Backfed Breaker Sizing
climb_on
Registered Users Posts: 14 ✭✭
I am looking to install a 2nd array at my home and I am working out the 120% rule for backfed breakers, which I currently exceed. The 2nd system needs to be run through a separate inverter, meter & breaker, because of 2 different incentive programs.
First system, which is currently running, has a Solaredge SE10000-US inverter with a Max Output rating of 41a and a Max OCPD of 60a. With no plans for a 2nd array, I just rather blindly used a 60a breaker.
I have a 225a rated bus and a 200a main breaker. 225a x 120% = 270a - 200a = 70a available to back feed.
My proposed 2nd system will have a SolarEdge SE5000H-US inverter with a Max Output rating of 21a and a Max OCPD of 40a.
Do I need to size the breaker for the inverter's Max OCPD rating or for the Max Output rating?
However...IF I can size the breakers for the Max output of the inverters of 41a and 21a, respectively, with 45a and 25a breakers I would be right at 70a and satisfy the 120% rule.
First system, which is currently running, has a Solaredge SE10000-US inverter with a Max Output rating of 41a and a Max OCPD of 60a. With no plans for a 2nd array, I just rather blindly used a 60a breaker.
I have a 225a rated bus and a 200a main breaker. 225a x 120% = 270a - 200a = 70a available to back feed.
My proposed 2nd system will have a SolarEdge SE5000H-US inverter with a Max Output rating of 21a and a Max OCPD of 40a.
Do I need to size the breaker for the inverter's Max OCPD rating or for the Max Output rating?
However...IF I can size the breakers for the Max output of the inverters of 41a and 21a, respectively, with 45a and 25a breakers I would be right at 70a and satisfy the 120% rule.
9.8kW Array, (34) 290w Heliene Modules, SE10000a SolarEdge Inverter. 8/12 pitch steel roof. NABCEP PVA. Minnesota.
Comments
-
What kind of breaker panel do you have?
A 25 amp tandem breaker may be possible but I don't know about a 45 amp.
You may just need to take some actual readings.
Also your breaker needs to only run at 80% of its rated capacity. Say you had a solar system that made 100 amps, you would need at least 120 amp breaker.Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.
Solar roof top GMC suburban, a normal 3/4 ton suburban with 180 watts of panels on the roof and 10 amp genasun MPPT, 2000w samlex pure sine wave inverter, 12v gast and ARB air compressors.
-
Thanks. I have an Eaton panel. I'm not familiar with tandem breakers....will look into it. If the breaker needs to be sized at 80% then I'm over the limit and would need to look at derating the main I think.9.8kW Array, (34) 290w Heliene Modules, SE10000a SolarEdge Inverter. 8/12 pitch steel roof. NABCEP PVA. Minnesota.
-
The purpose of an over current device is to protect the conductors, be it a branch circuit or a bus bar, let's use hypothetical values, the total current capacity of all the branch circuit breakers in the in the panel probably exceeds the value of the main breaker, rationale is, it would be highly unlikely to have all circuits are drawing maximum load at any one time. So let's put some numbers into the picture, say the load during the day is 100A, a high nominal figure, the grid tied inverters are producing 70A, the loads would absorb the 70A and only 30A would be pulled from the grid to supplement the deficit. Now the loads decrease to 10A, the inverters are now pushing 60A into the grid, 10A to the loads, so the main breaker is in effect reverse current flow. As the inverters could never exceed the capacity of the grid, the main breaker is well within its limitations, but now someone uses an auger to mount a post, accidentally severing the inverters supply conductors, the breaker protecting tthe conductors should be of an amperage rating less than that of the source of highest potential, the grid, but not exceeding that of the branch circuit conductors, 70A in this case.
The rated current carrying capacity of conductors is very conservative but remember the purpose of the over current device is to protect the conductors from the source of highest potential, so the feed in breaker could be of a higher value than the inverters could produce but not exceeding that the conductors used. Say in the case the distance between the inverters warrant a larger gauge to prevent voltage drop, it would be possible to increase the gauge but the OCP should not exceed the current carrying capacity of the conductors, obviously it could be less. Hope this makes sense
Edit. I should add the value of a branch circuit OCP should never exceed the value of the main breaker.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Thanks mcgivor that does make sense...mostly. My current inverter has max OCPD rating of 60a and 41a max output x 120% = 49.2a. So a minimum of 50a breaker to max of 60a breaker, depending on conductor size and distance (my run is about 10'). So 50a would be fine.
On the proposed 2nd system I would need a 25a (21a max output x 120% = 25a).
So 50a and 25a = 75a and is still over the max of 70a available to backfeed. Looks like I either need to size a smaller 2nd system or derate the main.
How do I determine if I can derate the main breaker?
9.8kW Array, (34) 290w Heliene Modules, SE10000a SolarEdge Inverter. 8/12 pitch steel roof. NABCEP PVA. Minnesota. -
Read this it will help explain a few things https://www.mikeholt.com/nec-conductor-sizing-and-protection.php there are many factors to sizing which are in the electrical code which I personally won't quote.
This thread will help you with the derating main breaker questions http://forums.mikeholt.com/showthread.php?t=1684481500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Thank you sir. I will take a look.9.8kW Array, (34) 290w Heliene Modules, SE10000a SolarEdge Inverter. 8/12 pitch steel roof. NABCEP PVA. Minnesota.
-
You only need a tandem breaker for 240v inverter. But for that size it should be 240v.
Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.
Solar roof top GMC suburban, a normal 3/4 ton suburban with 180 watts of panels on the roof and 10 amp genasun MPPT, 2000w samlex pure sine wave inverter, 12v gast and ARB air compressors.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed