LiFePo4 battery bank.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
Comments
-
Down on the baja? What is it like these days? Lot's of fish tacos and pacifico I hope!
If the BMS is off? The spec for the LFP I use is,Self Discharge (25°C / 77°F) < 3% per month (Battery Off) "we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Dave Angelini said:Down on the baja? What is it like these days? Lot's of fish tacos and pacifico I hope!
If the BMS is off? The spec for the LFP I use is,Self Discharge (25°C / 77°F) < 3% per month (Battery Off)
It's been hot and sticky long enough. Time for a new season.. Oddly Pacificos are hard to find in our area. Damn Covid 19 affected beer production right away and it has taken a while to recover.
I'm waiting on the BMS. At the moment There's nothing connected to the batteries. They're just parallel wired together. I will keep an eye on the voltage.
Thanks!2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
Damn that is bad news on Pacifico. Plenty in our small town. When we were there, the empties were refilled and so you saved them. The cost was almost free if you hauled the empty bottles in the boat or RV.
Fall is almost here in the southern Sierra. We did well this summer. Some really bad smokey hot ones of late."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
littleharbor2 said:I currently have a bank of 8 280 ah. batteries wired in parallel and sitting perfectly balanced at 3.269 volts. My question is can I leave them sitting, wired in parallel for an indefinite length of time while I assemble the rest of the components needed to put them into service as a 8s,24 volt bank. I'm in no big hurry to put them into service as my current AGM bank is somewhere shy of 3 years old and I figure I have at least 2 more years left on them.Off-grid cabin: 6 x Canadian Solar CSK-280M PV panels, Schneider XW-MPPT60-150 Charge Controller, Schneider CSW4024 Inverter/Charger, Schneider SCP, 8S (25.6V), 230Ah Eve LiFePO4 battery in a custom insulated and heated case.
-
Horsefly said:littleharbor2 said:I currently have a bank of 8 280 ah. batteries wired in parallel and sitting perfectly balanced at 3.269 volts. My question is can I leave them sitting, wired in parallel for an indefinite length of time while I assemble the rest of the components needed to put them into service as a 8s,24 volt bank. I'm in no big hurry to put them into service as my current AGM bank is somewhere shy of 3 years old and I figure I have at least 2 more years left on them.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
Dave Angelini said:Damn that is bad news on Pacifico. Plenty in our small town. When we were there, the empties were refilled and so you saved them. The cost was almost free if you hauled the empty bottles in the boat or RV.
Fall is almost here in the southern Sierra. We did well this summer. Some really bad smokey hot ones of late.Funny how there's more Mexican beer in the USA than here in Mex. Cheaper too. The days of dirt cheap Coronas are long gone. Funny thing, You can buy Coors Light and Bud Light cheaper than domestic beer down here. Oh and gas is about equal to So.Cal, pricewise.2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
littleharbor2 said:Horsefly said:littleharbor2 said:I currently have a bank of 8 280 ah. batteries wired in parallel and sitting perfectly balanced at 3.269 volts. My question is can I leave them sitting, wired in parallel for an indefinite length of time while I assemble the rest of the components needed to put them into service as a 8s,24 volt bank. I'm in no big hurry to put them into service as my current AGM bank is somewhere shy of 3 years old and I figure I have at least 2 more years left on them.Off-grid cabin: 6 x Canadian Solar CSK-280M PV panels, Schneider XW-MPPT60-150 Charge Controller, Schneider CSW4024 Inverter/Charger, Schneider SCP, 8S (25.6V), 230Ah Eve LiFePO4 battery in a custom insulated and heated case.
-
Horsefly said:littleharbor2 said:Horsefly said:littleharbor2 said:I currently have a bank of 8 280 ah. batteries wired in parallel and sitting perfectly balanced at 3.269 volts. My question is can I leave them sitting, wired in parallel for an indefinite length of time while I assemble the rest of the components needed to put them into service as a 8s,24 volt bank. I'm in no big hurry to put them into service as my current AGM bank is somewhere shy of 3 years old and I figure I have at least 2 more years left on them.
Please forgive my ignorance. This is completely new to me.2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
littleharbor2 said:
Please forgive my ignorance. This is completely new to me.
There are a ton of 0-30V / 0-10A bench power supplies on Amazon, all made in China. These work fairly well, but at only 10A it takes a long time to charge a parallel pack of 8 x 280Ah cells. www.circuitspecialists.com has a little higher quality supplies, some that go to 20 or 30A. I actually have 3 of the cheap supplies and 1 of the circuit specialist's supplies. If I was near Baja I'd be happy to loan one to you for however long you need it.Off-grid cabin: 6 x Canadian Solar CSK-280M PV panels, Schneider XW-MPPT60-150 Charge Controller, Schneider CSW4024 Inverter/Charger, Schneider SCP, 8S (25.6V), 230Ah Eve LiFePO4 battery in a custom insulated and heated case. -
Haven't decided on the BMS as of yet.Off-grid cabin: 6 x Canadian Solar CSK-280M PV panels, Schneider XW-MPPT60-150 Charge Controller, Schneider CSW4024 Inverter/Charger, Schneider SCP, 8S (25.6V), 230Ah Eve LiFePO4 battery in a custom insulated and heated case.
-
Horsefly, you are welcome to post links here too.More information is always good.BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
-
BB. said:Horsefly, you are welcome to post links here too.More information is always good.Bill
Some general BMS concepts:- The purpose of the BMS is to protect the LiFePO4 cells. All should have a LVD (Low Voltage Disconnect) where if any one cell gets to 2.5V, the BMS shuts off discharge from the battery. Similarly, a BMS should have a HVD (High Voltage Disconnect) that would shut off charging if any one cell gets up to 3.65V. Most also detect short circuits and will cut off the battery. A few have temperature probes, and allow charging to be cut off if the cells get below a certain temperature (LiFePO4 cells can be ruined if charged below 32°F), or discharging below or above a certain temperature.
- Most BMSs these days seem to use MOSFETs to connect or cut off the battery from the rest of the system. Some still use relays / contactors. There tends to be a religious argument about whether MOSFETs or contactors are better. Since MOSFETs are directional, they have the advantage of being able to cut off charging or discharging or both on a single connection to the battery pack. A few BMSs allow you to disable the MOSFET control and drive an external contactor.
- There are "dumb" BMSs and "smart" BMSs. The basic difference is that a dumb BMS has some hard-coded thresholds on all the settings, and it just - hopefully - does what a BMS is supposed to do. A "smart" BMS has at a minimum a Bluetooth interface and a phone app, where the user can see the status (voltage) of each cell. Better smart BMSs will also allow you to modify the settings, such as the LVD and HVD voltages, temperature cutoffs, etc. A good BMS should also have a Coulomb counter built in, so you can see the SoC of the battery. Finally, some of the smart BMSs allow your to calibrate the voltage readings, since an accurate voltage reading by the BMS is pretty critical (this requires a high quality multimeter). I personally think there it is a really bad idea to use a dumb BMS, especially for anyone doing DIY. It's useful to see on your phone how the cells behave during charge and discharge cycles, and it helps to see where the best bulk/absorption voltage is for your SCC, and where your LVCO on the inverter should be.
- For those that are really serious about it, there are some il primo BMS companies: Batrium (made in Australia, I think), Orion (rooted mostly in electric vehicles), and REC. These are quality units, but if you are building a DIY battery from LiFePO4 cells you probably will be paying more for the BMS than you did for the cells.
- There are quite a few Chinese BMS companies. The one that gets the most play on Alibaba and AliExpress is Daly. They are distinctive because of their very slick-looking bright red paint and cool looking heat sinks and fans. Unfortunately, it seems they have traded some quality control and design detail for those pretty looks, as I think I've seen more complaints about Daly than most others.
- I've seen some positive comments about Ant BMS, QUCC, and Heltec BMS, but not enough that I can say they much one way or the other about them.
- Chargery is another Chinese company that started out for EVs but has broadened their application and it seems there are a number of DIY LiFePO4 battery builders that are using them.
- There are some down in the weeds BMSs that get very little play but I have heard of them. TaoBMS seems to have lots of functionality. There are some others I can't think of at the moment.
- JBD (also Chinese, and on AliExpress) is my current choice, and from what I've seen most people are pretty happy with them. I have 5 of them right now. They are smart BMSs, have temperature-triggered cutoffs, and can be calibrated. They are entirely MOSFET-based, so if you don't like MOSFETs you should not look at JBD. Perhaps best of all, there are at least two companies in the U.S. that are reselling JBD and provide support and calibration of the BMS before shipping. Best of all (if you are in the U.S.) the shipping gets to you in a few days rather than the 30-60 days from China. The two companies are https://overkillsolar.com/ and https://www.currentconnected.com/. They both charge quite a bit more than JBD on AliExpress, but for some it is worth it.
- There are a ton that I'm forgetting, and probably even more that I don't know anything about.
Whew!Off-grid cabin: 6 x Canadian Solar CSK-280M PV panels, Schneider XW-MPPT60-150 Charge Controller, Schneider CSW4024 Inverter/Charger, Schneider SCP, 8S (25.6V), 230Ah Eve LiFePO4 battery in a custom insulated and heated case. -
littleharbor2 said:I currently have a bank of 8 280 ah. batteries wired in parallel and sitting perfectly balanced at 3.269 volts. My question is can I leave them sitting, wired in parallel for an indefinite length of time while I assemble the rest of the components needed to put them into service as a 8s,24 volt bank. I'm in no big hurry to put them into service as my current AGM bank is somewhere shy of 3 years old and I figure I have at least 2 more years left on them.
At 3.269v rested open circuit, if DVM is accurate, the cells are in ballpark of 30% state of charge. They will have between 1.5% to 2.5% cell capacity per month of cell self discharge depending on ambient temp. So you have a while.
If you only passively paralleled to balance, some cells may be greater or less than 30% state of charge. It takes 10-20 mV of overpotential before there is any small amount of cell current. While parallel connected, they will all read the same voltage, but if you separate them, some will change as much as 10-20 mV above or below 3.269v, after any surface capacitance charge bleeds off which could take a couple of days. That could mean some cells are as low as 20% state of charge and some as high as 40% state of charge. -
Horsefly said:BB. said:Horsefly, you are welcome to post links here too.More information is always good.Bill
Some general BMS concepts:- The purpose of the BMS is to protect the LiFePO4 cells. All should have a LVD (Low Voltage Disconnect) where if any one cell gets to 2.5V, the BMS shuts off discharge from the battery. Similarly, a BMS should have a HVD (High Voltage Disconnect) that would shut off charging if any one cell gets up to 3.65V. Most also detect short circuits and will cut off the battery. A few have temperature probes, and allow charging to be cut off if the cells get below a certain temperature (LiFePO4 cells can be ruined if charged below 32°F), or discharging below or above a certain temperature.
- Most BMSs these days seem to use MOSFETs to connect or cut off the battery from the rest of the system. Some still use relays / contactors. There tends to be a religious argument about whether MOSFETs or contactors are better. Since MOSFETs are directional, they have the advantage of being able to cut off charging or discharging or both on a single connection to the battery pack. A few BMSs allow you to disable the MOSFET control and drive an external contactor.
- There are "dumb" BMSs and "smart" BMSs. The basic difference is that a dumb BMS has some hard-coded thresholds on all the settings, and it just - hopefully - does what a BMS is supposed to do. A "smart" BMS has at a minimum a Bluetooth interface and a phone app, where the user can see the status (voltage) of each cell. Better smart BMSs will also allow you to modify the settings, such as the LVD and HVD voltages, temperature cutoffs, etc. A good BMS should also have a Coulomb counter built in, so you can see the SoC of the battery. Finally, some of the smart BMSs allow your to calibrate the voltage readings, since an accurate voltage reading by the BMS is pretty critical (this requires a high quality multimeter). I personally think there it is a really bad idea to use a dumb BMS, especially for anyone doing DIY. It's useful to see on your phone how the cells behave during charge and discharge cycles, and it helps to see where the best bulk/absorption voltage is for your SCC, and where your LVCO on the inverter should be.
- For those that are really serious about it, there are some il primo BMS companies: Batrium (made in Australia, I think), Orion (rooted mostly in electric vehicles), and REC. These are quality units, but if you are building a DIY battery from LiFePO4 cells you probably will be paying more for the BMS than you did for the cells.
- There are quite a few Chinese BMS companies. The one that gets the most play on Alibaba and AliExpress is Daly. They are distinctive because of their very slick-looking bright red paint and cool looking heat sinks and fans. Unfortunately, it seems they have traded some quality control and design detail for those pretty looks, as I think I've seen more complaints about Daly than most others.
- I've seen some positive comments about Ant BMS, QUCC, and Heltec BMS, but not enough that I can say they much one way or the other about them.
- Chargery is another Chinese company that started out for EVs but has broadened their application and it seems there are a number of DIY LiFePO4 battery builders that are using them.
- There are some down in the weeds BMSs that get very little play but I have heard of them. TaoBMS seems to have lots of functionality. There are some others I can't think of at the moment.
- JBD (also Chinese, and on AliExpress) is my current choice, and from what I've seen most people are pretty happy with them. I have 5 of them right now. They are smart BMSs, have temperature-triggered cutoffs, and can be calibrated. They are entirely MOSFET-based, so if you don't like MOSFETs you should not look at JBD. Perhaps best of all, there are at least two companies in the U.S. that are reselling JBD and provide support and calibration of the BMS before shipping. Best of all (if you are in the U.S.) the shipping gets to you in a few days rather than the 30-60 days from China. The two companies are https://overkillsolar.com/ and https://www.currentconnected.com/. They both charge quite a bit more than JBD on AliExpress, but for some it is worth it.
- There are a ton that I'm forgetting, and probably even more that I don't know anything about.
Whew!Horsefly said:Wow, now that's a lot of good info coming from experience. Again, thanks so much for your help2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
RCinFLA said:littleharbor2 said:I currently have a bank of 8 280 ah. batteries wired in parallel and sitting perfectly balanced at 3.269 volts. My question is can I leave them sitting, wired in parallel for an indefinite length of time while I assemble the rest of the components needed to put them into service as a 8s,24 volt bank. I'm in no big hurry to put them into service as my current AGM bank is somewhere shy of 3 years old and I figure I have at least 2 more years left on them.
At 3.269v rested open circuit, if DVM is accurate, the cells are in ballpark of 30% state of charge. They will have between 1.5% to 2.5% cell capacity per month of cell self discharge depending on ambient temp. So you have a while.
If you only passively paralleled to balance, some cells may be greater or less than 30% state of charge. It takes 10-20 mV of overpotential before there is any small amount of cell current. While parallel connected, they will all read the same voltage, but if you separate them, some will change as much as 10-20 mV above or below 3.269v, after any surface capacitance charge bleeds off which could take a couple of days. That could mean some cells are as low as 20% state of charge and some as high as 40% state of charge.Fluke DVM I trust it. The batts varied a bit before being passively balanced and a couple were farther off than the majority. Now they are all sitting still parallel wired and have been for a couple weeks now. I will disassemble the pack and watch the voltage.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed