M50 meter ?s
antiquepedaler
Registered Users Posts: 1 ✭
I used Power down to 10.5 running the furnace. Now the meter shows an X over the battery. The system seems to be charging as I’m showing 11.8. But the X is still there. Also the battery picture has never shown more than half full. What do I need to do?
Comments
-
Welcome to the forum AP,
I am not sure what the "X" is based on... So, lets do some basic debugging.
If you have a volt meter, check the battery voltage. Does it read ~12.4 volts too? If yes, at least the display is correct.
How big is your battery (12 volts at XXX Amp*Hours)? What is your solar a-rray Wattage?
Many times, when a charge controller sees the battery fall below ~10.5 volts (sometimes 11.5 volts, depends on configuration), it will turn of the LVD output (low voltage disconnect). The Charge Controller will not turn on the LVD output until the battery is >~12.7 volts (battery is being successfully/actively recharged).
So, it may keep the LVD off until the battery bus voltage is >12.7 volts, and then the "X" should then disappear (guessing). The battery is still discharged, but it is on its way to recovering. To fully recharge the battery, you will need to see the bus voltage hit the absorb set point (~14.4 to 14.8 volts) and be held there for something like 4-6 hour to get the battery back to 100% State of Charge.
Knowing your solar array wattage, assuming middle of the day, sunny weather, clear of shading, etc., we can estimate the typical charging current (i.e., is 6.5 amps charging "good or bad"):- 6.5 amps * 12.4 volts = 80.6 Watts
And then based on AH of the battery bank... If 100 AH 12 volt battery bank taken to dead:- 100 AH * 1/6.5 Amps = 15 Hours of "charging" or 2-3 days at least (plus another ~3-6 hours of 14.x volts absorb)
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
What kind of battery, Lead Acid or Lithium ?
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed