max charging rate fo battery
jtdiesel65
Solar Expert Posts: 242 ✭✭✭
Hi,
So I searched for this, but didn't get any specific results. Posts hinted at 10%. IIRC it's 10-15%.
I have a forklift battery 1576 AH @20 and currently max charge at 180a via generator and 175a via panels. So that is around 11.1 %. I recently got a new 12KW generator replacing an old 8.5KW unit and am wondering if I can bump up the charge level. I have two XW4024 each with 150A limit. 15% would put it at 236a or 118a per unit. If I did the math right, the new generator should be able to handle this amount.
Anybody know what the rule of thumb on the max rate is?
thx
So I searched for this, but didn't get any specific results. Posts hinted at 10%. IIRC it's 10-15%.
I have a forklift battery 1576 AH @20 and currently max charge at 180a via generator and 175a via panels. So that is around 11.1 %. I recently got a new 12KW generator replacing an old 8.5KW unit and am wondering if I can bump up the charge level. I have two XW4024 each with 150A limit. 15% would put it at 236a or 118a per unit. If I did the math right, the new generator should be able to handle this amount.
Anybody know what the rule of thumb on the max rate is?
thx
Comments
-
I went looking for GB information on charge rates for forklift batteries, where I had read 15%. I couldn't find the infor but here is an Exide Charger infor showing on page 63 a charge rate of 16%, I could presume that is based on a 6 hour rate so that would be around a 20% charge rate based on a 20 hour configuration. PLEASE LOOK FOR MORE INFO! I had fixed in m mind 15% charge rate was standard for forklift batteries based on a 20 hour rate!
http://www.gbcharger.com/Enersys_SCR_Charger_Manual.pdfHome system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Roughly 13% or C/8 rate of charge based on 20 hour capacity is common recommendation for flooded cell lead acid batteries. You can go higher--Utility (AC line powered) chargers are sized to 20% to 25% rate of charge. However, when you go above ~13% rate of charge, you need to monitor the temperature of the battery bank--It is possible to overheat the battery bank with higher rates of charge (and 13% rate of charge is usually the "maximum cost effective rate of charge" for solar systems--Larger systems will work, but system will sit at "float voltage" for much of that second 1/2 of the day).
Many fork lift batteries may be sized to 6-8 Hour discharge rate (a fixed current that takes a battery from 100% to 0% state of charge over 6/8 hours)--And a few of the manufacturers seem to have difficulties properly mapping into the 20 Hour capacity specification.
A 210 AH @ 20 hour capacity battery may have 175 AH @ 5 hour rate:
https://www.solar-electric.com/lib/wind-sun/T605_TrojanRE_Data_Sheets.pdf
So using the proper rate of charge against the correct capacity rule of thumb is important:- 0.13 * 210 AH = 27.3 Amps charging
- 0.15 * 175 AH = 26.25 Amps charging
Our rules of thumbs are short cuts to get to roughly correct designs that will work for most everyone. And the rules are not "exact"--Usually anything within 10% (watts, amps, etc.) is close enough for solar work.
Note that it is possible to overheat a battery bank with 2.5% to 5% rate of charge too--When the battery bank is full and you are pumping charge current into the battery bank for "equalization charging". During equalization, most of the energy goes into making hydrogen and oxygen gasses, and heating the battery bank.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset - 0.13 * 210 AH = 27.3 Amps charging
-
Depending on charge voltage setting and battery temp comp, at 236adc you may be setting max current a bit higher than 12kw. Also, I would be reluctant to run a generator at 100% load for extended periods as the alternator will run pretty hot etc.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 189 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed