Grid output drops to zero
Tumi
Registered Users Posts: 25 ✭✭
My system has almost been running for two weeks now and I've noticed that at least twice a day that my grid output drops to zero, or draws from the grid.
Here is a graph from today's production.
PV production= Purple
Grid output= Red
Load= Blue
Here is a graph from the battery, when the dips happend it goes to Bulk> absorption> then back to float within a short span of time
Here is a graph from today's production.
PV production= Purple
Grid output= Red
Load= Blue
Here is a graph from the battery, when the dips happend it goes to Bulk> absorption> then back to float within a short span of time
Comments
-
@Tumi
It looks very much like you're losing power from or at least connection to the grid for those short durations. Looks like a Schneider XW or CSW hybrid system, and by grid output you mean the system is selling to the grid, right? If this were the case, then when power is lost, selling to the grid would stop and AC out to grid would be 0V. The inverter would begin to power any loads using the batteries for the duration of the outage. Both the battery voltage and current would spike when the "load" of the power being sold to the grid was dropped.
Just my guess.
Rick
4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
The grid must be "good" as seen by the GT/Hybrid AC inverter... The voltage must be between ~210 and 265 VAC and 60 Hz +/- 1.0 Hz (if US/North America).
If the utility had issues, or (possibly more likely), you are at the end of a distribution circuit and perhaps you have a neighbor that is causing the grid to sag (large water pump or air compressor, etc.).
Another possible issue is a poor electrical connection between the line transformer and your main panel. I had been noticing that some of my lights have been flickering a bit in the last 6-12 months, and recently getting worse (and, it turned out, that a couple of my GFI outlets had been tripping too).
Turned out that a a few ounces of rain water had dripped down from the weather head (cable went into the weather head at the wrong angle) in the last ~15 years and got on one of the meter socket wire lugs and one of the copper drop wire was corroded (and blackened from the heat of the poor electrical connection). Replaced the socket and one wire, and all was good again.
Note that in the US, GT type inverters also measure voltage between the neutral and L1/L2 (i.e., 120 VAC line to neutral). If you have a "bad neutral" to the GT inverter, that could cause similar problems too.
If the GT inverter detects "bad line voltage or frequency", the GT inverter will shutdown, wait for line to come back into spec. Then wait 5 minutes before turning back on again.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 220 Forum & Website
- 128 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 189 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 606 Discussion Forums/Café
- 300 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed