Wire Sizing for added generator to Battery backup Gridtied system?

Is there a calculator that can help me size the wire needed from the generator to the manual transfer switch?
I have a battery backup grid tied system and want to add a generator for a secondary backup to the PV panels, especially if they can't charge the batteries using the panels.
The generator I have is a Ryobi 6,500-watt. I figure I can add a manual transfer switch between the generator and SMA Sunny Island and manually switch on the generator when needed if the grid goes down. The wire run will be approximately 35 feet from the generator to the transfer switch. I'm thinking of placing the transfer switch next to the Sunny Island.
I have a battery backup grid tied system and want to add a generator for a secondary backup to the PV panels, especially if they can't charge the batteries using the panels.
The generator I have is a Ryobi 6,500-watt. I figure I can add a manual transfer switch between the generator and SMA Sunny Island and manually switch on the generator when needed if the grid goes down. The wire run will be approximately 35 feet from the generator to the transfer switch. I'm thinking of placing the transfer switch next to the Sunny Island.
Comments
This is a full blown NEC based calculator:
http://wiresizecalculator.net/
You probably need the NEC code book to run it well... There are lots of variables.
The basics... What is the maximum current you want to run from the genset... Say:
- 6,500 Watts / 240 VAC = 27 amps max continuous
The conservative number would be to multiply the 27 amps * 1.25 NEC "continuous current" derating = 34 amps (round up to 40 amp standard breaker+wiring).A non-commercial genset will probably not be able to maintain 27 amp output without eventually overheating its wiring/alternator (running hours at 27 amps). Running 1.25x rated wiring is probably "overkill" (you need to decide what your loads will be--If much less than 27 amps, or close too it--especially if you add a larger genset later). Note that most loads are not very large or short term high current (starting well pumps, refrigerators, etc.). However, AC Battery charging can go many hours at maximum rated AC input current (and DC output current) for the AC to DC battery charger... So, for those circuits, you really do want the 1.25x NEC wiring+breaker derating. Otherwise you can get false trips (breakers) or overheated wiring connections (breaker connections, wire nuts, etc.).
Then you need to figure out what insulation/conduit fill/temperature of wiring you want to use (can get from your local supplier for a reasonable price). Roughly, 40 amps would look like:
https://lugsdirect.com/WireCurrentAmpacitiesNEC-Table-301-16.htm
(140° F)
(167° F)
(194° F)
Kcmil
Or somewhere around 10-8 AWG (ignoring other NEC factors).
You can verify the voltage drop using a simple calculator like this (27 amps, 35 feet, 240 VAC, 3% to 1% voltage drop):
http://www.calculator.net/voltage-drop-calculator.html?material=copper&wiresize=5.211&voltage=240&phase=ac&noofconductor=1&distance=35&distanceunit=feet&eres=27&x=62&y=7
12 AWG:
Voltage drop: 3.00
Voltage drop percentage: 1.25%
Voltage at the end: 237
http://www.calculator.net/voltage-drop-calculator.html?material=copper&wiresize=8.286&voltage=240&phase=ac&noofconductor=1&distance=35&distanceunit=feet&eres=27&x=56&y=6
14 AWG:
Voltage drop: 4.77
Voltage drop percentage: 1.99%
Voltage at the end: 235.23
So, the above 10-8 AWG able (required by code to carry current) is more than heavy enough to carry the current with "acceptable" voltage drop.
-Bill
Thanks for the detailed info. I really appreciate you taking the time to help me. I'll go with the 8 AWG, just incase I upgrade the generator at a future time.
Do you have a recommendation for a manual transfer switch. Looking at the wiring I have now, I'll need to bring the AC line from the main panel (where the meter is located) and tie it into the transfer swith with the generator, then take the ouput to the SMA Sunny Island AC2. I should be able to flip the transfer switch when the grid goes down to charge the batteries when the PV panels are lacking because of weather, etc.... ..
The "simple" AC relay (you power up genset, relay turns on in 6 seconds (or whatever it is)), then you have AC power from genset.
Wire the AC battery charger on the "up stream side" of your AC transfer switch (you don't want your AC battery charger pulling power from your off grid AC inverter--that is a bit of waste of energy battery bank using AC battery charger to charge itself).
https://www.solar-electric.com/pmts-50.html (relay)
https://www.solar-electric.com/midnite-solar-60-amp-240-volt-dual-ac-manual-transfer-switch.html (manual)
There are also "per circuit" manual AC transfer switches:
https://www.amazon.com/Reliance-Controls-Corporation-31406CRK-Generators/dp/B000BQN4T2
Nice if you have a mix of circuits that you may or may not want to run on genset.
Lots of choices out there--In the end, I suggest doing a couple of paper designs and figure out the cost/benefits between the different options.
I suggest staying away from "auto start" generator controllers unless you really need that--The more complexity, the more wild and wonderful ways things can fail.
-Bill
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
If I get the https://www.solar-electric.com/pmts-50.html (relay) as Bill has suggested, What other components do I need to purchase besides a 50 Amp Power inlet Box and wiring?
The SMA Sunny Island has a Digi In, which needs to be wired to a relay (PowerMax PMTS-50 Automatic AC Transfer Switch 50 Amp --I assume this will function with the Sunny Island). Once the Grid goes down the relay needs to act as a switch either removing or applying the battery voltage. You can see a short video here:
Will the PMTS-50 function with the Sunny Island's Digi In?
The relay I pointed to is powered by the AC line voltage. It sounds like the SMA S. Island has a (12 VDC?) output to control external relay(s)?
When you start building bigger systems like--The complexity can be an issue. Make sure you have drawings (yours or from the vendor/installer) that show how everything will be connected and what parts you will need.
This requires a fair amount of pre-planning to "get right" the first time.
-Bill
I have purchased these components: