Maximum Compensation Temperature (TS-45 Charge Controller)
Stuart
Registered Users Posts: 9 ✭✭
Thanks in advance. I am programming a TS-45 Morningstar charge controller for L16 Trojan batteries and there is one parameter that I am trying to understand: Maximum Compensation Temperature (and Minimum). They may just be the battery specification operating temperatures of -20C to +45C but the default TS-45 values are +80C to -40C which is wide so I am trying to make sure I get this right.
The TS-45 help file defines the Maximum Compensation Temperature as "Maximum temperature at which temperature compensation is clamped".
Any insight? Thanks
The TS-45 help file defines the Maximum Compensation Temperature as "Maximum temperature at which temperature compensation is clamped".
Any insight? Thanks
Comments
-
I'm not sure about the MS specifically, but my sense as someone who has written a bit of software in a past life is that these are "sanity check" values. Without them, a sensor failure or sotware bug could theoretically send charging voltage infinitely high or low.
The controller should increase voltage at lower battery temp, and decrease voltage at higher temps. Having a wide (but finite) range shouldn't be a bad thing. If the batteries are getting to anything like 80°C, you definitely want the controller dialing back voltage. If you never see battery temps less than -20°C, it wouldn't hurt to limit voltage increase there. Some inverters and other loads get picky about voltage when compensated to really cold temps.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Estragon, Thank you for your comment and I agree that the compensation needs to be limited. The question now is whether to use the battery operating temperatures for the min and max or the default controller values. Thanks again for your input.
-
Compensating based on a remote sensor attached to the bank is the better way to do it. Batteries are a large thermal mass.
If the bank is even getting as warm as 45°C, you likely have a problem. I would leave it at the default so it keeps reducing voltage at higher temps.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
DEFAULTS:
Maximum Compensation Temperature = All temperatures above +80C, will be treated as if they were +80C
Minimum Compensation Temperature = All temperatures below -40C, will be treated as if they were -40C
If your Charge Controller will be connected to your battery bank AND
your Battery Bank's temperature will be above +45C, or will be below -20C,
then enter the temperature values for your battery.
Changing these limits is not "critical" to normal operation.
My battery bank will never be above +45C / +113F,
and won't be much below -20C / -4F,
so the DEFAULTS work just fine for me.
Many battery banks will get cold in the winter,
but are you really planning on letting the temperature of your battery bank climb above +45C / +113F ?
-
Agree with @Estragon, leave it at default, the controller will compensate both ways, hot or cold, ensuring a corrected voltage, also use the voltage sence input provided for more accurate results.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Great information, thank you very much. I will leave the values at the default settings. I appreciate your expertise and time.
-
If you are in a very cold climate (arctic)--Then setting the minimum temperature may be required. Using numbers:
- (-40C+20C nominal)*-0.005 volts per degree C per cell * 6 cells (aka 12 volt battery) + 14.75 volts nominal charging = 16.55 volts charging (@ -40C)
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed