Hi
To every body wishing a pleasant change of the year and hope the very best for 2021 hoping the covid will be far away
Need a circuit breaker a need to know what amp
have a inverter with max amp imput of 18a*18a 500 vdc it is a mppt solar 8048 8kw
will usae 12 panels 500w each 10.27 amp
Plse let me know how to combine if possible.
regards
Bob
To every body wishing a pleasant change of the year and hope the very best for 2021 hoping the covid will be far away
Need a circuit breaker a need to know what amp
have a inverter with max amp imput of 18a*18a 500 vdc it is a mppt solar 8048 8kw
will usae 12 panels 500w each 10.27 amp
Plse let me know how to combine if possible.
regards
Bob
Comments
-
Hi Bob,
Can you give us a link to your inverter/charger/solar charger system?
Specific solar panel ratings (Vmp/Voc/Imp/Isc and series fuse rating)
Battery bank voltage/AH rating (if not obvious from your links).
You are in a warm climate as I remember: Curacao
Need for breakers and such depend on your array configuration (and that needs to match your charge controller's input requirements).
Details matter here.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Your inverter mfg will specify a style and value for the main breaker. It has to allow enough current for the expected starting surges, and trip before severe damage is done. I won't guess at if for you, but if I recall correctly, my main is 350A
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Hi Bill and mike
Happy New Year
the inverter is max MPP SOLAR 8048 8kw 230vac 48v dc 12pc total panels
panel 500w greensun imp 10.87 vmp 48.63 voc58.95 isc 10.28
hoping having been clear
regards
Bob
-
Is this the unit?
https://www.mppsolar.com/v3/catalogs/PCM5048_8048.pdf
If so, then- Vinput=140 VAC max (there is a higher voltage option, not yours?)
- 70 Amps input max
- 48 VDC battery bank
- panel 500w greensun imp 10.87 vmp 48.63 voc58.95 isc 10.28
- Voc-array= 2 * 58.95 volts = 117.9 volts Voc-array at 25C (assuming no "cold snaps")
- Vmp-array= 2 * 48.63 volts = 97.26
- Imp-array= 6 parallel strings * 10.87 amps = 65.22 Amps (is this Isc?)
- Isc-array= 6 * 10.28 amps = 61.68 amps (is this Imp?)
- Max series fuse guess= 10.87 amps (Isc?) * 1.25 NEC derating = 13.3 amps round up to = 15 amp fuse/breaker (spec sheet may say 20 amps max series fuse)
- Suggest wiring for array be rated for carrying 61.68 amps (Imp-array?) * 1.25 NEC derating = 77.1 amps minimum (wire and swirch/breaker if used minimum rated capacity).
2x panels in series works.
You would use a 6 to 1 combiner box with 15 (or possibly 20) amp fuses/breakers.
All make sense?
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
hi Bill that is NOT the unti is pip max 8048 8kw off grid inverter als white in color and black piece on the botrtom nblack color
Bob -
This is the one?
- Vmp-min~100 VDC
- Vinput-array-max 500 VDC
- 2x Solar PV input with 18 amp max per channel.
- 120 amps max charging (into ~60 volts @ battery bus?).
- You have 12 panels.
- Guessing warm tropical climate with temperature not falling below 25C
Your 500 Watt solar panels have Imp~10.28 amps... But the PV channel has a maximum of 18 amps input... So you are limited to one series string per channel. (smaller Imp panels of ~9 amps or less, you could but 2 in parallel and get more solar energy into the unit).Using 6 panels per string x 2 strings:- 6 panels in series * ~60 volts Voc (guess) = 360 Volts @ 25C (good, below 500 vdc)
- 1x panel per strings = 10.28 amps per string (good, below 18 amps max)
- 12 * 500 Watt panels = 6,000 Watt array (good, below 8,000 Watts)
- 6 panels in series * 48.63 volts Vmp (?) = 291.78 volts Vmp-std (good, over 100 vdc minimum Vmp-array)
Assuming that 6s x 2p is correct to two separate Solar PV inputs for the inverter-charger--Then you do not need any circuit breakers/fuses for safety.Note: With this controller--You have two separate 6 panel strings... One to each controller's PV input (2x PV input total)... So, you do not really have 2x parallel strings (the two strings are wired separately to the charge controller solar inputs).If you would like circuit breakers for service (turn on/off array when working on system)--Then, the minimum circuit breaker/switch rating would be:- 10.87 amps Isc(?) * 1.25 derating = 13.6 or round up to 15 amps minimum
- 360 VDC minimum working voltage
For example, here are 4x 150 VDC circuit breakers wired in series with a common trip to reach 600 VDC max working voltage:For ~$125 USD... And you would need two.Do not use standard AC rated circuit breakers on high(er) voltage DC (or wire wrong polarity)--They will fail:https://www.youtube.com/watch?v=Cup5fMGaE2g (various breakers on DC catching fire if used incorrectly)https://www.youtube.com/watch?v=Zez2r1RPpWY (knife switch on AC vs DC switching)
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed