings with quick search--A full size home Energy Star Fridge can be found around 1,000-1,200 WH per day... A converted freezer to fridge can get down towards 250 WH per day).For your setup, guessing Carson City Nevada, fixed array, mounted flat to roof:
http://www.solarelectricityhandbook.com/solar-irradiance.html
Carson City
Measured in kWh/m2/day onto a horizontal surface:Average Solar Insolation figures
- 560 Watt array * 0.77 off grid DC Li Ion system * 3.15 Hours of sun per day = 1,358 WH per day (February "break even")
- 1,358 WH per day harvest / 12 volt battery bank = 113 AH per day
Lots of guesses here... But having a 24x7 base load that must run (fridge), using 50-65% of predicted harvest is "comfortable" (don't need to run a genset every few days to keep up with occasional cloudy sky).- 1358 WH per day * 0.65 "base load fudge factor" = 882.7 WH per day for "base loads"
Using a Kill-a-Watt type meter for AC loads, and/or a DC AH/WH meter for DC loads. Measure the energy usage to be sure.https://www.amazon.com/s?k=dc+digital+amp+volt+energy+meter&crid=25P8P1GNKJVVX
Also, ventilation around the fridge is important... Above 85F ambient, many refrigerator/freezers tend to "have issues". And they also take more energy to cool.
Your thoughts?
-Bill
please clarify…
I am assuming the Li Ion batteries are pretty much 100% efficient. The 0.77 is the derating of the solar panels and charge controller efficiency.
- 0.81 panel derating (hot panels, Vmp falls and MPPT output drops or using PWM controller) * 0.95 charge controller efficiency = 0.77 overall efficiency
More or less, the "marketing" numbers for Vmp and Pmp are when the solar cells are at ~25C/77F and tested under a flash simulated sun (to keep cells "cool" and near room temperature).On a hot summer day under full sun, the cells can be upwards 40C over ambient.
MPPT (maximum power point tracking) charge controllers basically follow the equation:
- Power to Battery = Vmp * Imp * 0.95 controller efficiency
PWM (pulse width modulated) charge controllers basically take just the Imp of the solar panel and passes it to the battery. Example of a 100 Watt solar panel (to keep numbers simple):https://www.solar-electric.com/solarland-slp100-12u-100-watt-12-volt-solar-panel.html
Maximum power (Pmax): 100 WattsNominal voltage: 12 Volts DCVoltage at Pmax (Vmp): 17.2 Volts DCCurrent at Pmax (Imp): 5.81 Amps DCOpen-circuit voltage (Voc): 21.6 Volts DCShort-circuit current (Isc): 6.46 Amps DCPower tolerance: +/- 5%
As long as Vmp is over Vbatt--Then Imp (current from solar panel) is passed to battery:
- 5.81 Amps Imp * 14.5 volts charging = 84 Watts
- 84 Watts actual / 100 Watts Pmp = 0.84 "derating" for panels
- 0.84 panel derating (on PWM) * 0.95 Controller eff = 0.80 over all system eff
So, ignoring Imp (which rises a small amount at higher cell temperatures) and overall just to keep things "simple", I use 0.77 as the overall panel+controller deratings for both MPPT and PWM type controllers (close enough for solar).-Bill
Feel free to ask more questions as they come up.
Take care,
-Bill