Classic 150 Charge controller to 48v bank # of panels max in wattage i can have installed
offgridcabin2015
Registered Users Posts: 88 ✭✭
Hello experts.
I"ll be purchasing this charge controler and i'm trying to figure out the max number of panels for an array i can have to it.
wil be a 48v config.
I' know how to calculate the voc for in series but i'm a bit lost of how many strings i can have . IN other words
whatis the max total panel watts .
I've attached a chart . but where i'm lost is the Vmp what's that?
So this is my train of thought. 300 watt panel voc is 39.61x 3 panels x 1.25 (cold factor) i'm still under 150vdc. Good here. This is string one.
so i think i can do 5 strings that bring me to 4500 watts? is that right? Based on chart below if i'm reading it right . i can do 4672watts at 80amps? Sure that means i can have 15 panels on one array to this Classic 150 Charge controller and this even has HyperVOC which extends VOC limits when needed.. so basically 150+48v (wiggle room for extreme cold) i feel i'm safe.
Thoughts?
I"ll be purchasing this charge controler and i'm trying to figure out the max number of panels for an array i can have to it.
wil be a 48v config.
I' know how to calculate the voc for in series but i'm a bit lost of how many strings i can have . IN other words
whatis the max total panel watts .
I've attached a chart . but where i'm lost is the Vmp what's that?
So this is my train of thought. 300 watt panel voc is 39.61x 3 panels x 1.25 (cold factor) i'm still under 150vdc. Good here. This is string one.
so i think i can do 5 strings that bring me to 4500 watts? is that right? Based on chart below if i'm reading it right . i can do 4672watts at 80amps? Sure that means i can have 15 panels on one array to this Classic 150 Charge controller and this even has HyperVOC which extends VOC limits when needed.. so basically 150+48v (wiggle room for extreme cold) i feel i'm safe.
Thoughts?
Comments
-
Hi o g c,
Have you used the MN Classic String Sizing Tool(?):
MidNite Solar - Classic Sizing Tool.
Busy now, be back, VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Ty i'll see what i can learn from this tool. Ty for sharing.
-
offgridcabin2015 said:Hello experts.
I"ll be purchasing this charge controler and i'm trying to figure out the max number of panels for an array i can have to it.
wil be a 48v config.
I' know how to calculate the voc for in series but i'm a bit lost of how many strings i can have . IN other words
whatis the max total panel watts .
I've attached a chart . but where i'm lost is the Vmp what's that?
So this is my train of thought. 300 watt panel voc is 39.61x 3 panels x 1.25 (cold factor) i'm still under 150vdc. Good here. This is string one.
so i think i can do 5 strings that bring me to 4500 watts? is that right? Based on chart below if i'm reading it right . i can do 4672watts at 80amps? Sure that means i can have 15 panels on one array to this Classic 150 Charge controller and this even has HyperVOC which extends VOC limits when needed.. so basically 150+48v (wiggle room for extreme cold) i feel i'm safe.
Thoughts?
Not a copletely simple question, The Classic 150 can be 'overpaneled' without harm, and costeffective to use up to 20-30% more panels than normal, since panels tend to have a maximum output of about 75% of their panel rating.
All of thiis info is available at Midnites Classic sizing tool that Vic gave you a link to...Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
So i did the tool but and i'll post the results here for my 10 panels but why does it show in red over voltage no matter if i choose 1 or 5 or 10 panels. That part makes no sense to me.
-
offgridcabin2015 said:So i did the tool but and i'll post the results here for my 10 panels but why does it show in red over voltage no matter if i choose 1 or 5 or 10 panels. That part makes no sense to me.
I'd bet 5 strings of 3 panels should work and 6 strings of 3 panels should be too high, but cost effective (I don't think that's their words for it)Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Agree with Photowhit,
Generally, with Flooded Lead Acid (FLA) batteries in a 48 V system, strings of two 60 Cell PVs has a too low string Vmp for these 150 V MPPT CCs, strings of three are fine, and strings of four PVs has excessive input voltage.
The thing about the Classic HyperVoc, is, that, in this state, the Classic goes to Rest -- where it produces NO power, until the temperature of the PVs increases, which caused the Voc to be reduced. It is great, that the Classic is protected from damage of very high input voltage, when in HyperVoc, though.
Would run your PVs through the sizing tool, but really would help to know your lowest temperature at the site.
Later, VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Vic said:Agree with Photowhit,
Generally, with Flooded Lead Acid (FLA) batteries in a 48 V system, strings of two 60 Cell PVs has a too low string Vmp for these 150 V MPPT CCs, strings of three are fine, and strings of four PVs has excessive input voltage.
The thing about the Classic HyperVoc, is, that, in this state, the Classic goes to Rest -- where it produces NO power, until the temperature of the PVs increases, which caused the Voc to be reduced. It is great, that the Classic is protected from damage of very high input voltage, when in HyperVoc, though.
Would run your PVs through the sizing tool, but really would help to know your lowest temperature at the site.
Later, Vic2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed