Troubleshooting 101.

hillside
Registered Users Posts: 149 ✭✭

Voltage had dropped from 54 to 39, about 25%.
I checked the oldest panel, a 5 yr. old Trina (all are 24 volt) and it showed 27volts...about right?
I can check for no voltage from a hot line but how to check these connections with 2 branch connectors?
How do I check if a negative to a positive is not functioning? These are all new MC4 's with electrical tape over them to keep rain out.
Appreciate any help, thanks
8- 235Watt panels, 2 strings in series/parallel, 4L16 Deka 6Volt, 370AH FLA. batteries, 3000W Cotek pure sine inverter, SRNE ML2440 40Amp Controller & 40 Amp Renogy controller, 24 Volt system.
5 stand alone PV arrays; 12V gate opener, 24V Dankoff rain water pumping system, 12V Shurflo rain water garden pumping, 12V bathroom LED lighting and fan.
4- 450 Watt panels with 4 L16 6 volt batts./ 2-Renogy Tracer 40 Amp controllers/ Xantrex 1800W PSW Inverter.
4- 450 Watt panels with 4 L16 6 volt batts./ 2-Renogy Tracer 40 Amp controllers/ Xantrex 1800W PSW Inverter.
Honda EU3000W generator for backup.
Comments
-
What, specifically, is the Vmp/Imp/Voc of the panels?
What is the battery bus voltage (charging/discharging/resting)?
Do you have the ability to measure current from your solar array (via the charge controller) or have a DC current clamp DMM?
If flooded cell batteries, do you have a hydrometer and specific gravity readings?
A hydrometer and a DC Current Clamp meter (really an AC/DC current clamp DMM--Digital Multimeter). Here is a nice midrange price/quality meter (you can find DC Current Clamp DMMs for less than $50 if you look around):
https://www.amazon.com/gp/product/B019CY4FB4
Note that DC Current Clamp meters need to be zeroed before you get accurate measurements.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Mixed panels, One Boviet 255W, Vmp 30.5, Voc 37.8One Trina 230W, Vmp 30., Voc 37.Two Hanwha 235W, Vmp 30.1 Voc 36.8I'm not sure what you mean by battery bus voltage. I have readings on the controller showing as much as 27.5 and have not seen it go below 24.0.Measuring current from solar array I do at the controller, 54volts, now 38-39VI use a multimeter and s specicif gravity tester.Specific gravity went down to 1.225 on all 4 new Deka L16 6volt, 370AH FLA's.---so I shut it all down, and first covered the panels with tarps. Am in the process of using a 6amp battery charger on each battery separately (cables disconnected)and have brought two (so far) up to 1.275, almost 1.300One more thing. I took the cover off the Trina and noticed that something had gotten hot enough to melt one the the 4 plastic/nylon connectors, (not sure what they are) that are close to the outgoing positive. But it is still showing 27 volts in the sun. Could that be it ?Maybe I could post a picture of it..8- 235Watt panels, 2 strings in series/parallel, 4L16 Deka 6Volt, 370AH FLA. batteries, 3000W Cotek pure sine inverter, SRNE ML2440 40Amp Controller & 40 Amp Renogy controller, 24 Volt system.5 stand alone PV arrays; 12V gate opener, 24V Dankoff rain water pumping system, 12V Shurflo rain water garden pumping, 12V bathroom LED lighting and fan.
4- 450 Watt panels with 4 L16 6 volt batts./ 2-Renogy Tracer 40 Amp controllers/ Xantrex 1800W PSW Inverter.Honda EU3000W generator for backup. -
If something got hot enough to “almost melt” one of the MC cable connectors (I’m assuming that is what it is, youhave a problem, and you need to figure out what it is...could be something as simple as an improperly plugged in MC cable connector, or a bad connector. If i had to guess, you high resistance connection at that connector, and it is trying to push the current of the entire string (the two panels) through that bad connection, dropping the production of that string significantly. I don’t know how big your battery bank is, but it sounds like you may be under paneled as well. Assuming your battery bank is 48 vdc, you are, on a good day pushing ~15 amps into the battery. That battery bank (assuming 48 vdc would like ~36-48 amps of bulk charge.
If you have them wired for 24 volts, they would like to see close to 90 amps or so. You are probably seeing no more than about 40 amps I would guess, probably somewhat less.
The only thing that kills batteries faster than over drawing, is undercharge current over time. If they don’t see enough current, they will stratify, and begin to sulphate. After you solve your current problem, look to double your PV if you want good service out of the batteries.
BTW, a 6 amp 6 vdc charger is barely enough for a float charge on those L-16, each one would like ~40 amps EACH.
Tony -
It is wired for 24 volts and I know the system is under paneled by the past comments. But the system is only used part time; a couple of washer/dryer (propane dryer) loads a week, TV use 4-5 hrs. at night and often the system goes 2-4 days with no use and the inverter is turned off every time it's not in use.So I'll need to upgrade but having just bought the SRNE 40A controller (good for 1100Watts at 24V) and bought wiring, connectors, etc. I'm told here I will need a bigger charge controller, larger size wiring and somewhere in the area of 1300-1400watts. (Currently at 920watts)Is it worth it for part-time use? And with the frequent lightning strikes here in summer I'm reluctant to lose it all in one strike.Everyone we know has lost electronics here even with the best of surge protection. It's because of multiple pulses of lightning strikes (the best I can describe what people say). First pulse wipes out the surge protection and the next the electronics.Could the Trina be problematic?8- 235Watt panels, 2 strings in series/parallel, 4L16 Deka 6Volt, 370AH FLA. batteries, 3000W Cotek pure sine inverter, SRNE ML2440 40Amp Controller & 40 Amp Renogy controller, 24 Volt system.5 stand alone PV arrays; 12V gate opener, 24V Dankoff rain water pumping system, 12V Shurflo rain water garden pumping, 12V bathroom LED lighting and fan.
4- 450 Watt panels with 4 L16 6 volt batts./ 2-Renogy Tracer 40 Amp controllers/ Xantrex 1800W PSW Inverter.Honda EU3000W generator for backup. -
If the J-box cover is melting, it is either bad/corroded/loose/etc. wiring terminals or a bad bypass diode.
Many panels have sealed J-Boxes--So you are left figuring out if you want to try for warranty repair/replacement or cutting the box open and sealing it back up after your repairs.
You need to get the batteries to ~29.0 to 29.6 volts, and hold it there for 2-6 hours (longer if batteries are deeply discharged).
If you do not see over 28.something volts during the day when charging--Either you are not supplying enough current (5% minimum, 10%-20% for full time off grid recommended) or it will take a few days to get your battery bank recharged (especially if 5% rate of charge).
Just to estimate your array output:- 4x235 Watts (average) * 0.77 panel+controller derating * 1/28.0 volts charging = 25.85 Amps (average "best case harvest" on cool/clear day around noon--panels pointing at sun)
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset - 4x235 Watts (average) * 0.77 panel+controller derating * 1/28.0 volts charging = 25.85 Amps (average "best case harvest" on cool/clear day around noon--panels pointing at sun)
-
If your loads are so small, consider reducing the battery bank size to better match the loads and the PV. It is a classic error to over battery small off grid systems as it gives one the false sense of security. What it usually turns into is an expensive lesson in battery failure. All three elements ought to be well balanced for good performance...Loads first, determine the battery bank, which in turn determines the PV/shore power charge regimen.
When I built my (current) system, I was drawn to using 4 L16’s wired for 12vdc, at todays cost of ~$1000. I decided to go with 4 t-105s at a cost of ~$600. It turns out that I use about 10-15% of ah capacity per day, and charge at ~ 30 amps, getting fully charged in about 2-4 hours of good sun. The financial equation was if the t-105s lasted 5 years and the l-16s lasted 8 I was money ahead with the t-105s. I am in year 12 with the t-105s and they seem to be going strong. They are used full time now about 4 months a year, used to be used 12 months.
My guess (once you get your current problem sorted) you will not see anywhere near the expected life from those batteries sorry to say.
YMMV.
Tony -
ok, thanks. Lots to think about. Here in the Caribbean there are limited sources and vendors of batteries. They're out there, but having just spent the $ on these I'm better off adding more panels. Buying from vendors stateside and paying for shipping almost doubles the cost. So buying from a supplier here that imports by the pallet load is the way to go, but you're limited by what they have in stock.
8- 235Watt panels, 2 strings in series/parallel, 4L16 Deka 6Volt, 370AH FLA. batteries, 3000W Cotek pure sine inverter, SRNE ML2440 40Amp Controller & 40 Amp Renogy controller, 24 Volt system.5 stand alone PV arrays; 12V gate opener, 24V Dankoff rain water pumping system, 12V Shurflo rain water garden pumping, 12V bathroom LED lighting and fan.
4- 450 Watt panels with 4 L16 6 volt batts./ 2-Renogy Tracer 40 Amp controllers/ Xantrex 1800W PSW Inverter.Honda EU3000W generator for backup. -
As you know, the batteries are the expensive part of the equation now...keep them happy and they will last a long time with your loading. Budget more PV and figure out how to get it there. Even considering shipping doubling the cost, PV is way cheaper than it used to be, and way cheaper to ship than L16s.
good luck, find your problem and keep in touch,
T -
hillside said:Measuring current from solar array I do at the controller, 54volts, now 38-39V
Current is not the same as voltage, voltage is inversely proportional to current, when the batteries are demanding maximum current it will drag the input voltage down, this is normal. A short circuit test will reveal maximum current at zero volts, an ammeter is required to measure current, see post 3.
The evidence of hest damage in the junction box could be caused by a loose connection, screw or dry solder, this may allow voltage reading to appear normal but cannot pass current, hense the short circuit test. Having the correct tools make trouble shooting so much easier.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Thanks again. So, let's say I remove the Trina 230watt panel and replace it with a new 235W and add two more panels which gives me 6 total, for about 1410watts.I'll need to replace the 40Amp SRNE controller with a 60 Amp size?Do I need bigger wire than the current 10AWG between panels? If so, what size?(24volt, 3000W Cotek pure sine inverter, 4- 6V L16 370AH batteries, currently with 920watts in panels)8- 235Watt panels, 2 strings in series/parallel, 4L16 Deka 6Volt, 370AH FLA. batteries, 3000W Cotek pure sine inverter, SRNE ML2440 40Amp Controller & 40 Amp Renogy controller, 24 Volt system.5 stand alone PV arrays; 12V gate opener, 24V Dankoff rain water pumping system, 12V Shurflo rain water garden pumping, 12V bathroom LED lighting and fan.
4- 450 Watt panels with 4 L16 6 volt batts./ 2-Renogy Tracer 40 Amp controllers/ Xantrex 1800W PSW Inverter.Honda EU3000W generator for backup. -
hillside said:Thanks again. So, let's say I remove the Trina 230watt panel and replace it with a new 235W and add two more panels which gives me 6 total, for about 1410watts.I'll need to replace the 40Amp SRNE controller with a 60 Amp size?Do I need bigger wire than the current 10AWG between panels? If so, what size?(24volt, 3000W Cotek pure sine inverter, 4- 6V L16 370AH batteries, currently with 920watts in panels)
Wiring wise, when increases in capacity are made its prudent to review the size of the conductors, but first there needs to be a plan, including current, voltage and distance, one step at a time is the best way to proceed.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Categories
- All Categories
- 224 Forum & Website
- 132 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 196 Solar Information links & sources, event announcements
- 894 Solar Product Reviews & Opinions
- 255 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 428 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 652 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 617 Discussion Forums/Café
- 310 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed