Does anyone have a source for dealing with Inverter hook up to a manual transfer switch?
Tes42
Registered Users Posts: 7 ✭✭
Hi guys, new member here and I been reading furiously the last few days some old posts and I was wondering if I am missing the solution to my questions. Basically, I don't know what inverter to by for my situation, and confusion around how to rewire the connected neutral and ground wire bond that is in my homes breaker panel. Or optionally I would rather just by an inverter that does not have a bonded neutral.
Background details:
Right now my system is bare bones a couple 100 watt 18V panels wired in series (my plan is to add in pairs as I expand), and two AGM 12V 100AH batteries, and a third in the near future wired in parallel to maintain a 12V system. Intended to only power some of the 15 Amp branch circuits of my house (no microwave, no refridge, no washer ect.). And for days when I may not have enough sun I installed a manual transfer switch:
Thanks.
Background details:
Right now my system is bare bones a couple 100 watt 18V panels wired in series (my plan is to add in pairs as I expand), and two AGM 12V 100AH batteries, and a third in the near future wired in parallel to maintain a 12V system. Intended to only power some of the 15 Amp branch circuits of my house (no microwave, no refridge, no washer ect.). And for days when I may not have enough sun I installed a manual transfer switch:
Reliance Controls Corporation 31406B Pro/Tran 6-Circuit Indoor Transfer Switch for Generators Up to 7,500 Running Watts
To cover some of these loads (small ranch home) I don't think I need too much more than 600 watts but I may be interested in getting up to a 1500watt sine wave inverter (if needed in the future), can anyone recommend some details as to an inverter that can work in my situation? Also if I have to unbond the neutral wire in my breaker box is there a schematic showing how to do this?Thanks.
Comments
-
To clarify - is this a totally off-grid (not a backup) system?
What kind of generator?Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
This is totally off-grid, and no generator. I do get all my power now from my electric company and I will still be using that power for most of my house, except for a few branch circuits that I hope to power through the manual transfer switch.
-
You are on the exact right track with the Reliance Controls gear, but wondering why you are considering the 31406 B?
Have you considered the 306C as it has circuit breakers for the incoming solar loads and 3 position toggle switches for transfer. I use the 10 circuit 50 amp version. Works flawlessly. Look at the manual, as it describes how to handle the load, neutral and ground. But you will need to get an inverter that is 240v Single Split Phase or you will have to do some rewiring inside the Pro Trans as they are rated for 240v Single Split Phase and NOT for just 120v.
But IMHO, you are starting kinda backwards. The first thing you need to do is some actual load calculations to determine the actual loads you want to run. You say you need 600 watts. Is that per hour? Per day? 200 Ah's of battery is good for 1 200 Watt hours at 50% DOD best case. How many Watt Hours (not Watts) will you be needing for a 24hr period. This will determine battery bank size, number of panels, and inverter size. I would say for safety sake you don't need more than a 1000W inverter on a 12v battery. Here is why ...
1000W / 12v = 83 amps
1500 W / 12v = 125 amps
At 1000W you will need #3 gauge battery cable for all series / parallel connections and connection to the inverter. 1500W will take 1/0 all the way thru.
Also not sure if you care, but if you are wiring this inverter into the house for a few branch circuits thru the main panel, it needs to comply with UL 1741 standards or if you burn the house down, insurance will not pay.
REC TwinPeak 2 285W 3S-3P 2.6kW-STC / 1.9kW-NMOT Array / MN Solar Classic 150 / 2017 Conext SW 4024 Inverter latest firmware / OB PSX-240 Autotransfomer for load balancing / Trojan L16H-AC 435Ah bank 4S connected to Inverter with 7' of 4/0 cable / 24 volt system / Grid-Assist or Backup Solar Generator System Powering 3200Whs Daily / System went Online Oct 2017 / System, Pics and Discussion -
The biggest concern I do have is your last point. The transfer switch does not seem to mention using an inverter only a generator so there is my concern, and then when I read things about how inverter split voltage on both the line and neutral and these can't be used, or if they can they need a feature internal adjustment I think, and this is where I need most help.
I agree that all I need is < 1000W inverter in my case. I did do the calculations for three rooms of my house running lights only and since I run all energy saving florescent spiral type bulbs my calculated amps were low. I did not figure in battery bank size since I figured I can flip back to line voltage when needed and expand that in the future. I had the following notes:
Kitchen Lights 40W x 6 hours = 240W
Dining RM Lights 30W x 6 hours = 180W
Living RM Lights 40W x 6 hours = 240W
Total: 660W x 1.5 (loss factor) = 990W hours
990W x 2 (50% discharge) = 1980W / 12V = 165Ah (one days worth of storage)
I did buy 2 AWG to parallel the two batteries, and I will double check these figures on the 2 AWG.
As far as my Transfer switch it seems to be similar to the one you mentioned here is a image of it:
-
I'll just speak to the inverters without neutral ground bonds. Most inverters that are UL 458 (mobile use) will have an internal bond. There are a few pure sine wave inverters that will have a detachable bond, like the Exeltechs, down to the 600 watt XL line are hard wireable and have a detachable neutral ground bond. It appears they company still has a $100 rebuild if rebuild able policy, making used units attractive. I use the 1100 watt unit and it's quite nice in that range. It does use about 16-18 watts per hour in the 24 volt version.
It's not unusual to find them in the $2-300 range on eBay, nothing currently... A couple have sold in the $150 range this year.
In addition all UL 1741 inverters, for household use will either not be bonded or be detachable.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
> @Tes42 said:
> This is totally off-grid, and no generator. I do get all my power now from my electric company and I will still be using that power for most of my house, except for a few branch circuits that I hope to power through the manual transfer switch.
To be clear, this is not totally off-grid. You have grid power, and if I understand the transfer switch operation, it will backfeed generator (or inverter) power to the grid. Aside from fire risk, a lineman trying to restore power in an outage is unlikely to thank you for making a wire unexpectedly live.
What you want is a fairly simple lockout panel that lets you run a few circuits from either grid, or a generator/inverter, wired such that loads are connected to one or the other, but never both. If you want circuits to run off inverter only, you don't even need a switch, just a panel serving those loads from the inverter.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Estragon said:To be clear, this is not totally off-grid. You have grid power, and if I understand the transfer switch operation, it will backfeed generator (or inverter) power to the grid. Aside from fire risk, a lineman trying to restore power in an outage is unlikely to thank you for making a wire unexpectedly live.
@Tes42 Not sure why you would want the one with push button trips rather than the 15 amp hardware store replaceable breaker model.
REC TwinPeak 2 285W 3S-3P 2.6kW-STC / 1.9kW-NMOT Array / MN Solar Classic 150 / 2017 Conext SW 4024 Inverter latest firmware / OB PSX-240 Autotransfomer for load balancing / Trojan L16H-AC 435Ah bank 4S connected to Inverter with 7' of 4/0 cable / 24 volt system / Grid-Assist or Backup Solar Generator System Powering 3200Whs Daily / System went Online Oct 2017 / System, Pics and Discussion -
Well yeah I agree the push button setup I got looks odd now that you say that but I was trying to save a few $$. Functionally though I think its very similar if not almost the same.
-
Photowhit said:I'll just speak to the inverters without neutral ground bonds. Most inverters that are UL 458 (mobile use) will have an internal bond. There are a few pure sine wave inverters that will have a detachable bond, like the Exeltechs, down to the 600 watt XL line are hard wireable and have a detachable neutral ground bond. It appears they company still has a $100 rebuild if rebuild able policy, making used units attractive. I use the 1100 watt unit and it's quite nice in that range. It does use about 16-18 watts per hour in the 24 volt version.
It's not unusual to find them in the $2-300 range on eBay, nothing currently... A couple have sold in the $150 range this year.
In addition all UL 1741 inverters, for household use will either not be bonded or be detachable.
-
Estragon said:> @Tes42 said:
> This is totally off-grid, and no generator. I do get all my power now from my electric company and I will still be using that power for most of my house, except for a few branch circuits that I hope to power through the manual transfer switch.
To be clear, this is not totally off-grid. You have grid power, and if I understand the transfer switch operation, it will backfeed generator (or inverter) power to the grid. Aside from fire risk, a lineman trying to restore power in an outage is unlikely to thank you for making a wire unexpectedly live.
What you want is a fairly simple lockout panel that lets you run a few circuits from either grid, or a generator/inverter, wired such that loads are connected to one or the other, but never both. If you want circuits to run off inverter only, you don't even need a switch, just a panel serving those loads from the inverter.
Someone MUST have a tutorial on this? But then again maybe not too many people do it this way.
-
Although off-grid, I have a similar setup controlling which of two separate inverter systems is used for a number of circuits. It allows me to turn off my big inverters overnight and run lights etc on a small inverter which has much lower standby losses.
If the switch you have is UL rated for this use, it must be ok. On mine, there is a breaker for each inverter AC source, and a metal lockout making it impossible to have both breakers closed at the same time.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Tes42 said:Well yeah I agree the push button setup I got looks odd now that you say that but I was trying to save a few $$. Functionally though I think its very similar if not almost the same.
https://www.ebay.com/itm/NEW-RELIANCE-CONTROLS-306A-PRO-TRAN-2-6-CIRCUIT-POWER-TRANSFER-SWITCH-KIT-30-AMP/401508248264?epid=2255911471&hash=item5d7bc1aac8:g:v4gAAOSw~OVWv1en
Not much more than what you are wanting to pay I dont think. I would just rather have the breaker model because it would be more easily user serviceable.
As to an inverter, what is your budget?
REC TwinPeak 2 285W 3S-3P 2.6kW-STC / 1.9kW-NMOT Array / MN Solar Classic 150 / 2017 Conext SW 4024 Inverter latest firmware / OB PSX-240 Autotransfomer for load balancing / Trojan L16H-AC 435Ah bank 4S connected to Inverter with 7' of 4/0 cable / 24 volt system / Grid-Assist or Backup Solar Generator System Powering 3200Whs Daily / System went Online Oct 2017 / System, Pics and Discussion -
$500-$1200 or less but it almost seems like I need a more expensive one with a feature that allows un-bonding of the neutral in the inverter I am guessing but this is the part I am confused about.
I just sent out three emails to three separate inverter companies about this, see what they say IF they even respond.
-
If your up for spending $1,200 +/- ... I can't remember what battery voltage you needed, but you might as well consider the Schneider Conext SW series. All the models are Split Phase 120/240v. The only caveat to your budget might be that you would really also need the System Control Panel ... but shop around and price match ... I got my SW 4024 with SCP for just over $1450 (or something like that I cant recall now) 6 months ago. Heck if you were in FL and need batteries too I'd make you a good deal on my SW with batteries ... I want to sell it and upgrade to a 48v system
REC TwinPeak 2 285W 3S-3P 2.6kW-STC / 1.9kW-NMOT Array / MN Solar Classic 150 / 2017 Conext SW 4024 Inverter latest firmware / OB PSX-240 Autotransfomer for load balancing / Trojan L16H-AC 435Ah bank 4S connected to Inverter with 7' of 4/0 cable / 24 volt system / Grid-Assist or Backup Solar Generator System Powering 3200Whs Daily / System went Online Oct 2017 / System, Pics and Discussion
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed