More Batteries
abdulnaeem74
Registered Users Posts: 5 ✭✭
Nice place to learn for beginner for solar system setup
i have this system
4 mono panels 150 watt (2 in series for 24v system)
2 batteries 80Ah each
24v inverter/ups
30A PWM cm3024z solar charge controller china made
my questions are
a. can i install 4 batteries (100 Ah) for this system and with same charge controller
b. can add 2 more panels (150 watt) with same charge controller
i have this system
4 mono panels 150 watt (2 in series for 24v system)
2 batteries 80Ah each
24v inverter/ups
30A PWM cm3024z solar charge controller china made
my questions are
a. can i install 4 batteries (100 Ah) for this system and with same charge controller
b. can add 2 more panels (150 watt) with same charge controller
Comments
-
Welcome to the forum
Without details such as location, loads, depth-of-discharge, are you off grid, and if so how many days of autonomy are required etcetera and not calculating in losses, a basic answer would be:
a. 200Ah/24V battery may be a little too large for the maximum array you could safely use, 600W/24V
b.You could use 2 more panels with the 30A controller to a maximum of 600W/24V
This is a simple answer, provide all details listed and include panel specifications to get a more detailed calculation/estimate.
There are options such as adding a second charge controller in parallel with 2×450 W arrays to increase capacity but best to start with basics.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Thanks for Prompt reply!
i live in Lahore Pakistan (ASIA),
in summer Sun shine almost 10 hours and temp almost 30-42 degree Celsius
in winter sun shine 5-7 hours and temp 10- 20 degree Celsius
this is my panel specs 4 no. 150W mono-crystalline
VOC 21.5
Isc 9.83A
Vmp 18.5V
Imp 8.75A
i want my system to be off grid
my load is 300 W per hour,
therefore i want to have 4 batteries of 100Ah 24v system
will it be ok with 30A PWM CC china made
and
can i add 2 more 150watt mono panels with same 30A PWM CC in future or have to replace Charge controller with 40A
-
abdulnaeem74 said:Thanks for Prompt reply!
i live in Lahore Pakistan (ASIA),
in summer Sun shine almost 10 hours and temp almost 30-42 degree Celsius
in winter sun shine 5-7 hours and temp 10- 20 degree Celsius
this is my panel specs 4 no. 150W mono-crystalline
VOC 21.5
Isc 9.83A
Vmp 18.5V
Imp 8.75A
i want my system to be off grid
my load is 300 W per hour,
therefore i want to have 4 batteries of 100Ah 24v system
will it be ok with 30A PWM CC china made
and
can i add 2 more 150watt mono panels with same 30A PWM CC in future or have to replace Charge controller with 40A1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
6 hours specially in night
-
Sorry one more thing, are you using an inverter or are your loads DC, if you have an inverter what is it?1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
i am using APC UPS 1000va (24v)
-
Long answer short, adding 2 more panels will exceed the rating for your 30A controller, so yes a larger one would be required, 40A or more would be needed. The APC UPS is not an inverter per say, but I think I understand what you are doing, using a salvaged UPS used as an inverter, on a budget, correct? As far as the hours of sunlight are concerned you have to base it on the lowest figures for the year for an accurate estimate, and this depends on direction and angle, see link
As I'm not as well versed in estimating, as others such as @BB I won't venture into that, hopefully the gracious Bill can assist, he is such a wizard at those calculations.
http://solarelectricityhandbook.com/solar-irradiance.html
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
In general, I do not recommend UPS systems for use as off grid inverters... Many are MSW (modified square/sine wave) which can be hard on motors/electronic power supplies (something like 80% of loads may work fine, 10% may fail in hours/days/weeks, and another 10%--Who knows). And they are usually designed for 30 minutes of use or so (just long enough to ride through a short power outage and/or shutdown a computer system).
A small inverter (only available in 12 volts) that could work well for your needs (plus has remote on/off and a "sleep mode") is the MorningStar 300 watt 12 volt (120 VAC 60 Hz and 230 VAC 50 Hz models available) PSW (pure sine wave). If you can find something similar locally (this inverter may be hard/expensive for your to get)--I would suggest over a UPS.
http://www.morningstarcorp.com/products/suresine/
So--Some basic math. I will use 12 volt battery bank, but a 24 volt battery bank will give the same results (i.e., 12 volt @ 400 AH battery bank is the "same" as a 24 volt @ 200 AH battery bank--just different series/parallel connections, and/or different choice of battery voltage/capacity).
300 Watts for 12 hours with 2 days of storage (poor sun) and 50% maximum discharge seems to be a good "optimum" bank design for use with lead acid batteries. Deep cycle storage batteries should have 5% to 13% rate of charge typically. With 5% good for weekend/seasonal use. And 10%+ recommended for full time off grid use (better battery life, less day to day load management vs available sun):- 300 Watt load * 6 hours per day night usage * 1/0.85 AC inverter eff * 1/0.77 solar panel+controller deratings * 2 days storage * 1/0.50 maximum discharge * 1/12 volt battery bank = 916 AH @ 12 volt battery bank
- 916 AH * 12 volts / 24 volts = 458 AH @ 24 volt battery bank
Next need to size the solar array based on two different calculations. First is based on battery bank capacity (5% to 13% rate of charge, base on 20 Hour battery rated Amp*Hour capacity). Using the above calculation:- 916 AH * 14.5 volts charging * 1/0.77 solar panel+controller deratings * 0.05 rate of charge = 862 Watt array minimum
- 916 AH * 14.5 volts charging * 1/0.77 solar panel+controller deratings * 0.10 rate of charge = 1,724 Watt array nominal
- 916 AH * 14.5 volts charging * 1/0.77 solar panel+controller deratings * 0.13 rate of charge = 2,242 Watt array "cost effective" maximum
http://www.solarelectricityhandbook.com/solar-irradiance.htmlLahore
Measured in kWh/m2/day onto a solar panel set at a 58° angle from vertical:
Average Solar Insolation figures
(For best year-round performance)
Based on 300 Watts * 6 hours per day or 1,800 WH per day and a minimum and 4.71 hours per day (January long term 20 year average):Jan Feb Mar Apr May Jun 4.72
5.66
6.16
6.50
6.68
6.34
Jul Aug Sep Oct Nov Dec 5.52
5.46
6.00
6.43
5.73
4.91
- 1,800 Watt*Hours * 1/0.52 off grid system eff * 1/4.72 hours of sun per day (noontime equivalent full sun) = 733 Watt minimum array
If you will run more power during the day (say water pumping, laptop computer, etc.)--Then you may want to get towards 1,724 Watt array.
The above would be a "nominal" designed system with lead acid batteries for full time off grid. If the system is only used for weekends or a week or two at a time--You might be able to get away with a smaller battery bank (1/2 the AH ratings I calculated)...
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
its very nice that much you guided. i wl make it possible in next year with more PV array and batteries..
keep smiling
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed