Problem with Xantrex Inverter/Charger

My Xantrex inverter/charger has stopped picking up any charge from my Honda HX 4000 generator. Always worked before. Have serviced generator. Any suggestions as to possible cause. 

Comments

  • Estragon
    Estragon Registered Users Posts: 4,496 ✭✭✭✭✭
    I'd start by measuring generator AC output voltage and frequency.  If possible, I'd also check inverter transfer switch operation using a different generator or AC source.
    Off-grid.  
    Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
    Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
  • BB.
    BB. Super Moderators, Administrators Posts: 33,613 admin
    Some starting suggestions:
    • Get a Kill-a-Watt meter or Digital Mulimeter and measure the line voltage (~208 to 264 VAC nominally 220-230 VAC, 50 +/- 5 Hz) (guessing Spain?). If the generator frequency or voltage is out of range, the inverter-charger will not "connect".
    https://www.amazon.co.uk/s?k=kill+a+watt&ref=nb_sb_noss (most Kill-a-Watt type meters display voltage, current, Watts, frequency, etc.)

    And there are volt meters with frequency measurement capability (below are AC+DC Current Clamp DMMs... They make current measurements very safe and easy):

    https://www.amazon.com/gp/product/B019CY4FB4 (Current Clamp DMMs run from USD$50 to $350+)
    https://www.amazon.com/gp/product/B07546L9RT (cheap meter)

    If the genset is not within range, and you cannot easily adjust, try putting on a 100 Watt light bulb or small electric heater (any stable load) and see if this stabilizes the output voltage for connection.

    More than that, probably need to know the exact Xantrex inverter-charger model.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset