I am a little confused about your question... "Equalization" tends to be (for lead acid batteries) controlled over charging of the battery (6-24 cells for a 12 to 48 volt battery bank) so that any "under charged cell" (less than 100% state of charge) is brought to 100% by a high charging voltage (typically around 15-16 volts for a 12 volt bank and around 2.5% to 5.0% charging current) that "forces" current through the 100% full cells so that the series connected less than full cell(s) can be brought to full charge too. This can take 30 minutes a month or many hours over several days for seriously unbalanced/poorly performing (low specific gravity industrial/large deep cycle) batteries.
There are battery "equalizers" or battery/cell balancers too. Lead Acid batteries (usually flooded cell) are somewhat tolerant of "over charging" (aka equalization). Other types of batteries (AGM, GEL, various Lithium Ion) are not tolerant of "over charging" (forcing current through a 100% full cell) and can be damaged/ruined by an "equalization" charge.
Instead, what is done by many is to put a "balancing circuit" across each cell (usually done for various Li chemistries). The balancer monitors the cell voltage and when 100% SoC, the balancer "leaks current" around the full cell--which allows other cells to continue charging until they are 100% full too. There are multiple ways that balancing can be done (top balancing, bottom balancing, etc.). Each has their proponents and applications.
And for other folks, Li Ion cells do not go out of balance very fast or very often. And some folks will manual balance the cells (charge individual cells to 100% each, or place a small load across "full cells" to bring them down to the neighbor cell voltages, etc.). And manually balanced batteries can go many months or even years between re-balancing.
The reason for equalizing/balancing cells in a battery--If you have 5 cells at 100% and one cell at 80% state of charge--Then the battery is only to 80% state of "useful" charge... Most rechargable battery chemistries die if the battery is tank to 0% state of charge or the voltage is "reversed" on the terminals (the low charge cell is "reversed charged" by the other cells. It is hard to "reverse charge" a 12 volt battery with active loads as one cell goes dead, the battery voltage drops by 2 volts (say 11 volts to 9 volts) and the loads stop functioning. With 48 volt batteries, if you have on cell go "dead", that is typically 46 volts to 44 volts and the loads will keep functioning (and the weak cell/battery will be ruined).
For various Lithium Ion chemistries, they have maximum and minimum voltages that the cell must not be taken beyond, or the cell will be ruined (and in some chemistries, the cell can explode/catch fire).
For Flooded Cell Lead Acid batteries, equalization does some good (balancing cells, mixing electrolyte, shedding "dead" plate material). However, equalization is also hard on the battery too... Oxygen generated can cause positive grid/plate corrosion, gassing erodes plate material, and gassing (hydrogen+oxygen gas generation) loses water from the electrolyte plus generates heat--Hot batteries have shorter life.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
It will attempt to equalize the voltages in a series string of any batteries. On the other hand, it's unlikely that it can move enough amps to succeed during high charge/discharge rates.
I am available for custom hardware/firmware development
-
BB. said:I am a little confused about your question... "Equalization" tends to be (for lead acid batteries) controlled over charging of the battery (6-24 cells for a 12 to 48 volt battery bank) so that any "under charged cell" (less than 100% state of charge) is brought to 100% by a high charging voltage (typically around 15-16 volts for a 12 volt bank and around 2.5% to 5.0% charging current) that "forces" current through the 100% full cells so that the series connected less than full cell(s) can be brought to full charge too. This can take 30 minutes a month or many hours over several days for seriously unbalanced/poorly performing (low specific gravity industrial/large deep cycle) batteries.
There are battery "equalizers" or battery/cell balancers too. Lead Acid batteries (usually flooded cell) are somewhat tolerant of "over charging" (aka equalization). Other types of batteries (AGM, GEL, various Lithium Ion) are not tolerant of "over charging" (forcing current through a 100% full cell) and can be damaged/ruined by an "equalization" charge.
Instead, what is done by many is to put a "balancing circuit" across each cell (usually done for various Li chemistries). The balancer monitors the cell voltage and when 100% SoC, the balancer "leaks current" around the full cell--which allows other cells to continue charging until they are 100% full too. There are multiple ways that balancing can be done (top balancing, bottom balancing, etc.). Each has their proponents and applications.
And for other folks, Li Ion cells do not go out of balance very fast or very often. And some folks will manual balance the cells (charge individual cells to 100% each, or place a small load across "full cells" to bring them down to the neighbor cell voltages, etc.). And manually balanced batteries can go many months or even years between re-balancing.
The reason for equalizing/balancing cells in a battery--If you have 5 cells at 100% and one cell at 80% state of charge--Then the battery is only to 80% state of "useful" charge... Most rechargable battery chemistries die if the battery is tank to 0% state of charge or the voltage is "reversed" on the terminals (the low charge cell is "reversed charged" by the other cells. It is hard to "reverse charge" a 12 volt battery with active loads as one cell goes dead, the battery voltage drops by 2 volts (say 11 volts to 9 volts) and the loads stop functioning. With 48 volt batteries, if you have on cell go "dead", that is typically 46 volts to 44 volts and the loads will keep functioning (and the weak cell/battery will be ruined).
For various Lithium Ion chemistries, they have maximum and minimum voltages that the cell must not be taken beyond, or the cell will be ruined (and in some chemistries, the cell can explode/catch fire).
For Flooded Cell Lead Acid batteries, equalization does some good (balancing cells, mixing electrolyte, shedding "dead" plate material). However, equalization is also hard on the battery too... Oxygen generated can cause positive grid/plate corrosion, gassing erodes plate material, and gassing (hydrogen+oxygen gas generation) loses water from the electrolyte plus generates heat--Hot batteries have shorter life.
-Bill
-
solarking said:No Bill I am not talking about the equalization charge. I am talking about the device usually called as battery equalizer which equalize battery voltage in series connection. For eg.In a 48v battery bank batt1 is 13.2v, batt 2 is 13.5v, batt 3 is 13.6v and batt4 is 13.1v, battery equaizer will prevent the lower voltage battery in a battery bank from getting overcharged.
Typically, this device is used on a "per cell" basis inside Lithium Battery Packs, as part of the BMS.
Do you have a URL LINK to this Lead Acid Balancer?
It is OK, to slightly over-charge one Lead Acid Battery, to get the entire Series String to 100% SOC.
So, we do not use a Balancer Circuit with a Series Bank of Lead Acid Batteries
We do not normally mix old & new batteries.
If you have batteries of different age, then most likely they will have different voltages.
Bulk Charging can supply way more amps than the Balancer Circuit can by-pass,
so how does the Balancer prevent over-charging ???
-
As I understand it, these essentially charge each of serially connected batteries individually. That might help if entire batteries need individual charging, but they don't charge individual serially connected cells. Your 48v bank is 24 cells connected in series. The equalizer charges in groups of 6 instead of 48.
You could do the same thing by hooking up a 12v charger in turns to batteries 1 and 4. That may be easier on batteries 2 and 3 than doing a normal EQ, which as Bill points out, can be hard on batteries.
Will it work on old and new batteries mixed in a bank? I suppose, but I don't know that it will do much to prevent the new batteries from aging prematurely.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
A 12 volt balancing circuit still is balancing 6 cells in series--So, i am not sure how it is much better to have these for 24/48 volt battery banks. I have always wondered if 2 volt balancers for lead acid batteries are more trouble than they are worth (49 wires to balance 24 cells in a 48 volt battery string--And even more if you are have several parallel strings.
And thought of a bluetooth or wifi enabled battery monitor module--You clip to the smallest battery unit in your system (12/6/4/2 volt) and it watches for high/low voltage units so you can investigate/equalize the bank when needed (detect hidden failures in long series strings of batteries without having to go out with a mutimeter every week or four).
There are 12/24 volt battery balancers. These are used, for example, in a 24 volt bus that has 12 volt house loads. The balancer is an isolated DC to DC converter that (in some models) is bidirectional. It can take charging from 24 volts and supply 12 volt loads, or even take 12 volt charging and recharge the "upper" 12 volt battery bank. These are "high power" devices that can run the 12 volts directly from the "high 12 volt" battery too (basically moving power between batteries):
http://www.dan-marcrvparts.com/vo12vobaeq.html
I guess, if you are looking to mix old/new 12 volt batteries (or series pairs of 6 volt, etc.) together in the same series string, a 12 volt based balancer circuit will "make up" for the higher self discharge that is present in older batteries.
I guess you are asking about this type of unit?:
https://www.amazon.com/ZHC-Equalizer-Lead-acid-Batteris-Balancer/dp/B01JJ3UKDU
It looks to have a 5 amp rating... That should be good for upwards of a 500 AH rated battery bank (assuming 1% rate of charge transfer--should be "good enough" for batteries in good shape). Batteries that are "failing" will show upwards (and over) 2% rate of self discharge (and can run hot/fail).
I do worry about added complexity / points of failure--The more wiring and circuits added, the more chances something will go wrong.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
A balancer is statistically advantageous, even if you only have one connected every 6 cells. And cells within the the same package/battery are more likely to be balanced anyway.
A 5A balancer operating during a 30A charge will certainly help, but imagine the case where one 12V battery is fully charged and the other (in series) isn't. The former will have to boil away ~360W of excess energy being applied (not good for the battery). Should help to put the temperature sensor on the weakest battery.I am available for custom hardware/firmware development
-
Or is this the type of equalizer the op is referring to. This is for tapping 12 volts from a 24 volt battery. It monitors usage and switches from one side to another as power is drawn.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
I was referring to sukam 48v battery equalizer
-
jonr said:A balancer is statistically advantageous, even if you only have one connected every 6 cells. And cells within the the same package/battery are more likely to be balanced anyway.
A 5A balancer operating during a 30A charge will certainly help, but imagine the case where one 12V battery is fully charged and the other (in series) isn't. The former will have to boil away ~360W of excess energy being applied (not good for the battery). Should help to put the temperature sensor on the weakest battery.
Will a battery eventually overcharge if left at its absorb voltage long enough? Yes, of course! With fairly healthy batteries, they tend to balance out when given adequate time to charge. This is always the danger with PV systems with a weak ratio of PV to battery bank size. With Concorde and Fullriver AGM's, adequate time at Float voltage on a regular basis will keep them close.
In my experience, you will see a voltage rise across the batteries that are full, while the other(s) catch up.
Again, in my experience, the batteries that "charge" first are done accepting current because they won't accept as much capacity as the others. If this is due to sufation, the voltage rise will perform a mini-equalization bringing that battery more in line with the others.
Watching individual batteries can tell you a lot.
Marc
I always have more questions than answers. That's the nature of life. -
Marc Kurth said:jonr said:A balancer is statistically advantageous, even if you only have one connected every 6 cells. And cells within the the same package/battery are more likely to be balanced anyway.
A 5A balancer operating during a 30A charge will certainly help, but imagine the case where one 12V battery is fully charged and the other (in series) isn't. The former will have to boil away ~360W of excess energy being applied (not good for the battery). Should help to put the temperature sensor on the weakest battery.
Will a battery eventually overcharge if left at its absorb voltage long enough? Yes, of course! With fairly healthy batteries, they tend to balance out when given adequate time to charge. This is always the danger with PV systems with a weak ratio of PV to battery bank size. With Concorde and Fullriver AGM's, adequate time at Float voltage on a regular basis will keep them close.
In my experience, you will see a voltage rise across the batteries that are full, while the other(s) catch up.
Again, in my experience, the batteries that "charge" first are done accepting current because they won't accept as much capacity as the others. If this is due to sufation, the voltage rise will perform a mini-equalization bringing that battery more in line with the others.
Watching individual batteries can tell you a lot.
Marc
The OP's example was ... four (4) batteries in series, with a mix of old and new.
When the Charger is in Bulk Mode, all four (4) batteries must have 30 amps flowing them.
If there is a significant mismatch between batteries, then one battery can get to 100% SOC and start gassing way too soon.
This battery will lose more water through electrolysis.
The other batteries can never "catch-up" with normal charging.
Bulk Mode should get all four (4) batteries to an equal ( +/- 85% SOC ) but it cannot.
Extreme Example
==============
Bulk Mode = 30 amps until 59.2 Volts = 14.8 Volts per battery x 4 batteries
Old Battery #1 = 16.0 Volts <<< This battery is already 100% SOC in Bulk Mode and is already creating excessive gas
New Battery #2 = 14.4 Volts <<< This battery never reaches 14.8 Volts in Bulk Mode, only +/- 75% SOC
New Battery #3 = 14.4 Volts <<< This battery never reaches 14.8 Volts in Bulk Mode, only +/- 75% SOC
New Battery #4 = 14.4 Volts <<< This battery never reaches 14.8 Volts in Bulk Mode, only +/- 75% SOC
======================
Total = 59.2 Volts
Battery #1 is fully charged but still has 30 amps flowing through it.
When the "Smart" Charger hits 59.2 Volts, it assumes all 4 Batteries are at 14.8 Volts - which is wrong.
And now the "Smart" Charger will switch to Absorb mode, which is way too early for Batteries #2, #3 & #4.
In Absorb Mode ...
a) Battery #1, which is already at 100% SOC, will continue to generate excessive gas.
b) The amps will drop below 3% way before Batteries #2, #3 & #4 can ever get to 100% SOC.
In this scenario ...
Battery #1 is habitually over-charged.
Batteries #2, #3 & #4 are continuously in a "Partial State of Charge" - PSOC is a very bad idea for Lead Acid batteries.
This is why we do not mix old batteries with new batteries.
I do believe that a Voltage Equalizer can help with a mix of old new and new batteries
What if, during Bulk Mode the Voltage Equalizer was able to get all four batteries to 14.8 Volts, at the same?
The $64,000 question is ... Does "Equal Voltage" mean "Equal SOC" for both old and new batteries?
Maybe not "equal SOC" but good enough SOC?
Battery Equalizer
=============
Bulk Mode = 30 amps until 59.2 Volts = 14.8 Volts per battery x 4 batteries
Old Battery #1 = 14.8 Volts = 85% SOC
New Battery #2 = 14.8 Volts = 85% SOC
New Battery #3 = 14.8 Volts = 85% SOC
New Battery #4 = 14.8 Volts = 85% SOC
======================
Total = 59.2 Volts
With mixed age batteries ...
a) The Voltage Equalizer appears to prevent over-charging of the old batteries
b) The Voltage Equalizer appears to prevent under-charging of the new batteries
A Voltage Equalizer that can transfer the charge from the higher voltage battery to the lower voltage battery is more efficient.
A Voltage Equalizer that just puts a load / resistor across the higher voltage battery just wastes the power!
Some other questions ...
1) How do you determine the correct size ( amps ) of the Voltage Equalizer, for your Battery Bank
2) Is the price of the Voltage Equalizer worth the cost vs buying all new batteries?
3) Does the Battery Equalizer consume a significant number of watts?
-
solarking said:I was referring to sukam 48v battery equalizer
-
Note that there is a big difference between "what is the SOC" and "are the SOCs equal". The latter is much less error prone and voltage might be the best available way to measure it (I haven't seen data either way).
Some people use SG, but:"The specific gravity of fully charged deep-cycle batteries of the same model can range from 1.270 to 1.305. ... Inaccuracies in SG readings can also occur if the battery has stratified..."
http://batteryuniversity.com/learn/article/how_to_measure_state_of_charge
My question:
With matched batteries, does battery voltage balancing increase life (less under/over charging) enough to pay for the cost and complexity (a few extra wires). My guess is it's important with AGM and nice to have with flooded.
I am available for custom hardware/firmware development
-
littleharbor2 said:Or is this the type of equalizer the op is referring to. This is for tapping 12 volts from a 24 volt battery. It monitors usage and switches from one side to another as power is drawn.
Which is an interesting subject, but it is not really the subject of this thread.
This device is missing 1/2 the functionality of the Sukam 48v Battery Equalizer.
This device will only make sure the voltage of "lower battery" is never below the voltage of the "upper battery".
This device will do nothing, if the voltage of the "upper battery" is below the voltage of the "lower battery".
"lower battery" and "upper battery" per the schematic diagram.
This is the proper device when you need to support 12V Loads & 24V Loads simultaneously.
-
Many of us in South Africa have had great success with Chinese made HA01 and HA02 battery balancers (discussed here).
Mid points are measured using a Victron BMV 702 and even people with huge battery banks have had success bringing banks into better balance (eg. here).
Regards
Mark- Main: Infinisolar 3+ (3kv) 48V Grid-Tied PV=3410w NE facing (8x 330W JASolar, 3x 310W Yingli), + Victron MPPT 150/60 @1240w SW facing (2x 310W Renesola, 2x 330W JASolar), Pylontech US3000, Victron BMV 700, 6 string combiner box with PV isolator switch, subDB for inverter supplied power.
- Draadkar: Axpert 800w, 24V, 8x 12V - 105ah Leisure Batteries 400ah, PV=480 (2x 240W ElChepo), Victron BMV 702 for laptop, relays backup.
- ICC for management, automated switch over and monitoring, pushing data to EmonCMS and PVOutput.org (Aloe Ridge Farm).
- Weather from personal weather station using Weather Display.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed