Voltage dropping too fast
roadrunnerjoe
Registered Users Posts: 2 ✭
i have a very simple 12V system I put together to use mainly as an alternative to my generator during power outages. It’s a 100W panel going through a 30A controller to two 35AH batteries and finally ending at a 1500W inverter.
The other night I used the system for a single LED light. The controller was showing 13V when I turned on the light but 90 minutes later the alarm started chiming and I was now seeing 10.4V.
Clearly something isn’t right. Is the inverter too much for what I need to it to do? Have my batteries quit? They are two years old and charge to 13.8V daily.
I appreciate any advice, thanks.
Welcome to the forum Joe.
Can you tell us a bit more about your AC inverter... It can take ~10-20 Watts itself, just being turned on and no load (tare loss).
And what are your "expectations" of power/energy (Watts and Watt*Hours) usage?
Personally, I like to design a "balanced" system. Loads drive the size of the battery bank. Battery bank and daily loads (and amount of sun for your location) define the size of the solar array.
I am guessing your batteries are near death... Flooded Cell Lead Acid batteries need to be stored charged, and recharged every ~1 month (if not float charged).
For example, a 1,500 Watt AC inverter needs ~100 AH @ 12 volts of FLA battery size for every ~250 Watts of inverter capacity (reliable system over time, temperature, partially discharge battery bank, etc.):- 1,500 Watts * 1/250 Watts * 100 AH = 600 AH @ 12 volt battery bank
- 70 amps * 1/20 hour discharge rate = 3.5 amps (for 20 hours, until battery "dead")
- 70 amps * 1/8 hour discharge rate = 8.75 amps (maximum recommended continuous draw)
- 70 amps * 1/5 hour discharge rate = 14 amps short term (minutes to ~1 hour)
- 70 amps * 1/2.5 hour discharge rate = 28 amps surge current (seconds to 10's of seconds)
- For example: 8.75 Amps * 12 volts * 0.85 AC inverter eff = 89 Watt @ 120 VAC average load for ~3-4 hours
Lead Acid Batteries should never be allowed to sit (stored) at less than 75% state of charge.
And to be properly recharged, you have a minimum amount of current needed. 5% for weekend/emergency usage, 10-13%+ for full time off grid usage:- 70 AH * 14.5 volts charging * 1/0.77 solar panel+controller derating * 0.05 rate of charge = 66 Watt array minimum
- 70 AH * 14.5 volts charging * 1/0.77 solar panel+controller derating * 0.10 rate of charge = 132 Watt array nominal
- 70 AH * 14.5 volts charging * 1/0.77 solar panel+controller derating * 0.13 rate of charge = 171 Watt "cost effective maximum" array
And how much energy can you harvest from your 100 Watt panel? Say fixed array near Philadelphia Pennsylvania:
http://www.solarelectricityhandbook.com/solar-irradiance.htmlPhiladelphia
Measured in kWh/m2/day onto a solar panel set at a 50° angle from vertical:
Here we are in December, a 100 Watt panel will produce (on average):Jan Feb Mar Apr May Jun 3.07
3.77
4.23
4.46
4.74
4.84
Jul Aug Sep Oct Nov Dec 4.95
4.79
4.55
4.21
3.12
2.77
- 100 Watts * 0.52 end to end system efficiency * 2.77 hours of sun (Dec) = 144 Watt*Hours of 120 VAC power per day
- 144 Watt*hours per day (Dec) * 1/24 watt AC load = 6 hours per day (night)
- 70 AH * 12 volts * 1/24 Watts * 0.50 typical max discharge = 17.5 hours to 50% state of charge on battery
Of course, I have make lots of assumptions, and skimmed over a lot of details--But the above gives you an idea of what to expect from your system for the Month of December.
I would suggest that you define what you want your system to do, and the design (on paper) a system that will meet those needs. Conservation is your friend here... I.e., a 10 Watt LED 12 volt lamp uses 1/2 the energy (or less) of a 9 Watt LED lamp on a 120 VAC AC inverter...
I will stop typing here. Ask more questions, correct my guesses, and we can go forward.
Quite low for lead acid battery while charging and quite high for after charging. Look into having your batteries tested.I am available for custom hardware/firmware development
This is great info Bill. The inverter is a 1500W MSW I got with the panel from Windy City. It has three outlets with individual on/off toggles and has a display for either current system voltage or wattage output. As I plan to use it mainly for outages, I don’t currently have output expectations but that is definitely something I will need to do. The batteries have been on the panel since they were purchased so they are charged full everyday, I have a feeling this may be my weak link. I tried charging a portable cell phone charger yesterday using a USB port so the inverter wasn’t even on and the voltage dropped to 10.4 in just under an hour. Once I unplugged the device the voltage steadily climbed back to 12.5. As jonr suggests, I think I’ll test the batteries. I guess I shouldn’t have expected much from Harbor Freight batteries. The numbers you provided based on location are probably pretty close using Philly as I’m up in New Hampshire and not getting much sun these days, just a couple hours above the trees. Thanks for all the info you provided, as always I’m open to any and all comments and I’ll let you all know about the batteries’ status.
You need to plan this system out!Do you want emergency lighting or to replace the grid in an outage?Virtually all LED lights are 12 v at the heart of the light, so get rid of the inverter if it is an emergency light..If you want grid replacement, you really need larger storage and a smaller inverter m the size to be determined by the sum of all the items you want on at the same time. Look at higher quality inverters, like Cotek, that give you specifications on power efficiency etci.e. a good inverter will have a surge rating that is ~ 2 times the continuously rated output.. like thisyou might be able to get away with a 200 W unit... http://www.cotek.com.tw/product_detail.php?prod_id=JCU5IyE=hope this helps.
Batteries are the "Heart" of your system. And they are the one piece of gear that if not treated "kindly", will have a very short life.
13.8 volts is usually about right for "float charging" your battery bank, but not great for fast/full recharging of a cycling battery (for flooded cell, closer to 14.8 volts for 2-8 hours or so, depending on how deeply discharged).
Here is some light reading on batteries:
http://www.windsun.com/Batteries/Battery_FAQ.htm
http://www.batteryfaq.org/
http://batteryuniversity.com/
After reading the above, you will probably be convinced that batteries do not work...
However, they really do work. Just need to understand their needs and limitations.
A nice system for emergency backup power (not for running your refrigerator) would be something like 2x 6 volt @ ~200 AH flooded cell golf cart batteries, a ~500 Watt maximum AC inverter (there is a very nice 300 Watt MorningStar TSW 12 volt inverter and others). And somewhere around a 377 Watt solar panel/array (10% rate of charge)+ appropriate charge controller.
Add a hydrometer to measure battery specific gravity, and an DC Current Clamp DMM to monitor/repair/understand your system...
I can give you links and the math, if you are interested. Golf cart batteries because they are pretty rugged, cheap, and forgiving (just check the electrolyte levels once a month). Great for the time (night, quiet time) when you are not running the genset during the day (refrigerator, water pumping, washing machine, etc. loads).