Bulk Charge Current / Battery Rule of Thumb
Razed11
Registered Users Posts: 14 ✭✭
I have read somewhere that the bulk charge current should be about 10 % of the capacity of the battery. Is this simply to keep the charge time reasonable? I'm asking because at the moment I have a 100 W panel with a short circuit current of 5.8 A, a 90 Ah battery, and a charge controller that supports up to 6 A but I'm exploring a 50 W panel by the same vendor (Renogy) that has a short-circuit current of just under 3 A.
Thanks.
Thanks.
Tagged:
Comments
-
My rough rule of thumb:
- 5% minimum rate of charge for Lead Acid battery--Weekend/seasonal power usage
- 10% rate of charge for Lead Acid Battery--Full time off grid (9+ months a year, some daytime loads)
- 13% rate of charge for Lead Acid Battery--Typically about the "cost effective" maximum charging current, plus roughly the maximum amount of current into a flooded cell lead acid battery without a Remote Battery Temperature Sensor to reduce the chances of thermal run-a-way during charging.
There are folks that will run 20-25% rate of charge--Typically with an AC Battery Charger (mains or genset powered).
Note that while a Lead Acid battery only needs around 2.5% to 5% rate of charge for "equalization" charging--If you "force" even 2.5% rate of charge into a 100% full battery, it can overheat and fail (or even catch more).
There is a lot more behind the rules of thumbs--But this is our "go to" numbers for a typical off grid solar power system. If you have "non-typical" power needs, we can discuss the details.
But, you are correct, one of the reasons that 10% rate of charge is "better" than 5% rate of charge... It is to "fast charge" the battery (you have several days of cloudy weather, the next day you have full sun and need to get all of the energy you can harvest. Discharge a battery to 50% state of charge, it will take around 12-14 hours of "sun" (about two long summer days) to get back to 100% state of charge. A 10% rate of charge can get you backup in (roughly) 7-8 hours (a bit more than 1 day of full sun).
Also, if you have loads during the day (household appliances, computers, TV, water pump, etc.), that uses energy from the solar panel to run those loads, and slows down the recharging of the battery bank. Having a larger array usually means less day to day energy management decisions (what loads I can turn on today with a bit of overcast).
Also, for larger deep cycle (tall case) and industrial flooded cell lead acid batteries--Some vendors recommend 10% minimum rate of charge.
Now, if you want to talk about AGM, LiFeO4, or other type batteries--These rules can be adjusted some.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
IMO, the optimal % for a typical use has been increasing as solar panels drop in price and LA batteries stay about the same.
If de-stratification isn't an issue, then one can trickle charge at very low rates.
I am available for custom hardware/firmware development
-
To add a bit to Bill's comment, it's also worth noting that the panel is rated under specific test conditions. If you are up a high mountain with clear cold air, and proper tilt, you might get a bit better. In most cases though, you will get less, so you need more panel to offset.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
The amps for the Bulk Charge should be the value specified by the Battery Manufacturer.
That way you transition from Bulk Charge Mode to Absorb Mode at the correct % SOC.
There can be three "Set Points" ...
1) Specific "Volts & Amps" combination to signal when to transfer from Bulk Mode to Absorb Mode
2) Specific "Volts & Amps" combination to signal when to transfer from Absorb Mode to Finish Mode
3) Specific "Volts & Amps" combination to signal when to transfer from Finish Mode to Float Mode
Changing the volts and/or amps of any "Set Point" changes when your battery gets to 100% SOC, or not.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 190 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed