Battery Failure
williwite
Registered Users Posts: 1 ✭
Good day all,
I'm new here, I have had some issues concerning a solar and backup system I installed 4 months ago. I used 12 units of 300w solar panels, a 60a charge controller (Ipanda), and a felicity 5kva 48V inverter and 8 units of 200AH batteries running on a Load of about 2000W.
The system ran smoothly for the first 3 months, then suddenly system lasted for less than 2hours. I tested the internal resistance of individual batteries and 5 was replaced. I suspected the ambient temperature (36 degree Celsius) to have been the cause of the damage and ventilated the surrounding, and changed the interconnecting cables of batteries from 25mm2 to 16mm2 but retained the 25mm2 for connections from battery to inverter.
In 2 weeks latter the same problem occurred again. I checked the internal resistance of the batteries 3 of those not replaced initially failed the test and also the readings of 2 the newly replace battery gave 15.3V and 16V respectively. This has really got me confused as to the cause of this continuous failure. I would be of utmost gratitude if a solution came up.
Regards
William
I'm new here, I have had some issues concerning a solar and backup system I installed 4 months ago. I used 12 units of 300w solar panels, a 60a charge controller (Ipanda), and a felicity 5kva 48V inverter and 8 units of 200AH batteries running on a Load of about 2000W.
The system ran smoothly for the first 3 months, then suddenly system lasted for less than 2hours. I tested the internal resistance of individual batteries and 5 was replaced. I suspected the ambient temperature (36 degree Celsius) to have been the cause of the damage and ventilated the surrounding, and changed the interconnecting cables of batteries from 25mm2 to 16mm2 but retained the 25mm2 for connections from battery to inverter.
In 2 weeks latter the same problem occurred again. I checked the internal resistance of the batteries 3 of those not replaced initially failed the test and also the readings of 2 the newly replace battery gave 15.3V and 16V respectively. This has really got me confused as to the cause of this continuous failure. I would be of utmost gratitude if a solution came up.
Regards
William
Comments
-
I take this is 2 banks of 12v batteries wired 4 ea. in series for 48v? If so and your standing battery voltage is 15.3 and 16V you have cooked them to death. Are these fla or what type of battery and who programmed your charge controller?
-
What you are describing is a common problem in high temperatures, there are however many pieces missing from the puzzle.
1. Are the batteries lead acid and if so are they flooded or sealed?
2. Dose the charge controller have a remote temperature sensor (RTS) to compensate for high battery temperature?
3. How are the batteries configured, and where are the charge/discharge conductors connected?
4. The load of 2000W is without a time factor, how many hours is the load powered?
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
I am guessing this is his CC. It appears to have a BTS on the far left hand side but it's not stated in the specs?
-
William,
While 36C is very warm for a Lead Acid battery bank (check the actual battery temperatures, especially when charging--During charging and equalization charging for a period of time, the batteries can exceed 45C or so--When charging is normally stopped until the bank cools).
As the others have asked--Need to know more about the battery bank (6 volt or 12 volt @ 200 AH batteries or what?) for an XXX AH @ 48 volt battery bank.
A 5,000 Watt AC inverter is pretty large--And a bit oversized for a 400 AH @ 48 volt battery bank (roughly a 2,000 to 4,000 Watt max inverter suggested).
There is average power usage (Watts is a rate, like kilometers per hour) and total energy usage per day (Watt*Hours per day is an amount, like kilometers driven per day).
For example, say you are in Lago Nigeria:
http://www.solarelectricityhandbook.com/solar-irradiance.htmlLagos
Measured in kWh/m2/day onto a solar panel set at a 84° angle from vertical (6 degrees from horizontal) :
Average Solar Insolation figures
(For best year-round performance)
3,600 Watt array...Jan Feb Mar Apr May Jun 5.80
5.72
5.34
5.00
4.71
4.02
Jul Aug Sep Oct Nov Dec 3.91
3.85
3.91
4.59
5.32
5.77
- 3,600 Watt array * 0.52 off grid solar eff * 3.91 hours of sun per day (September) = 7,320 Watt*Hours per day (Sept long term average)
- 7,320 WH per day / 2,000 Watt load = 3.7 hours
- 800 AH * 48 volts * 0.50 max planned discharge = 19,200 WH of "usable" storage
- 19,200 WH / 2,000 Watt load = 9.6 hours to take battery bank to 50% capacity
- 19,200 WH (50% discharge) / 7,320 WH per day (Sept) = 2.6 days to recharge
The second guess is that the batteries were being recharged at too high of voltage, and they overheated multiple times/days/weeks (hot batteries, and/or lots of gassing/bubbling in cells during charging). The above members were asking about a "remote battery temperature sensor"... When lead acid batteries get hot, the charge controller is supposed to reduce the charging voltage to the battery bank. Basically, a 35C battery bank would be:- Assume 59.0 volts charging, 35C battery temperature
- (35C temp - 25C room temperature) = 10C rise
- 10C rise * 0.120 volts per degree C = -1.20 volts (for hot batteries)
- 59.0 volts standard temperature charging voltage - 1.20 volt offset = 57.8 volts @ 35C actual charging voltage
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed