Weirdest thing Ever.
Comments
-
First off that aims is a boat anchor, get rid of it.
dont even consider the power jack, that thing is worse
magnasine and outback both make good inverters suitable
but what to do first....
pull all the weak batteries and charge them at 10% of capacity for about 6 hours at the manufacturers absorb setting, probably 14.3 volts.
during charging feel the sides of the batteries for a hot spot, better yet if you have an temperature gun check the sides of the battery about half way up the cells, a bad cell will be much hotter
record voltage of each battery
after charging let them set not connected for 2-3 hours
record voltage of each battery
if you find any that have sunk to 10 volts, that one is junk...it has a dead cell, very unlikely to recover
any down to 8-9 volts 2 dead cells...junk
shorted cells get very hot.
I get cell tower batteries free from cell companies, they are 105ah AGM made by cdtechnologies.
from each series string of 10 batteries I usually find one or two that have hot cells on charging maybe 15-20 degrees hotter than the rest, those are recycled immediately. I have never recovered a failed AGM. OK I will admit that I am in favor of FLA's...flooded as I can measure specific gravity and get 12-20 years from a set, mind you I have done electricity for 50+ years, I log all my batteries every month, s.g. readings , temperature of each cell during charging, temperature of every high current connection, etc. Systems fail due to LOM! Lack of maintaince.
enough said
get a more approiate inverter, skip the Chinese junk! The only Asian inverter that is worth buying is the Cotek, also rebranded as Samlex America
I think I would recommend the MagnaSine MS4448 If you don't really need 120/240 get the 120 volt one
i use a MagnaSine MS4024AE , 24 volt, 4kw unit 120/240 volt. and it works well, My next inverter will be a MidNite but they are still in development and not available yet
david2 Classic 150, 2 Kid, 5 arrays 7.5 kw total 2ea. 2S6P Sharp NE-170/NE-165, 1ea. 12P Sanyo HIT 200, 2ea. 4/6P Sanyo HIT 200, MagnaSine MS4024AE, Exeltech XP-1100, 2 Banks L-16 battery, Rolls-Surette S-530 and Interstate Traction, Shunts with whizbangJr and Bogart Tri-Metric, iCharger i208B dc-dc buck/boost converter with BMS for small form lithium 8S 16650 or LiFePO4, -
Forgot to mention, any sign of gassing during charging is a bad omen....its been cooked
AGM's should never vent
david2 Classic 150, 2 Kid, 5 arrays 7.5 kw total 2ea. 2S6P Sharp NE-170/NE-165, 1ea. 12P Sanyo HIT 200, 2ea. 4/6P Sanyo HIT 200, MagnaSine MS4024AE, Exeltech XP-1100, 2 Banks L-16 battery, Rolls-Surette S-530 and Interstate Traction, Shunts with whizbangJr and Bogart Tri-Metric, iCharger i208B dc-dc buck/boost converter with BMS for small form lithium 8S 16650 or LiFePO4, -
Have you given any thought to a 48v forklift battery of suitable size? Easy to check specific gravity, eliminates all the interconnections, can use an Anderson connector which provides a convenient disconnect when needed, most come in their own steel case which makes for easier placement, no exchange batteries required, you will own the scrap value at the end of life.
-
I'm going to scrap the whole system if I can ever get anyone on the phone at NAWS, I just can't catch anyone there because of my work schedule and their limited hours.
I am installing everything in a room off my garage so I want no venting batteries, and am looking at the Battle Borns just for that reason.
I am guessing 4KW will be plenty for everything in my house, I'm just trying to figure out if it can sustain the Mitsubishi zoned A/C system. Its one of those 'Happy wife, Happy Life' things.Aimes Power 12KW Inverter/Charger, 15-285W Panels in 5/3 config, Aimes Power 60A MPPT Controller. 12-200Ah Renogy Batteries in 4/3 config for 48Vs
Off Grid, Whole house system in the Mohave Desert. -
HRTanner said:I'm going to scrap the whole system if I can ever get anyone on the phone at NAWS, I just can't catch anyone there .................8 kW Enphase micros AC coupled to a SolArk 12K
-
no, I guess since I'm only an hour and half drive from them it would be easier to reach them, but I guess not.
Aimes Power 12KW Inverter/Charger, 15-285W Panels in 5/3 config, Aimes Power 60A MPPT Controller. 12-200Ah Renogy Batteries in 4/3 config for 48Vs
Off Grid, Whole house system in the Mohave Desert. -
What is the voltage and ah of your existing battery bank ?Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
48v, 600AhAimes Power 12KW Inverter/Charger, 15-285W Panels in 5/3 config, Aimes Power 60A MPPT Controller. 12-200Ah Renogy Batteries in 4/3 config for 48Vs
Off Grid, Whole house system in the Mohave Desert. -
HRTanner said:48v, 600Ah
So you HAVE to get your daily usage settled up right first. Do you have any sort of metering to measure what you are consuming??Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed