Learning curve
HotRod
Registered Users Posts: 82 ✭✭
Hey all! My battery just finished a bulk/absorbtion charge cycle, so I thought it would be a good time to check temps and SG. Here's what I got:
Temp on top in F. SG on bottom. 58°F ambient temperature.
Is this what I should expect to see?
Temp on top in F. SG on bottom. 58°F ambient temperature.
Is this what I should expect to see?
2 Schneider XW+ 6848 inverters
2 Schneider MPPT 80 600 Charge Controllers
Combox
40 335w Canadian Solar panels, 13.4kW array on an Iron Ridge racking system
1 big ass 24-85-27 refurbished forklift battery w/1430AH
2 Schneider MPPT 80 600 Charge Controllers
Combox
40 335w Canadian Solar panels, 13.4kW array on an Iron Ridge racking system
1 big ass 24-85-27 refurbished forklift battery w/1430AH
Comments
-
Forgot to mention the battery is a refurbished forklift battery. It's a 24-85-27, so 24 cells, 1430AH, lead acid.2 Schneider XW+ 6848 inverters
2 Schneider MPPT 80 600 Charge Controllers
Combox
40 335w Canadian Solar panels, 13.4kW array on an Iron Ridge racking system
1 big ass 24-85-27 refurbished forklift battery w/1430AH -
Battery A2 at 1.27 SG would be a candidate for Equalization charging... Ideally, batteries should be within 0.015 to 0.030 SG units from high to low cell(s). Over 0.030 difference, suggest EQ needed.
However, cells to differ and change SG limits over time. Doing EQ once a month, higher voltage charging until SG stop rising (and monitoring temperatures to ensure batteries do not overheat), then log the temperature corrected SG... That is your "new" 100% SoC.
EQ is hard on FLA batteries. You only want to do it when needed (SG differences, some mfg. suggest once a month, especially if "tall cased" cells).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Thanks Bill! The battery has only been online since the 27? of last month. Cell A2 was low of fluid when I checked it before start up. Altogether I added 1.5 gallons to top off all the cells. Not sure which ones took the most, I have a flow-Rite watering system on it, I just know that one was obviously low when I gave the thing a visual inspection.
So, should I do a forced equalization charge on it? I'm thinking I should wait til I have the temp sensor to do that though. I don't know. Suggestions?2 Schneider XW+ 6848 inverters
2 Schneider MPPT 80 600 Charge Controllers
Combox
40 335w Canadian Solar panels, 13.4kW array on an Iron Ridge racking system
1 big ass 24-85-27 refurbished forklift battery w/1430AH -
Roughly, a 0.100 SG change from ~1.27x to 1.17x SG units is the difference between 100% SoC and 50% SoC... So, a 0.030 SG difference is about 15% storage difference (State of Charge) between the high and low cell.
If you are not deeply cycling the battery bank at the moment, say down to (typically) 75% SoC (and not going to 40% SoC), everything should work OK--And exercising the bank and EQing after 30 Days of Service and see what you in SG at that time (with full EQ), it should not hurt anything.
Given that you have added a bunch of water, and this is a new (to you) installation, running an EQ to mix the water and electrolyte, and getting your first SG readings for your logs and verifying the battery is in good condition, would not be a bad idea.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Thanks again Bill. I have been setting the night time grid support voltage down to 49.5v, but it has yet to go below 50v. in the mornings its usually down around 51.5 - 52v ballpark. the panel says thats ~50% SoC. It's just 5 LEDs on the front of the inverter and at least 3 are lit every morning.2 Schneider XW+ 6848 inverters
2 Schneider MPPT 80 600 Charge Controllers
Combox
40 335w Canadian Solar panels, 13.4kW array on an Iron Ridge racking system
1 big ass 24-85-27 refurbished forklift battery w/1430AH -
FWIW, +1 on Bill's suggestion for an EQ. Ideally, I'd want a temp sensor controlling voltage vs temp, but if it's going to be a while I'd probably do the eq and monitor temp manually. "Warm" (say 80-90ish °F) is okay. "Hot" (eg. 110-120+°) means stop EQ.
The low cell is likely fine, just a bit of dilution not mixed in from watering, but IMHO it's important to establish a good baseline reading on a new bank. It probably won't take a heck of a lot of EQing to get the baseline reading.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
I EQed the battery yesterday as suggested. The hottest temp I got was 79.9 at the center of the bank. The low cell, A2, came up to 1.28SG. should I hit it again?
Few basic questions.
How often should I take SG and temp readings?
How often should I be adding water?
What should I be doing besides that?2 Schneider XW+ 6848 inverters
2 Schneider MPPT 80 600 Charge Controllers
Combox
40 335w Canadian Solar panels, 13.4kW array on an Iron Ridge racking system
1 big ass 24-85-27 refurbished forklift battery w/1430AH -
I generally check SG on every cell on long weekends (which is just ny way of remembering to do it), so about every couple of months. If I find a range of SGs, which I usually do, I EQ and check SG on the lowest couple of cells every 1/2 hour. When the SG stops rising on the low cells between checks, I stop the EQ. If the 1.28 cell stopped rising, that may be as good as it gets. I sometimes have to EQ over a couple of days depending on sun and loads.
I check water at the same interval as SG. If low, I might add a bit of water to be sure plates stay covered during the EQ, but as the acid can expand a bit I don't fill too full. On my L16s, about 1/4" from full (bottom of the fill tube) seems to work well.
Aside from that, just keeping things clean and getting to know your bank's "personality". Over time, if you watch things, you get to know what normal is for it with your specific usage.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
"I sometimes have to EQ over a couple of days depending on sun and loads." Can you elaborate on that a bit? Im assuming you meant that you run EQ on a given day and then do it again the next day, not allow the EQ to run all night unsupervised, right?2 Schneider XW+ 6848 inverters
2 Schneider MPPT 80 600 Charge Controllers
Combox
40 335w Canadian Solar panels, 13.4kW array on an Iron Ridge racking system
1 big ass 24-85-27 refurbished forklift battery w/1430AH -
If A2 stopped and did not exceed 1.280 SG--Then that is the "new" SG level.
Regarding the auto watering... You might want to turn it off and only autowater once a month or something like that (i.e., when doing monthly SG checks and EQ, ... SG first and make sure all plates are covered, do not fill now, EQ with SG check every 30-60 minutes until SG rise stops, then top off water. You do not want to fill to brim, then EQ (gassing and heat, electrolyte may spill out of cell(s).
Auto watering is nice, but I fear over filling and a stuck valve that overflows a cell (uncontrolled filling). Running auto water only when you are there (or at least do this for awhile until you trust that all is good)--Would be my suggestion.
As the battery cycles, SG levels will change, and can even rise over a few months of use/EQ cycles. Normally, you are trying for >90% SoC at least once per week. You are not trying for 100% (basically light EQ) every day--That is hard on the FLA batteries.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Thanks Bill. For clarity about the Flo-Rite watering system, it's just the float caps and connecting hoses. I manually water the whole bank simultaneously with a bulb hand pump. So I'm there when the watering takes place. I just have no way of knowing which cells are low and taking water. I've only watered it the one time. From what I'm gathering, once a month should be adequate, once I've learned the behavior of the equipment. I'm still learning and trying to develope my plan. I plan on gathering a set of readings early Monday morning before charging starts. Then do it again after the battery has been in float for about an hour. The temp sensor is going in as soon as my back will let me get back in the swing of things. Probably this coming week.
-Jason
2 Schneider XW+ 6848 inverters
2 Schneider MPPT 80 600 Charge Controllers
Combox
40 335w Canadian Solar panels, 13.4kW array on an Iron Ridge racking system
1 big ass 24-85-27 refurbished forklift battery w/1430AH -
I never EQ unsupervised. Sometimes if loads and/or weather means the sun goes while SG is still rising, I continue (ie by checking SG on the low cell(s) every 1/2 hr) the next day after bulk/absorb is done.
I'm sort of tempted by watering systems, but I do like to see if any cells are using more water than others. I guess I could still check with a system, but hand watering kinda makes me notice.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
You have 24x "identical" cells. You are, at first look, trying to find cells that are "different" from the rest. That could be low SG, could be high SG. Could be cell(s) using too much or too little water.
Ideally, you want to check the SG and water levels before your fill (and EQ).
When you see something "out of balance", then that is an indication to check further.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Thanks Estragon, my watering system came on the battery. I thought it sounded like a good idea, so I paid a $100 for the seller to leave it in place. And it's great for watering. Very easy, clean. The drawback is the need to remove it to check the SG and temps.
Thanks Bill, I believe I'll just start eyeballing the water levels weekly for a few weeks while checking the SG and temps. That should give me some idea of which cells are using water before I water the whole bank simultaneously.
-Jason2 Schneider XW+ 6848 inverters
2 Schneider MPPT 80 600 Charge Controllers
Combox
40 335w Canadian Solar panels, 13.4kW array on an Iron Ridge racking system
1 big ass 24-85-27 refurbished forklift battery w/1430AH -
" I plan on gathering a set of readings early Monday morning before charging starts. "
I didn't make it. got up too late, cause GoT.....LOL
2 Schneider XW+ 6848 inverters
2 Schneider MPPT 80 600 Charge Controllers
Combox
40 335w Canadian Solar panels, 13.4kW array on an Iron Ridge racking system
1 big ass 24-85-27 refurbished forklift battery w/1430AH -
The water levels looked good. All the plates were covered plus some. It was in the mid 40's last night so I'm not surprised by the battery temps. The little + and - signs are for when the reading was just above or just below the mark. Temps shot three times with an IR gun and took the average. The battery scale on the front of the 6848 says I'm at about a 50% SoC.2 Schneider XW+ 6848 inverters
2 Schneider MPPT 80 600 Charge Controllers
Combox
40 335w Canadian Solar panels, 13.4kW array on an Iron Ridge racking system
1 big ass 24-85-27 refurbished forklift battery w/1430AH -
Da panels.2 Schneider XW+ 6848 inverters
2 Schneider MPPT 80 600 Charge Controllers
Combox
40 335w Canadian Solar panels, 13.4kW array on an Iron Ridge racking system
1 big ass 24-85-27 refurbished forklift battery w/1430AH -
Cell D1 is a misprint. It was 1.305
2 Schneider XW+ 6848 inverters
2 Schneider MPPT 80 600 Charge Controllers
Combox
40 335w Canadian Solar panels, 13.4kW array on an Iron Ridge racking system
1 big ass 24-85-27 refurbished forklift battery w/1430AH -
If a .100 drop in SG is equivalent to 50% SoC, can i assume that every .01 drop is 5%? If true, is my battery actually only discharging to 85-90% SoC? After shopping digital SG meters, that $450 Schneider battery monitor aint looking so bad.2 Schneider XW+ 6848 inverters
2 Schneider MPPT 80 600 Charge Controllers
Combox
40 335w Canadian Solar panels, 13.4kW array on an Iron Ridge racking system
1 big ass 24-85-27 refurbished forklift battery w/1430AH -
Very roughly...
https://www.trojanbattery.com/tech-support/battery-maintenance/TABLE 1 State of Charge as Related to Specific Gravity and Open Circuit Voltage Percentage of Charge Specific Gravity Corrected To Open-Circuit Voltage 6v 8v 12v 24v 36v 48v 100 1.277 6.37 8.49 12.73 25.46 38.20 50.93 90 1.258 6.31 8.41 12.62 25.24 37.85 50.47 80 1.238 6.25 8.33 12.50 25.00 37.49 49.99 70 1.217 6.19 8.25 12.37 24.74 37.12 49.49 60 1.195 6.12 8.16 12.27 24.48 36.72 48.96 50 1.172 6.02 8.07 12.10 24.20 36.31 48.41 40 1.148 5.98 7.97 11.89 23.92 35.87 47.83 30 1.124 5.91 7.88 11.81 23.63 35.44 47.26 20 1.098 5.83 7.77 11.66 23.32 34.97 46.63 10 1.073 5.75 7.67 11.51 23.02 34.52 46.03 -Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Are there any "affordable" precision SG meters that can be reliably read to .001? I'd even go to float bulbs if I can gain accuracy.
If I am using less than 15% of my battery daily, how often should I be equalizing? Am I really using that little or am I fooling myself?
-Jason2 Schneider XW+ 6848 inverters
2 Schneider MPPT 80 600 Charge Controllers
Combox
40 335w Canadian Solar panels, 13.4kW array on an Iron Ridge racking system
1 big ass 24-85-27 refurbished forklift battery w/1430AH -
Consider a Refractometer for about $20 largeAnd I dont know if you call it "Affordable", but I really like the HydorVolt. Big numbers, Easy to read, Auto Temp comp. Mine agrees with both my refractometer and my float type hydrometer.
REC TwinPeak 2 285W 3S-3P 2.6kW-STC / 1.9kW-NMOT Array / MN Solar Classic 150 / 2017 Conext SW 4024 Inverter latest firmware / OB PSX-240 Autotransfomer for load balancing / Trojan L16H-AC 435Ah bank 4S connected to Inverter with 7' of 4/0 cable / 24 volt system / Grid-Assist or Backup Solar Generator System Powering 3200Whs Daily / System went Online Oct 2017 / System, Pics and Discussion -
Refractrometers are generally pretty accurate, no bubbles, floats. Just make sure the temp offset is set rightBut generally, after a couple months of living with the system,, you should be able to interpret the voltage and get close to your state of charge.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
You need a 1.265 (or similar) sg equivalent sample solution to calibrate the hydrometer.I don't think most will calibrate to 1.000 sg units pure water and measure 1,2xx sg.BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
-
MrM1,I like this. It happens to be the exact one from the link, LOL! But I'm still gonna order the bulb mentioned as well. It just looks easier to use.
Mike, thanks. I'm with ya on the couple months of watching it. I'm trying to build up a data base now. It's a steep learning curve.2 Schneider XW+ 6848 inverters
2 Schneider MPPT 80 600 Charge Controllers
Combox
40 335w Canadian Solar panels, 13.4kW array on an Iron Ridge racking system
1 big ass 24-85-27 refurbished forklift battery w/1430AH -
I considered a refractometer, but I'm waaay to much of a klutz to be holding something containing battery acid up to my eyeOff-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Well folks, here's what it looks like now after seven weeks in operation and 2 monthly EQs under it's belt. After charging and in float all the cells are around 85°F. My spread is .04 from highest to lowest and I'm not sure I'll be able to close that gap.
Last night, after 2 EQ cycles, A2 and B3 managed 1.29 SG. They were 1.29 after both the first and second EQ cycle so I stopped. Am I doing this wrong?2 Schneider XW+ 6848 inverters
2 Schneider MPPT 80 600 Charge Controllers
Combox
40 335w Canadian Solar panels, 13.4kW array on an Iron Ridge racking system
1 big ass 24-85-27 refurbished forklift battery w/1430AH -
I think you're doing it right. Assuming adequate EQ voltage, when your weakest cell(s) stop rising, that's about as good as it gets. No point stressing the stronger cells if you aren't improving the weak onesOff-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed