De-ice the stock tank with 12 V heater
molniya
Registered Users Posts: 1 ✭
Folks are selling 12 volt stock tank heaters. Chopping ice for the ponies every day is getting...old.
I now have a 600W 12 volt heating element. The application charts always show the heating element wired
directly to a 12 volt battery. Only one battery, not a bank of batteries, and there are no low voltage drop out circuits
involved. The only device between the heating element and the battery is a "freeze switch", a sealed [probably bimetallic]
switch that is supposed to close and connect the heating element when the ambient temp is around 32F and open at
about 40F. If there is NO provision for a low voltage disconnect to save the battery from the anticipated 50 Amp load,
[600W / 12 Volt] how is this NOT a "battery self destruct circuit? I have built several very small scale solar powered
systems, and the battery always had a low voltage disconnect circuit [usually the charge controller].
The battery I intend to use is a marine type with a 180 min reserve rating. [25 Amp discharge at 80F]
It would appear that at best I can run the water tank heater for about an hour or so [50 A load]
and then have a depleted battery with essentially a dead short across the terminals. [the heating element].
The wiring chart that appears all over the internet for this heater seems to be dangerously over simplified.
How can this work [safely] without a disconnect circuit?
? is there some subtle bit of "water tank heating" mojo that is escaping me?
I now have a 600W 12 volt heating element. The application charts always show the heating element wired
directly to a 12 volt battery. Only one battery, not a bank of batteries, and there are no low voltage drop out circuits
involved. The only device between the heating element and the battery is a "freeze switch", a sealed [probably bimetallic]
switch that is supposed to close and connect the heating element when the ambient temp is around 32F and open at
about 40F. If there is NO provision for a low voltage disconnect to save the battery from the anticipated 50 Amp load,
[600W / 12 Volt] how is this NOT a "battery self destruct circuit? I have built several very small scale solar powered
systems, and the battery always had a low voltage disconnect circuit [usually the charge controller].
The battery I intend to use is a marine type with a 180 min reserve rating. [25 Amp discharge at 80F]
It would appear that at best I can run the water tank heater for about an hour or so [50 A load]
and then have a depleted battery with essentially a dead short across the terminals. [the heating element].
The wiring chart that appears all over the internet for this heater seems to be dangerously over simplified.
How can this work [safely] without a disconnect circuit?
? is there some subtle bit of "water tank heating" mojo that is escaping me?
Comments
-
Most 'freeze' switches I've encountered are set to 45 degrees F, not 32. Do you have product names, model numbers you can share?
I just looked at some farm forums, and it looks like they deliberately let the battery go dead, then recharge it or swap it out the next day.
You would need a fairly large solar array to heat a water trough.
How many gallons?
Camden County, NJ, USA
19 SW285 panels
SE5000 inverter
grid tied -
If my arithmetic is right, that element would raise the temp of about 30 gallons of water from 32f to 40f in one hour. Heating anything with solar electric gets expensive pretty fast, especially if batteries are involved.
If you have sun near the tank, maybe a DIY solar thermal setup with some black poly waterline and a small pump?
Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
some of the PWM charge controllers have a circuit to turn on lights and other small loads..., you could use the built in timer to turn the heater switch on, via solenoid, and off after X hours of melting based on the batteries capacity. I assume you want it there when you feed in the AM,..?
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Estragon said:If my arithmetic is right, that element would raise the temp of about 30 gallons of water from 32f to 40f in one hour.Camden County, NJ, USA
19 SW285 panels
SE5000 inverter
grid tied -
molniya,
All of your concerns are justified.
I would definitely add a Low Voltage Drop-Out device.
I would never, ever, ever, ever want the heater to discharge the battery to 0 volts = quick death.
I would not discharge more than 50% because you have a hybrid "marine" battery.
What if you used a heavy duty $20 PWM like ...
https://www.amazon.com/dp/B01HEXJUX8?psc=1
and dialed back the power, to say 10% PWM, just enough to keep the water from freezing?
I think, approx 25 watts can raise 10 Gallons of water 1° F
Insulate the water container - all sides and bottom.
If you minimize the heat lost then you will significantly reduce the load on the battery.
Maybe, now the battery could last 180 minutes / 60 min/hour / 10% = 30 hours ?
If you purchase two batteries you can swap daily.
Use bolted-on Power Pole Connectors to make swapping, less of chore.
Or skip the battery and buy a 12 V DC 50 Amp MegaWatt power supply for $110. -
My sister just uses a hatchet to chop the ice out. Easier to swing than changing a battery that froze soild
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed