programming outback inverter/charger fyir generator size

We live off grid in the UK and use an Outback fm80 charge controller to keep our 24v bank of 2v cells charged and power our cabin with an Outback gfx1424e iverter/charger. Now that it is winter we struggle to replace our power usage from the solar. We are careful with how much power we use and in previous winters have used a victron 350w sine wave inverter and really limited our usage and just managed to get through with the solar.
This winter we would like to use the charging facility on the outback gfx1424e however we are unable to replace our generator at the moment. Our current generator has been sized for our house truck so is smaller than ideal for the gfx1424e. If we purchased the mate display/control unit for the inverter would we be able to programme the iverter to charge from our generator? The user manual seems to suggest we could. The generator is a petrol inverter geny 230v 50hz 900w constant 1000w peak.
We intend on purchasing a larger 3kva generator next year but for now we need to get through this winter with what we have.
Please advise if it would be possible to set the gfx1424e to run from our 900/1000w sine wave geny with using the mate controller to programme the inverter. If so what settings would I need to set?
This winter we would like to use the charging facility on the outback gfx1424e however we are unable to replace our generator at the moment. Our current generator has been sized for our house truck so is smaller than ideal for the gfx1424e. If we purchased the mate display/control unit for the inverter would we be able to programme the iverter to charge from our generator? The user manual seems to suggest we could. The generator is a petrol inverter geny 230v 50hz 900w constant 1000w peak.
We intend on purchasing a larger 3kva generator next year but for now we need to get through this winter with what we have.
Please advise if it would be possible to set the gfx1424e to run from our 900/1000w sine wave geny with using the mate controller to programme the inverter. If so what settings would I need to set?
Off grid,
12 x 170w in 6 strings, outback fm80, 600ah 24v in 2v cells,
Outback gfx1424e. Victron 350w inverter.
12 x 170w in 6 strings, outback fm80, 600ah 24v in 2v cells,
Outback gfx1424e. Victron 350w inverter.
Comments
Have you read the post on Generator support? http://forum.solar-electric.com/discussion/17098/demonstration-of-generator-support
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
the main reason for the geny would be for charging on days when we have very little sun rather than supporting large loads.
in the manual for the gfx1424e it says using the mate you can limit generator ac in current to min 2.5amps max 30amps with the default setting being 25amps. But doesn't say what the increments are. Could I set this so it won't overload our small geny with a constant 900w output and a 1000w peak?
12 x 170w in 6 strings, outback fm80, 600ah 24v in 2v cells,
Outback gfx1424e. Victron 350w inverter.
Perhaps, somebody with a similar inverter can look at the programming steps and let us know. Or you will have to call Outback support.
From what I recall here, nobody has complained that the gen/ac2 steps were too large.
-Bill
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
12 x 170w in 6 strings, outback fm80, 600ah 24v in 2v cells,
Outback gfx1424e. Victron 350w inverter.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter