f66 on xw4024

i brought down my system with to XW In order to install a shunt. Now I get a f66 fault on the slave. I looked all over the config and I don't see anything wrong. I changed the cable and no luck. I changed the config to make the master the slave and slave the master with no luck. The fault follows the slave. Any ideas?
Comments
I would do the below and also try a DC shutdown of the slave for 5 minutes.
F66 on XW multi-unit system.
Multi-unit XW system shows F66
Environment:
Multi-unit XW system
Resolution:
1. Ensure Xanbus and AC Sync cabling correct
2. Ensure XW Inverters have unique device numbers (00, 01, 02, etc.)
3. Ensure Inverter mode is set correctly (split phase master, slave, etc.)
4. Ensure ALL settings in CONNECTIONS menu of all inverters match exactly.
Cause:
Cabling or configuration errors
http://members.sti.net/offgridsolar/
E-mail [email protected]
I would try, if you have not is a reset to factory on the bad one. If no dice I would make sure the fault inverter just sits without dc for a day.
I would inspect the stacking ports for corrosion or damage. Good Luck !
http://members.sti.net/offgridsolar/
E-mail [email protected]
Non Specified, I was told means they did not test it and even though I did a bit here, they did not want me to do this offgrid.
http://members.sti.net/offgridsolar/
E-mail [email protected]
Have you looked at the relays?
If they are not clear plastic and are smokey, you need repair or replace. Since there a numerous way to wire 2 4024's I think you should list it or draw it , if anyone is going to be able to give you a decent answer.
http://members.sti.net/offgridsolar/
E-mail [email protected]
For your problem, also check the history in faults and warnings logs. On gateway it is called events / historical.
At least you have s spare 😉
http://members.sti.net/offgridsolar/
E-mail [email protected]
You said you updated firmware? Which is it ? What are you running?
Yes your PDP will work fine with xwp. I did this many times back when 4024 became non-serviceable in the field.
http://members.sti.net/offgridsolar/
E-mail [email protected]
Your 4024 is pretty old and I can't say for sure if a modern config tool would work with it. I only did this on the 6048 back in the day.
I don't like strings of batteries offgrid but.....
I also think I would sell the 4024's. You can get a CSW4048 pretty cheap and it could be a spare or used for additional charging. About the only thing that will kill an XW is lightning or gensets, so use SPD's if you are not now.
A bit chilly I see up there! Good Luck!
http://members.sti.net/offgridsolar/
E-mail [email protected]
It is said that the Delta LA series "arrestors" have an arc gap that is designed to breakdown at about 7500 V nominal. The ones that I've looked at are just an arc gap with SAND for quenching.
Our systems really need Supressors (like the MN SPDs), which have MOVs that conduct at a much lower voltage than the Deltas, especially, in lightning alley, IMO.
Vic
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Many of us use spare Combiner box breaker positions to add a breaker, that connects the SPDs hot lead to the Combiner output busbar. Do not know how you accomplish this with your Deltas.
Vic