New member, old question on converting existing pump to solar

Hello all, new member here.
I
am researching for my first solar project,
which will be to migrate my house well pump from grid to off-grid
solar. The primary goal is for water supply independence in the event
of extended power outage. I have read several threads on this topic, but
most of them end up with the recommendation to install a Grundfos.
Since this is our home water supply, I really don't want to muck-up a
working system (not to mention the cost) by replacing the pump.
One
of the most informative threads is here :
https://forum.solar-electric.com/discussion/352536/how-to-size-battery-and-panels-to-run-my-well-pump
, however, that goes way over my head.
The
specs on my pump are (not sure of the manufacturer, but Franklin does
sound familiar): 3/4 HP, 230V, 1 phase, 60 Hz, 7.2A (8.3 SF Max), 3450
RPM, KVA code M, .55Kw
There is a pump control box in the pumphouse, so I assume it is a 3 wire pump.
The
well is 260-270 ft. I estimate total run time per day at 3 hrs
maximum. Best I can tell, the run time per fill to top off the storage
tank is maybe 3-5 minutes.
I have been
looking at a Magnum MS4024PAE MS-PAE Series 4000W 24VDC inverter /
charger, but want to get other's experience on what they are using in a
similar setup.
I have already purchased 2 100Ah 12v Battle Born batteries, but that is it so far. I am still trying to size the array, charge controller, etc. I don't mind over-engineering the system, unless it would be harmful to my well pump.
My location is central Texas.
Any input from other members that have also gone through this process would be much appreciated.
Comments
That is what we do offgrid or we run ACV out to the pump from the house system or genset for back-up. You already have that right?
As for over engineering, I would make sure you do not destroy those batteries by charge or discharge currents. Seen too much of that lately with LFP! Good Luck!
htps://offgridsolar1.com/
E-mail [email protected]
Your pump has a pressure switch control box
it might have a 3-wire control/starter cap box. Make sure you know the difference
a 3/4 pump has a huge starting surge on the AC side, which means you inverter has to supply that, and the batteries feed the inverter
3/4hp surge 9,200watts starting
inverter will consume 11,040 watts starting it
battery @ 24V will supply 460 amps for about 1 sec to start
a 48V battery will supply 230 amps for starting.
The inverter has to be robust enough to handle this surge several times a day, and not give out.
Good inverters have a complete data sheet displaying their limits, so the customer can make a wise decision
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
htps://offgridsolar1.com/
E-mail [email protected]
So you can research it yourself, or open the junction box and see how many wires go to the pump (not counting the green wire)
So, ways to get out of the hole.
can those batteries supply 230A and can they be wired 4x for a 48V bank ? Otherwise, back to basics.
And maybe start with a 6kw conventional generator. If you take something off grid, you need backup generator for it, or do without.