Back to wiring .............
Chris11
Registered Users Posts: 130 ✭✭
I bought some 2 gauge wire as suggested by Bill to run from the CC to the bats for my new 2000 watt system. By the way this wire is like some stranded copper running through the middle of pvc pipe, unbelievably stiff. I hate it but I got it installed. So in true style I didn't buy enough. I really don't want to go back to Homedepot (virus) so here's my question.
I have enough 4 gauge to run from the CC to the ground side of the bats. Is it Okeydokey or baddywaddy to go to a smaller wire temporarily? It would be about 2.5 feet.
Thanks, Chris
Comments
-
It is fine... You could also put 2x 4 AWG in parallel, and that is the equvalent as 1 AWG (for every "doubling" in wire cross section area, the AWG drops by 3 units).
2 AWG is conservative (as I recall).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
What you purchased is likely RW 90 or similar which is usually 7 strand and difficult to bend in short radius, welding cable is easier having hundreds of strands but the insulation is generally thicker.
If you have enough #4 you could parrallel for the time being, that would be larger in cross section than #2, not the best practice but would be better ran a single #4 and far better than getting sick.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
I don't have enough 4 gauge to double up so I'll just try one. I have no idea McGivor what they sold me but my analogy of wire through pvc pipe is accurate. When I stripped off the insulation it was like a very hard piece of plastic. That was just one of many difficult things that I encountered while doing this simple rewiring job ....and the easiest and nicest was using the cheap plastic tool to disconnect all the MC4 connectors. Strange that using the $2.00 crappy tool was the nicest thing that happened all day .... lol.Tomorrow I have to monkey around with the new combiner since it's larger than my old one so I have to do some recombobulating to make everything fit. ( Ya like that word? )Thanks, Chris
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed