Morningstar PWM to Schneider MPPT conversion
mcgivor
Solar Expert Posts: 3,854 ✭✭✭✭✭✭
So to begin with I made a fundemental mistake in choosing panels with my initial installation with PWM, chose the cheaper 60 cell panels, only to discover the error of my ways, later on. What the system consisted of was a Morningstar TS 60 PWM with 6 of the following panels in parallel:
Schutten 250W
VOC 37.75V
ISC 8.98A
VMP 30.2V
IMP 8.3A
Batteries are Yuassa EB 12V 130 Ah, 2 strings of 2 for 260Ah / 24V nominal. Attached pdf for specs.
The system appeared to work fine, but there may have been a period of extreme hot weather when demand was high and I was absent, my suspension family members ran fans all night for several weeks , evident from logged data, but long story short the battery was heavily discharged for some time but not destroyed.
Conversion to MPPT, wanted to stay with Morningstar but the local vendor, in Thailand, said there was a minimum order of 2 units, so I looked for an alternative, ending up with Schneider Conext 60 -150 MPPT, for $ 450 shipping included, $200 cheaper if the meter is included (Morningstar) and to be honest it seems a better CC, based on features and overall construction.
The array was rewired 2 panels series, 3 parallel, used Morningstar string calculator as I can't access Schneider's with an Android tablet, but believe it to be accurate since both are fundementaly the same, so after 3 days here are the findings.
The Schneider is set up using the default setting for flooded batteries, 28.8V bulk and absorbtion and float 27V, exactly the same as the Morningstar. Here is where things are interesting, bulk charging amperage is the same around 25A, the time to reach absorption is about the same, the Schneider however goes into float and reduces the voltage to 27V, temperature compensated, at about the same time as the Morningstar would be at 35% PWM. The Morningstar would hold the voltage at 28.8v until the array could no longer exceed the battery voltage. In fact the only time I ever saw it in float was the first time it was hooked up and performing a commissioning charge.
Resulting differences, there is a lot less gassing of the batteries at 27V float, my loads never pull it out of float, float is a stranger to me, everything else seems to be the same, including morning battery voltage at 24.4V, not rested inverter connected, daily Ah identical, it seems there is no advantage except perhaps when it gets to above 45°C ambient, but that will be in a month or two. Never needed a generator as even with the PWM setup it could fully charge on an overcast day, but my suspension it will be better with MPPT due to the higher array voltage.
Any ideas, thoughts or suggestions are most welcome, this is a new language so to speak and the learning curve, although not too steep, is a learning curve none the less.
Schutten 250W
VOC 37.75V
ISC 8.98A
VMP 30.2V
IMP 8.3A
Batteries are Yuassa EB 12V 130 Ah, 2 strings of 2 for 260Ah / 24V nominal. Attached pdf for specs.
The system appeared to work fine, but there may have been a period of extreme hot weather when demand was high and I was absent, my suspension family members ran fans all night for several weeks , evident from logged data, but long story short the battery was heavily discharged for some time but not destroyed.
Conversion to MPPT, wanted to stay with Morningstar but the local vendor, in Thailand, said there was a minimum order of 2 units, so I looked for an alternative, ending up with Schneider Conext 60 -150 MPPT, for $ 450 shipping included, $200 cheaper if the meter is included (Morningstar) and to be honest it seems a better CC, based on features and overall construction.
The array was rewired 2 panels series, 3 parallel, used Morningstar string calculator as I can't access Schneider's with an Android tablet, but believe it to be accurate since both are fundementaly the same, so after 3 days here are the findings.
The Schneider is set up using the default setting for flooded batteries, 28.8V bulk and absorbtion and float 27V, exactly the same as the Morningstar. Here is where things are interesting, bulk charging amperage is the same around 25A, the time to reach absorption is about the same, the Schneider however goes into float and reduces the voltage to 27V, temperature compensated, at about the same time as the Morningstar would be at 35% PWM. The Morningstar would hold the voltage at 28.8v until the array could no longer exceed the battery voltage. In fact the only time I ever saw it in float was the first time it was hooked up and performing a commissioning charge.
Resulting differences, there is a lot less gassing of the batteries at 27V float, my loads never pull it out of float, float is a stranger to me, everything else seems to be the same, including morning battery voltage at 24.4V, not rested inverter connected, daily Ah identical, it seems there is no advantage except perhaps when it gets to above 45°C ambient, but that will be in a month or two. Never needed a generator as even with the PWM setup it could fully charge on an overcast day, but my suspension it will be better with MPPT due to the higher array voltage.
Any ideas, thoughts or suggestions are most welcome, this is a new language so to speak and the learning curve, although not too steep, is a learning curve none the less.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Comments
-
"The time to reach absorb is about the same".
How is this determined with the new controller? Are there settings for absorb time and/or end amps on the controller? If so, what are they? I'm wondering if they may be set to some really conservative default setting resulting in a premature shift to float.
Have you checked SG since the deep discharge incident?Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
"The time to reach absorb is about the same".
How is this determined with the new controller? Are there settings for absorb time and/or end amps on the controller? If so, what are they? I'm wondering if they may be set to some really conservative default setting resulting in a premature shift to float.
Have you checked SG since the deep discharge incident?
Absorption is set for 3 hours, default or can be adjusted between 1 and 8 hours.
The SG after the deep discharge recovered with the exception of one cell, which has since been recovered by using a water treatment technique. The SG is checked on a weekly basis and water added if below maximum level, all are right on the money, albeit the new CC has only been in service now for 4 days.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
2% sounds good. You're checking SG regularly so if the new controller needs needs tweaking you'll know. Floating should be easier on the bank than holding at higher voltage as long as it gets proper absorb.
With loads the same and battery charging fine why would production be much different? You can't produce more than you use (off grid). If you're getting a long time in float, maybe consider some sort of opportunity load?Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed