lithium batteries
Plucka
Registered Users Posts: 130 ✭✭
Is a 12 volt lithium battery made up of 4 x 3.2 volt units or 4 x 3.7 volt units to show a charge of 13.8 volts and a float of 14.4 volts?
Tagged:
Comments
-
The 3.2V nominal would be of different chemistry to the 3.7V nominal so the series charge voltage would differ accordingly. Normally the charging would be constant current until close to fully charged voltage is reached then it becomes constant voltage, a BMS would be used to limit charging current and or provide cell ballancing. This constant current / voltage may seem complicated but it's actually not, it means full current until
Lifepo4 has a nominal voltage of 3.2V per cell with maximum of 3.6V which coincides with 14.4V for a 4 series topography, the 3.7V nominal cells would likely be LIPO which typically would be arranged 3 series for a 12V battery with a maximum of 4.2V per cell or 12.6V for the string.
It is of extreme importance to limit the charging current when at the maximum limitations, either with termination, or by the preferred method with a BMS. For off grid applications it is common to program the charge controller to not venture into the upper voltages in order to improve the cycle expectancy, the same applies to the lower termination voltage, keeping within the 20 to 90% state of charge is typical.
Some operators rely solely on the charge controller along with inverter low battery cut out to achieve this, however having the added protection of a BMS is something I believe is important because it protects against not just the voltage but many other parameters. It must be noted that most inverters are designed for lead acid batteries so have LBCO well below the requirements of lLifepo4 which would destroy the cells.
The pre made packs such as drop in replacement type will most likely have an on board BMS along with specified charging voltages such as 14.4V for a 12V nominal lifepo4, this doesn't mean the terminal voltage couldn't be set lower to prevent long periods at maximum but it would be prudent to check with the manufacturer.
All the above is in general terms mainly concerning lifepo4, where my experience is, LiPo may be very similar however I think it's best to focus on a single chemistry to avoid confusion.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
So the answer is 3.2 volts x 4 is the normal 12 volt lithium battery size.
-
No, each chemistry within the lithium umbrella has different characteristics, LiFePo4 is one and it's nominal voltage is 3.2V per cell. There are advantages along with compromises along with different cell voltages for each type, LiFePo4 whilst not having the highest energy density are one of the safest, LiPo on the other hand has higher energy density but much more dangerous. Understanding the chemistry being used is critical to its use, this link
https://batteryuniversity.com/learn/article/types_of_lithium_ion explains in detail each type.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed