New battery bank
lee1
Registered Users Posts: 7 ✭✭
Hi
I have just purchased 3 fullriver dc85 batteries and have them in parrell
Don't think the connecting wires are substantial enough what gauge should I use they are stacked together so connections are only 4 to 6 inches apart and would I need a inline fuse
I have just purchased 3 fullriver dc85 batteries and have them in parrell
Don't think the connecting wires are substantial enough what gauge should I use they are stacked together so connections are only 4 to 6 inches apart and would I need a inline fuse
Comments
-
The gauge would be dependent on the loads, the overcurrent protection would be sized according to the gauge. To maintain ballance between the batteries is important to configure the wiring correctly, this link explains the rationale between different methods http://www.smartgauge.co.uk/batt_con.html1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
In cars, they either use very heavy copper cables for connection to the starter--Without fuses(?)--Or use a "fusible link" (wire) for the intial protection to the car's electrical system.
If your electrical loads/charging are small, you can use small AWG wiring and a fuse/breaker to protect each wire back to its battery.
Or you can use much heavier cables and a single fuse/breaker to the rest of the electrical system... The chances that a single lead acid battery would fail "shorted" is small--The bigger issue is that something falls on the bank (metal tool), or somebody (like a child playing) shorts the bank. The costs of good quality fuses/breakers and the space to install them--Many people choose to go without.
And example of small form factor fuses and fuse holders that can manage 100's of amps are those from BlueSea. The MRBF holders (you have to buy fuses separately) are really nice:
https://www.bluesea.com/products/category/16/72/Fuse_Blocks/Terminal_Fuse_Blocks (holders)
https://www.bluesea.com/products/category/0/42//Marine Rated Battery Fuses (fuses)
Using circuit breakers are also a good (larger) solution... They give you circuit protection, but also allow you to shut down power (switch function) too.
https://www.solar-electric.com/residential/circuit-protection/circuit-breakers.html?nav_breaker_type=500&product_list_limit=all
Using McGivor's link for parallel battery wiring:
http://www.smartgauge.co.uk/batt_con.html
I like method #3 as this gives you obvious wire connection to the + bus where you can mount breakers or fuses.... If you use the BlueSea fuse mounts above, you can attach one to each battery + terminal, then wire as needed using any of the other suggested wiring methods.
Those are 85 AH batteries, that supply upwards of 85 amps into a load (AGM have very low internal resistance).... Using fuse or breaker is one solution, using heavier cable is another. This simplified NEC table shows you wire ratings:
https://lugsdirect.com/WireCurrentAmpacitiesNEC-Table-301-16.htm
4 or 2 AWG wire would be heavy enough to support any "normal/maximum current loads". If you are planning on 10% of rated load (8.5 amps charging or discharging max)... A 14 AWG cable is going to carry that current. Fusing currents:
https://www.powerstream.com/wire-fusing-currents.htm
A 14 AWG wire will fuse around 123 amps. If you are "OK" if a 14 awg wire "fuses" (gets red hot an melts) or there is nothing that can draw >~15 amps--Then per battery protection is not really needed (battery in metal box/on concrete floor, nothing flammable nearby). 14 AWG is good for 12-20 amps pretty easily and probably appropriate to this level of current for these 85 amp cells.
If you use 6 or 4 AWG cable (6 AWG is around 500-600 amps fusing current)---They will carry and "reasonable" fault current for this size battery bank.
One issue with parallel power systems (power supplies, batteries, etc.)... As you add more parallel devices, the total current available increases... 3x85ah (at 1C discharge rate) = 255 amps into a fault. And you start needing to look at "per device" fusing/breakers. Why N+1 power systems are a pain in the behind (additional costs for protection of the individual N's against N+1 faults.
Many decades ago--An old ~1954 Chevy/GMC shop pickup. The battery was under the passenger floor board with a metal cover. And the metal cover had a large steel "latch rod"... The latch rod assembly failed and dropped on the battery causing lots of smoke... Replaced the battery and tossed the broken latch assembly into the garbage... My quick fix (no other damage, no more latch assembly to fall onto the pickup's battery battery box).
-Bill "things happen" B.
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed