Two inverters???

I am setting up an off grid battery back up system and I want to run my AC 1hp well pump and a chest freezer and two refrigerators at a minimum.
My pump is 240vac that requires 9.8 amps (call it 10a) at startup. So 2400w.
My freezer and refrigerators will draw less than 1500w at 120vac combined.
But I’ve found that without spending a small fortune I can’t get an inverter that will do both. So I was thinking about running two inverters. One for the well and one for the rest.
I have a 48 volt battery bank that is set up in 2 strings of 4, using Eight 12v 200ah SLA batteries.
I have 1200 watts worth of pv panels and a solid off grid solar charge controller.
What am I about to do wrong?
Comments
Your well pump. Is going to need a 4kw inverter with a large surge rating. It takes a $400 AC peak hold meter to read your starting current the inverter needs to supply, and if you have the option to only run the pump when you need to fill a tank, that makes things a lot more flexible. My 1/2 hp pump, consumes 1kw, as measured by my inverter (that's Volt-Amps, since it's a motor, not simple watts)
48A @ 230V starting = 11Kw surge capacity for your inverter. That's why I run a 6kw inverter to manage my 1/2 hp pump, which has to run every day !
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
The XW's that are currently on the market are 6.8KW continuous, 8.5KW for 30 minutes and 12KW for 60 seconds. Alot higher power for the short time it takes to start a well motor. At some point in this, the battery becomes a factor if it is too small. (below 400AH).