combine solar panel wirh batteries
robocop
Registered Users Posts: 118 ✭✭
At last got 500w 48v solar panels and 8 12v 250 ah solar batteries now a 48v battery pack
Have a 5.5kw continiuos hybrid inverter also 48v
First would like to know how to connect to form the 48 v panels to stay with the 48v.
would like advise
Robert
Have a 5.5kw continiuos hybrid inverter also 48v
First would like to know how to connect to form the 48 v panels to stay with the 48v.
would like advise
Robert
Comments
-
Need exact Vmp and Imp of panels. And exact brand/model/type charge controller.Rough min and Max temperatures for your area would help.Length of cable run from array to charge controller.How many 500 watt panels.Mix and match work any existing panels?Etc.BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
-
Generally, for a 48V system, you will need at least 2, and often 3 panels in series, you want to feed a MPPT controller about 80 or 90V, so it can do it's downconversion. And it's likely you will need a 150V rated controller, because in cold weather, 90v of panels can produce 120V open circuit before the controller starts up. A 100V controller would be fried.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Hi mike some info each panel is 500w vmp 58,95 imp 10,87 voc 48.63 isc 10.28 max fuse 15a operating temp -40 to +85c
battery is gel battery 12v 8 pcs so far I know can make 48 v 500ah in 2 packs
inverter is a 5,5kw continius hybrid must ph1800 max batt discharge is 150a charging 60a
do have all components to begin to install , have also 2 extra 500w panels
if more inf needed let me know this is Caribbean temp is abot 30-34 C sometimes under 30 C
thnks for reading
Bob
-
Do you have a link to the inverter/solar charger?And it looks like you have Vmp/Imp values swapped with Voc/Ioc.Looking for min/max Vpanel input voltages. Usually Vmp 72 volts or over... And if you have Voc over 140-150 volts is common.To panels in series (and a bunch of strings on series (each parallel string with a series fuse or breaker in a combiner box) should be ok.Details matter.BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
-
hi bill each panel is 500w vmp 58,95each panel is 500w vmp 58,95V imp 10,87A voc 48.63V isc 10.28 A
-
Spec open circuit voltage (Voc) is always higher than voltage at max power (Vmp) because voltage drops as the panel warms in the sun.
In sizing strings, you need to adjust Voc (~59v?) up to adjust for the record low temperature at your location so the string voltage won't be higher than the controller max input voltage.
Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Robocop,
If you can also link to the inverter-solar-charger product/specifications/manual, that would help... Really need to mix/match everything together. I.e., the array operational voltage range needs to match both the inverter's Vpanel input range, and (many times) the battery bank voltage too (12/24/48 volt all usually have different minimum array voltages).
I don't know anything about your inverter-solar-charger product.... Need the details.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed