Hi People,
I'm about to connect just half of my offgrid future 10 panel system. So I have 5 100 watt 12 volt panels going into a combiner, just using one of my two breakers. From there onto the Flexmax 80 and then to the 4 Costco 6 volt batteries.
The panels are going to be in series...total voltage of approximately 90 here in the summer.
My questions....
The panels have 12 gauge mulitstrand wiring...no fuses inline....what wiring should I use to the combiner? (i need an extension) And does wiring for AC differ from DC wiring? Should i insert one fuse per panel line or?
What gauge wiring from the single breaker to the Flexmax? And size from Flexmax to the batteries, allowing for the future expansion to 10 panels. The distance is less than a foot or so from each component.
Thanks so much for your help.
Chris
I'm about to connect just half of my offgrid future 10 panel system. So I have 5 100 watt 12 volt panels going into a combiner, just using one of my two breakers. From there onto the Flexmax 80 and then to the 4 Costco 6 volt batteries.
The panels are going to be in series...total voltage of approximately 90 here in the summer.
My questions....
The panels have 12 gauge mulitstrand wiring...no fuses inline....what wiring should I use to the combiner? (i need an extension) And does wiring for AC differ from DC wiring? Should i insert one fuse per panel line or?
What gauge wiring from the single breaker to the Flexmax? And size from Flexmax to the batteries, allowing for the future expansion to 10 panels. The distance is less than a foot or so from each component.
Thanks so much for your help.
Chris
Comments
-
Chris you won't need a breaker or fuse for 1 or 2 strings of panels. In fact you could/should just use a "Branch connector" unless you intend to add more than 2 strings.
The panels will have a fuse rating on the back (generally). For strings of 100 watt panels you will usually find it's a 15 amp fuse or breaker for each string.
Once combined the amperage doubles, but with 2 strings of 100 watt panels putting out about 90 volts (18 volt panels, summer voltage will actually be lower than fall and winter, colder panels =higher voltage) you could use a 25-30 amp fuse or breaker going into the charge controller, this would be handy for shutting down if needed.
From the Charge controller to the battery bank will depend on system voltage, if it's 12 volts you will have a potential of 1000 watts at 12 volts or @83 amps. For a wire gauge to handle 83 amps (it will rarely if ever be this high) 6 gauge should be fine and likely even 8. For 24 volt battery bank 8 or 10 gauge.
Outback has a string sizing tool, you can plug in numbers and I think it will give gauges and fuses.
http://www.outbackpower.com/outback-support/string-sizing-tool
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Thanks Photowhit. I just went and bought some 8 gauge stranded. Now to install that and the bats. If you don't hear back from me send flowers to my widow.
Chris -
I forgot to mention, be sure to get DC rated fuses and breakers! And check that they are designed for enough voltage!
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Yep, gottem already. Thanks again.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed