breaker keeps tripping on enphase system
Comments
-
Do you have an AC current clamp meter?In general, a 20 amp breaker will never trip below 17 amps (0.85 of name plate).May trip at 20 amps (minutes to hours).Above 20 amps, will trip faster, but usually takes many amps over 20).My first guess is that you have too many panels and gt inverters on one string (miss wiring?).Second guess is your 240 VAC line voltage is too low of voltage (closer to 210 vac or less... Possibly 208 3ph?).The third possibly is that you have a great micro inverter going bad that is occasionally putting a short circuit on the AC line.I had a central inverter that did this... But if this happens, I would expect that you would have a dead inverter after the first time (my inverter died after the first breaker trip).BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
-
Posting from Europe , got me a datasheet of the 190 version :
21 units alowed to either a "leg" or a "branch" with the 208V 3phase version ,
or 15 units with the 2x120V 240V Split Phase version .
Not sure , if the 210er is much different .
51/3 strings is 17 , therefore 50/5 sounds reasonable ,
but 50/3 a bit asynchonic .....
-
Solfyr,
What is the current rating of the branch circuit? The 208 circuit, is it >20 Amp breaker? Nominally, the same 190 version would output less current on a 240 VAC circuit vs a 208 VAC circuit (Power=Voltage*Current, higher voltage, lower current for same power/Watts).
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Curent rating :
Split Phase 240V : ACout Amps 0.8 (800 mA) -> x15 = 12 Amps
3phase 208V : ACout Amps 0.92 (920 mA) +> x21 = 19.32 Amps
-
Solfyr
I have an Enphase system on my house and monitor each panel on the internet. My 4k system is one string and that's all I need. If I had a bad Micro Inverter I would see it right away. I would think the M210 would be either dead or alive but that hasn't happened to me yet so good luck in tracking it down. BB
-
4000 W ÷ 250 W = 16 micros .
Usually , the output of Amps is less than the optimum , and therefore probably works with one more , than noted in the datasheet .
The OP has too many Amps being supplied into the one string of ?number of? micros .
Assuming Three Phase , it could be possible , that some crazy constellaton had been installed ,
like 13 East, 13 West , and 24 South , thus the southern string supplying too many amps occassionally ...
-
I expect the OP is long gone.
I am available for custom hardware/firmware development
-
Danger of Mismatch : The manual for the M190_M210 allows only 15 A max circuit breakers , but the next generation M250_M215 then allows 20 A breakers .
While the AC cable for Splitphase and Threephase is interchangeable at the former version , the later has different cables for Split and Three Phase .
External grounding wire not required anymore , for the non-original 250_215 , since inside the new Engage Wire .
For M190_M210 there is also an AC amps maximum given , that exceeds the "typical" AC-Aout in the datasheet by almost 15% , as for the M210-84-208-S1x typical 1000 would max at 1147 mA .
Imaginable is a mismatch of newer and older inverters , either by adding panels , or usage of old hoarded micros , together with newer ones , especially the original M215-60-2LL-S22 , that still needed Ground Electrode Conductor , and probably used the same AC cables , as the M190_M210 .
if installing a mix of IG (Integrated Ground) and non-IG microinverters, install the non-IG
microinverters closer (electrically) to the junction box to minimize GEC use
-
Does anybody know what normal wait time on the telephone with Enphase is for service? Also how quickly do they send out warranty parts?
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed