Clipping issues with Enphase IQ7 paired with LG NEONS 335, How to solve this issue?
dks1
Registered Users Posts: 20 ✭✭
How to solve clipping issues with ENPHASE IQ7???
Tagged:
Comments
-
Not sure if it's pertinent, but my enphase installation was having clipping issues when first installed. The 10kw was being clipped down to about 6kw. The production curve display would rise until mid morning, then there would be up down, up down hash happening until late afternoon. The top of the curve would be hacked off sort of. Voltage and/or frequency out of range messages. The utility power would measure out at least to 250 - 255vac or so. High in other words.
Enphase worm hole-ed into my inverters via the Envoy and re-programmed the inverters to change their grid profile and accept voltage up to their design limit . The settings shows "IEEE 1547 Mainland Alternate". That solved the clipping issues. Worth investigating as it costs nothing to get Enphase to get set up properly. I don't think it's something you can change yourself, installer or Enphase has to do it. Check your "selected grid profile" through the settings page of your Enlighten Manager site.
Good luck -
Ralph Day said:Not sure if it's pertinent, but my enphase installation was having clipping issues when first installed. The 10kw was being clipped down to about 6kw. The production curve display would rise until mid morning, then there would be up down, up down hash happening until late afternoon. The top of the curve would be hacked off sort of. Voltage and/or frequency out of range messages. The utility power would measure out at least to 250 - 255vac or so. High in other words.
Enphase worm hole-ed into my inverters via the Envoy and re-programmed the inverters to change their grid profile and accept voltage up to their design limit . The settings shows "IEEE 1547 Mainland Alternate". That solved the clipping issues. Worth investigating as it costs nothing to get Enphase to get set up properly. I don't think it's something you can change yourself, installer or Enphase has to do it. Check your "selected grid profile" through the settings page of your Enlighten Manager site.
Good luck
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed