well pumps ?

i just jumped in and started out by buying 9 355 watt panels, 47.45 voc. i am intending to build it using 2 make sky blue s340 and one 3kw all in one off grid tie, 24vlt 220. my understanding is that the more panels and charge controlers the fewer batteries needed. my biggest draw will be the two 3/4 hp, 1495 watt 6.5 amp well pumps, and they are my biggest concern. i do not yet know how to find the starting draw and dont know if a 3kw will handel the well pumps.
Comments
Will both pumps start / run at the same time ever ?
Pumps run sunlight hours only ?
Are the pumps 2 wire ( starting cap underwater with the pump) or 3 wire - cap above ground in the control box. 3 wire starts a bit easier.
Is your chosen inverter a low-frequency or high-frequency inverter
My 1/2 hp pump, after starting and is running stably, logs 1,000 watts in use by the inverter. That's includeing Power Factor ( PF ) losses, copper losses and efficiency losses.
Having this be successful long term, at only 24V, is going to be rough. What are the batteries, Flooded Lead Acid, Li, ??
A low budget. 3Kw inverter, is going to be marginal at starting 3/4 hp
The minimal battery for a 24V system would be about 500Ah to keep the inverter happy, maybe 250ah at 48V , regardless how much solar is present. Panels and charge controllers cannot respond to the 120hz peak power draw from the DC bus, batteries have to handle that.
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
I was going to run it on solar but it seam like a wast of power I’m just running it off my inverter for 1/2 hour a day in good sun and have 0 troubles the pump was a lot but in the end it was very east to set up with nothing extra to buy .
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Have you figured out how many Watt*Hours (or kWH) per day you will need?
And how many panels (Watts) are you going to use? And what voltage for the battery bank (12/24/48)?
Refrigerators and Freezers use a lot of energy in a home... If they are modern Energy Star Rated, something like 1,500 WH (1.5 kWH) per day EACH. And will this be a weekend or full time off grid installation?
Just to give you an idea of the math... Say 3,000 WH per day (2x fridge/freezer set) near Houston Texas:
http://www.solarelectricityhandbook.com/solar-irradiance.html
Houston
Measured in kWh/m2/day onto a solar panel set at a 60° angle from vertical:Average Solar Insolation figures
(For best year-round performance)
- 3,000 WH per day * 1/0.52 off grid AC system eff * 1/3.51 hours of sun per day (December) = 1,644 Watt array for December "break even"
That would close for a "summer" system... But if you want to run in December, either larger array (upwards of 2x larger) or backup genset and fuel for bad weather...This is a big jump in system specifications... Want to make sure you are OK with sun/genst/etc. for your needs....
-Bill
I was running my standard 1 hp well pump off my Conext inverter but the start up surge was so massive (somewhere around 8000 watts) it would occasionally trip a "low DC voltage" warning if I had another high load running after sundown. I have since bitten the bullet and had the pump changed out to a 1 hp Grundfos SQ pump and it maxes out around 2300 watts draw.
This also means that if I ever need to use a generator to power the water pump I can get by with a much smaller generator.