Need to replace my 48V FLA battery bank - should I change technologies?
Riley
Registered Users Posts: 67 ✭✭
I have am off-grid seasonal home. Used mainly in the spring/summer... some fall and one visit in winter.
3.5 KW of panels and a 12 KW generator. 6KW inverter/charger.
My system used Rolls L16 6V (S-550) batteries to provide 48VDC with 8 battery packs.
I was just going to replace with the same but wondering if things have changed.
What about carbon/lead?
I should say that in the wintertime, they are left fully charged and disconnected when I am not there for months at a time.
They do get cold (-15C)
Thoughts?
3.5 KW of panels and a 12 KW generator. 6KW inverter/charger.
My system used Rolls L16 6V (S-550) batteries to provide 48VDC with 8 battery packs.
I was just going to replace with the same but wondering if things have changed.
What about carbon/lead?
I should say that in the wintertime, they are left fully charged and disconnected when I am not there for months at a time.
They do get cold (-15C)
Thoughts?
Off-grid: XW+6048 / 48V FLA battery bank (428 A/H (Rolls S-550 batteries)) / Conext MPPT 60 150 charge controller / SCP / Insight gateway / 12 - 260W solar panels / Kohler 12KW 12-RES propane genset
Comments
-
I’m not seeing much of a Advantage in going to LC battery’s
They do charge faster and they say that last longer ?But if you are not charging with a generator I would just stick with LA .
They may have some thing better when you are ready for your next setOut back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
I agree with wellbuilt, in the cold weather unless you have a conditioned space for your batteries, stick with lead acid. How long did your present set last you?
-
I got 5/6 years from them and they were still in good shape until I made a mistake in the fall (October).
Because my panels can get snow covered for multiple months at a time, I usually "mothball" the batteries by fully disconnecting them (open breaker to the batteries from the charge controller and the inverter). In doing so, the parasitic draw of the charge controller will not slowly discharge the batteries. This has served me well....
Last October, I didn't open the breaker to the charge controller (due to another reason) and this destroyed my batteries. I figure they were about half way thru their lifetime so that makes me feel a little better (I was hoping to get 10 years from them if I didn't make any stupid mistakes).
The longer story is why I didn't open the breaker... let me know if interested and I can post that.
I am glad to hear your guys comments on sticking with old school FLA batteries as that's what I have on order.
Off-grid: XW+6048 / 48V FLA battery bank (428 A/H (Rolls S-550 batteries)) / Conext MPPT 60 150 charge controller / SCP / Insight gateway / 12 - 260W solar panels / Kohler 12KW 12-RES propane genset -
Wow killing off your battery’s is a real bummer .That’s why I went with golf cart battery’s for 90 bucks each x16 I have a 430ah battery .
It’s hard to stay 100% on top of the battery / second home thing.I try to make a list of what has to happen before I leave but I still miss things when we are in a hurry.I forget the cooler full of food some times , and I had the door wide open for a few weeks because I did not check it .
It’s allways some thing .Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
Its an interesting story that I will write up later for others to learn from. I have been on top of this and didn't really forget anything.
Long story short, when I opened the breaker for the charge controller to leave the batteries disconnected, the MPPT went into fault due to the sunshine and no battery present. I freaked out and closed the breaker to check I hadn't damaged the charge controller...
it was ok so I left it as it and figured I would return later to resolve it after researching.
I did return after 2.5 months... and they were dead... too much snow.
Oh well, I did get 6 years from them but it still hurts.
Off-grid: XW+6048 / 48V FLA battery bank (428 A/H (Rolls S-550 batteries)) / Conext MPPT 60 150 charge controller / SCP / Insight gateway / 12 - 260W solar panels / Kohler 12KW 12-RES propane genset -
Riley,
I sent you a PM. -
We also have an off grid cabin in snow country, I tilt the panels to 65 degrees for winter which helps with snow cover. I am usually up there weekly, some times every other weekend and always leave the inverter off and the CC on for the last 8 years and have not had any problems returning to a discharged battery bank. I guess we have been lucky so far?
-
Saggys said:We also have an off grid cabin in snow country, I tilt the panels to 65 degrees for winter which helps with snow cover. I am usually up there weekly, some times every other weekend and always leave the inverter off and the CC on for the last 8 years and have not had any problems returning to a discharged battery bank. I guess we have been lucky so far?
The other thing to consider is that your batteries are being discharged and charged ever so lightly so that does cycle them a bit..
That's another reason I do a full disconnect. Why wear them for nothing. I would at least open the breaker to the inverter... it will draw some current as well.
Off-grid: XW+6048 / 48V FLA battery bank (428 A/H (Rolls S-550 batteries)) / Conext MPPT 60 150 charge controller / SCP / Insight gateway / 12 - 260W solar panels / Kohler 12KW 12-RES propane genset -
I agree in the winter months I just turn every thing off once the battery’s are full .I’m allways above full voltage when I return 51. 5 or so .In the summer months I’ll leave the charge controller on for a week with 1 or 2 strings of solar panels just to raise the SG instead of equalizing equalizing the batteries .This top me up to full and keeps SG good .Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar .
-
I have a snowy off-grid system. I would definitely be looking at LifePo4 server rack batteries like EG4 for your system. Either warm the battery above 32 degrees before using it or figure out a battery box with heater - the battery management system won't let you hurt the battery in any case.
Cold won't hurt them if you aren't using them and they have hardly any self discharge. They will last forever and perform way better with no maintenance and you can take them to 95% DOD with no issues and they are way cheaper than lead acid when you consider how much usable power you have and their longevity.
-
javid said:..... - the battery management system won't let you hurt the battery in any case.
warming the pack up, and restarting the BMS What happened to your MPPT controllers when the battery disconnected and they lost V+ and are running +137V and no 48V battery ?
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
mike95490 said:javid said:..... - the battery management system won't let you hurt the battery in any case.
warming the pack up, and restarting the BMS What happened to your MPPT controllers when the battery disconnected and they lost V+ and are running +137V and no 48V battery ?
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed