96 volt bank and mppt with 2 x 48 volt inverters ?

Options
spacebass
spacebass Registered Users Posts: 87 ✭✭
As title suggests can I have a 8 x 12 volt series lithium battery bank fed by a 96 volt controller with two 48 volt inverters taking off from two points on the battery bank permanently wired ?
Thanks x

Comments

  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Options
    You can, but you won't like what happens.   The batteries will become unbalanced and if any of the gear is grounded, you could short out 48V+ to the 96V+   Boom ! 
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||