array ground wire

wellbuilt
wellbuilt Solar Expert Posts: 763 ✭✭✭✭
Could any one tell me what size wire I need to run from my array to ground .
I have 10g PV wire for my -+ could I just mark a black POV wire with green tape
Out back  flex power one  with out back 3648 inverter fm80 charge controler  flex net  mate 16 gc215 battery’s 4425 Watts solar .

Comments

  • Photowhit
    Photowhit Solar Expert Posts: 6,006 ✭✭✭✭✭
    I thing 6 or 8 gauge s usually called for, 6 gauge bare ground wire is reasonably cheap and can often be bought by the foot.
    Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites,  Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
    - Assorted other systems, pieces and to many panels in the closet to not do more projects.
  • wellbuilt
    wellbuilt Solar Expert Posts: 763 ✭✭✭✭
    Would I run the bare copper wire in my 1” conduit to the combiner box ?
    And how many 10 g pv wires am I aloud in 1” conduit