Victron Bluesolar and Equalisation
bigbrovar
Registered Users Posts: 32 ✭✭
Hi guys. I changed my charge controller from the chinese epsolar to victron energy bluesolar mppt charge controller 150/45
So far so good, been impressed by the controller especially the tracking speed in cloudy weather. However today is the first time the controller will be performing equalization of my batteries (220ah @ 24v, FLA with tubular plate) with my old controller (and inline with all documentation I read about equalization) equalization process takes minimum of 2 hours.. infact the user can set the number of hours the cc can perform equalization of the batteries but the default is 2 hours.
With victron blue solar, it is impossible to set equalisation time, you can only set the equalisation voltage. Here is the part of the bluesolar manual that talks about equalisation.
So far so good, been impressed by the controller especially the tracking speed in cloudy weather. However today is the first time the controller will be performing equalization of my batteries (220ah @ 24v, FLA with tubular plate) with my old controller (and inline with all documentation I read about equalization) equalization process takes minimum of 2 hours.. infact the user can set the number of hours the cc can perform equalization of the batteries but the default is 2 hours.
With victron blue solar, it is impossible to set equalisation time, you can only set the equalisation voltage. Here is the part of the bluesolar manual that talks about equalisation.
Automatic equalization
Automatic equalization is default set to ‘OFF’. By using the
configuration tool mpptprefs this setting can be configured with a
number between 1 (every day) and 250 (once every 250 days).
When automatic equalization is active, the absorption charge
will be followed by a voltage limited constant current period (see
table in section 3.5). The current is limited to 8% of the bulk
current for all VRLA (Gel or AGM) batteries and some flooded
batteries, and to 25% of the bulk current for all tubular plate
batteries and the user defined battery type. The bulk current is
the rated charger current unless a lower maximum current
setting has been chosen.
In case of all VRLA batteries and some flooded batteries
(algorithm number 0, 1, 2 or 3) automatic equalization ends
when the voltage limit maxV has been reached, or after
t = (absorption time)/8, whichever comes first.
For all tubular plate batteries and the user defined battery type
automatic equalization ends after t = (absorption time)/2.
When automatic equalisation is not completely finished within
one day, it will not resume the next day, the next equalisation
session will take place as determined by the day interval.
My controller is set to algorithm number 2 which is the default. My question is, is 30 min of equalization enough? My battery are rarely discharged below 65% SOC in fact my average day to day cycle is at 70-85% SOC. My fear is just that the victron cc would leave my battery under equalized because most of what I read says equalization charge should be held for 2 hours to be effective.
My controller is set to algorithm number 2 which is the default. My question is, is 30 min of equalization enough? My battery are rarely discharged below 65% SOC in fact my average day to day cycle is at 70-85% SOC. My fear is just that the victron cc would leave my battery under equalized because most of what I read says equalization charge should be held for 2 hours to be effective.
Comments
-
Took SG readings with my hydrometer some minutes after the above stated equalization attached is the SG level I got from my hydrometer for pretty much all the battery cells.
-
Took SG readings with my hydrometer some minutes after the above stated equalisation attached is the SG level I got from my hydrometer for pretty much all the battery cells.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
-
below is my charge cycle data for the last 30 days.. pulled from the controller history logs
-
Manufacturers recommendations aside, that appears to be good, what temperature were the batteries when you took the readings? Who is the manufacturer of the battery?1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
extended logs showing max battery voltage, Time spent in bulk, Absorption and float (all in minutes)
-
mcgivor said:Manufacturers recommendations aside, that appears to be good, what temperature were the batteries when you took the readings? Who is the manufacturer of the battery?
-
It sounds like the default setting #2 may be for a VRLA battery of some type, with a 4hr timed absorb cycle.
The battery page doesn't appear to have some specs needed. It would help if you could find out from the manufacturer:
- recommended absorb voltage range
- recommended equalize voltage range
- recommended specific gravity at full charge.
Setting the controller to the tubular plate type profile looks like it would extend the EQ time to 2hrs, but it would be a good idea to check the above recommended values vs the profile values. With warm batteries and no remote temp sensor there is a risk of using too high voltage.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed