Math check on battery usage
solomon_says
Registered Users Posts: 6 ✭✭
12V x 100Ah = 1200W
I want to find out total watts for a single 12V 100Ah battery assuming 100% efficiency. Measuring a 60 W bulb for one hour, I can run the bulb for 20 hours?
Do I measure bulb usage in watts or watt hours? I don't need a sizing, I just need to know the math.
I want to find out total watts for a single 12V 100Ah battery assuming 100% efficiency. Measuring a 60 W bulb for one hour, I can run the bulb for 20 hours?
Do I measure bulb usage in watts or watt hours? I don't need a sizing, I just need to know the math.
Comments
-
Your formula is OK, except it has the wrong units.
12 Volts x 100 Amp-Hours = 1200 Watt-Hours
You must use the correct "units".
Also, Watt-Hours = Watts x Hours
Yes, you can run the bulb for 20 hours, but it will be very dim.
Typically, we run for 10 hours or less, then we stop.
Typically, we run until a specific "Low Voltage" is hit, then we stop.
EDIT: fixed typo! -
My battery is 12V and 100Ah. If V x Ah = Wh I will only have 100 watt hours?
-
solomon_says said:My battery is 12V and 100Ah. If V x Ah = Wh I will only have 100 watt hours?
DoD= depth of discharge= amount removed from that battery SoC= state of charge= amount remaining in that batterySo, 0% DoD= 100% SoC, 25% DoD= 75% SoC, 50% DoD= 50% SoC, 75% DoD= 25% SoC, 100% DoD= 0% SoCA/C= air conditioning AC= alternating current (what comes from the outlets in your home) DC= direct current (what batteries & solar panels use) -
I was confused cause mvas said 12V x 1200Ah = 1200 Wh.
If I know 1 battery has 1200 watt-hours, is it correct to calculate run time of a 60W light bulb if 1200Wh ÷ 60W? I read somewhere that watt-hours are found by V x Ah ÷ 100 so now I'm very confused. -
solomon_says said:I was confused cause mvas said 12V x 1200Ah = 1200 Wh.
If I know 1 battery has 1200 watt-hours, is it correct to calculate run time of a 60W light bulb if 1200Wh ÷ 60W? I read somewhere that watt-hours are found by V x Ah ÷ 100 so now I'm very confused.
DoD= depth of discharge= amount removed from that battery SoC= state of charge= amount remaining in that batterySo, 0% DoD= 100% SoC, 25% DoD= 75% SoC, 50% DoD= 50% SoC, 75% DoD= 25% SoC, 100% DoD= 0% SoCA/C= air conditioning AC= alternating current (what comes from the outlets in your home) DC= direct current (what batteries & solar panels use) -
solomon_says said:I was confused cause mvas said 12V x 1200Ah = 1200 Wh.
If I know 1 battery has 1200 watt-hours, is it correct to calculate run time of a 60W light bulb if 1200Wh ÷ 60W? I read somewhere that watt-hours are found by V x Ah ÷ 100 so now I'm very confused.
You are getting confused by mixing a time based figure with a value that has no time base.
Example
A 12V, 50 W lamp is required to operate for 10 hours from a 12v battery, what would the recommended battery capacity be, for a maximum 30% depth-of-discharge ?
Current is power divided by voltage, so 50/12 = 4.167 amps
Ampere hours would be current multiplied by time in hours, 4.167 × 10 = 41.67 AH
Battery size for 30% depth-of-discharge 100/30 × 41.67 = 138.9 Ah
Personally I prefer to do the electrical calculation first then involve the time, working with Ah and Wh together is confusing, batteries are sized in Ah. so easier to transpose.
So the 60W, 100Ah battery question.
60W/12V = 5 A
The 100 Ah battery is really 30Ah, for a 30% depth-of-discharge
Therefore 30Ah/5A = 6 hours running time to 30% DOD.
Of course this is a rough calculation, assuming full capacity etcetera, voltages would be slightly higher, therefore power higher, it's always better to be conservative, by increasing battery capacity, or reducing the run time.
Hope this helps.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
@mcgivor ok I finally see how the numbers work. Thanks for the help everyone, I think I'm getting smarter now
-
Fixed typo in message #2 ...
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed