SW4024 power Issues

Power cut out completely this morning. Got this fault warning:
Time | Action | Device | ID | Code | Description |
---|---|---|---|---|---|
2019/12/21 09:27:53 | Cleared | CSW4024 | 847509 | F47 | DC Under Voltage OK |
2019/12/21 09:27:44 | Set | CSW4024 | 847509 | F47 | DC Under Voltage |
Disconnected from load, batteries and grid. Left it disconnected from loads, connected to grid and batteries. Inverter started up, started charging as usual but only at about 3 amps, it usually is about 30 amps when first starting to charge in Bulk, and went to AC Good at 25.3 in just a few minutes which is unusual.
I have the charge setting at 180 minutes, Bulk Absorb at 28.6 and float at 26.8. It was at the normal Bulk voltage when it was charging.
I have a 24 volt Sun Frost refrigerator, turned it back on so that is the only load on the batteries and it seems to be working okay. Cloudy so only getting a few amps from solar array, batteries are still at low 25's voltage.
Any ideas on why the charge rate is so low and is there a fix or is the inverter done for?
Comments
A simple possible explanation might be something causing excessive voltage drop between the inverter and bank. Reading and comparing the above 3 values may help?
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
How old is the inverter?
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
It probably is the battery/connections causing LBCO. Combox and the config tool can log just about anything system wise.
The new gateway will have custom logging in the next firmware. The mobile app will also get lots of updates this coming year.
The CSW should have surge protection especially with a grid source.
htps://offgridsolar1.com/
E-mail [email protected]
htps://offgridsolar1.com/
E-mail [email protected]
Failing that, something in the voltage sense circuit?
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
htps://offgridsolar1.com/
E-mail [email protected]
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
I disconnected and separated the batteries overnight, hours of rest, and have a consistent 6.2 volts per battery. Had this reading last night and again this morning. Next I will turn on the inverter and see how the inverter charger and batteries act without the frig load.Then I will try and disconnect each compressor on the frig and see if I can determine if it is one of the frig compressors.
htps://offgridsolar1.com/
E-mail [email protected]